6.6 KV/11 KV Circuit Breaker Preventive Maintenance Checklist

0
19
6.6 KV/11 KV Circuit Breaker Preventive Maintenance Checklist
6.6 KV/11 KV Circuit Breaker Preventive Maintenance Checklist

Circuit breakers are essential protective equipment in medium-voltage power networks, particularly in industrial & substation settings. 

Regular preventive maintenance of 6.6kV & 11kV circuit breakers ensures that power distribution systems run smoothly, reduces downtime, and avoids future breakdowns. 

The checklist below is divided into two sections: 

  1. Circuit Breaker Testing Checklist
  2. Preventive Maintenance Activity Checklist

Test-based performance evaluation & step-by-step physical maintenance activity, both of which are required to preserve operational integrity.

This section describes the standard testing techniques that must be followed during preventative maintenance. 

Each test verifies several aspects of the breaker’s health, including mechanical performance, insulation, and contact integrity.

A circuit breaker analyzer kit is used to test the timing of breaker operations. This tests the opening, shutting, & bouncing times of contacts to ensure mechanical parts are operating within acceptable parameters.

Prolonged timings could indicate mechanical wear (or) lubrication concerns.

The main contacts’ resistance is tested with a micro-ohm meter. 

High contact resistance may indicate contact erosion or oxidation, which can cause heating & inefficiency during operation. 

The value must fall within the manufacturer’s specified range.

Use a 5kV or 1kV megger to measure insulation resistance (IR) across breaker poles. 

This is essential for detecting degeneration in insulation material, which can lead to internal failures or flashover. 

Minimum acceptable values must be based on ISO/IEC standards (or) OEM guidelines.

This section discusses physical inspection, cleaning, mechanical tests, and functional verification methods to ensure the circuit breaker is in good working order.

Begin by obtaining a Permit to Work (PTW) & establishing full electrical isolation. 

When working with medium-voltage switchgear, safety is the most important consideration.

Visually inspect the breaker for signs of physical deterioration, rusting, or contamination. 

This includes inspecting the 

  • Panel’s surface, 
  • Nameplates, 
  • Wire quality, and 
  • Signs.

Turn off the DC power source to prevent unwanted actions. 

Before proceeding with any internal work, remove the control plug to completely isolate the control circuit.

If the breaker is spring-operated, make sure the springs are drained before performing any maintenance. 

This prevents unintended movements when service.

Dust, carbon deposits, and foreign particles can be removed from inside surfaces using a dry cloth or a vacuum cleaner. 

Clean the insulators to prevent tracking and flashover.

Check for oil leaks in Minimum Oil Circuit Breakers (MOCBs). Leaking oil can weaken insulation and cause fires. 

Before proceeding with additional testing, stop any leaks that have occurred.

To ensure that sliding surfaces, interlocks, racking mechanisms, & latch parts operate smoothly, use the proper grease or lubrication.

Check that the outgoing cable ends are correctly earthed before handling terminals. 

This is an precautionary measure to avoid residual charge shocks.

Look for evidence of 

  • Overheating, 
  • Discolouration, or 
  • Loose connections 

at the terminal lugs. 

Also, check surge arrestors for cracks, wear, and missing pieces.

Ensure that the breaker racks move smoothly into & out of the cubicle with minimal resistance. 

Lubrication & alignment may be required if binding is detected.

Check that all panel indication bulbs (Trip, Close, Healthy, etc.) are working. Replace faulty bulbs (or) LEDs as necessary.

Space heaters keep moisture from condensing inside the breaker panel. Test their resistance and functionality.

Examine all primary contacts for evidence of pitting, wear, and discolouration. 

If the erosion exceeds the permitted limit set by the manufacturer, replace the contacts.

Repeat breaker timing tests after maintenance to confirm improvements or consistency in operation.

Assess oil condition in MOCBs by sampling and testing for dielectric strength, moisture content, and sludge presence. 

If the oil does not satisfy the dielectric specifications, replace it.

For vacuum circuit breakers, examine the insulating resistance of the vacuum bottle. 

A decline in IR value may indicate internal arcing or a loss of vacuum integrity.

Verify contact resistance after cleaning and tightening. Low resistance minimizes energy loss & heating.

Check the mechanical & electrical interlocks that govern the close/trip actions. To avoid misoperation, all interlocks must function properly.

After conducting internal checks, disconnect temporary earth connections & securely close & lock all compartment doors.

To avoid unintentional energization, ensure that the breaker is only racked into the service position when triggered.

Reconnect the control socket and turn on the DC supply to ensure the control circuit is completely operational.

Switch the breaker to the test position to ensure adequate control response without igniting the load.

To check that the breaker trips successfully on a protection instruction, simulate problems using relay circuits.

Return the PTW – permit to work and notify the appropriate staff once all maintenance tasks have been completed and the system has been verified safe.

All works must be signed by both the Site Engineer & the Maintenance Engineer. This assures accountability and adherence to safety & operational standards.

Previous articleKW to HP Calculator
Rabert T
As an electrical engineer with 5 years of experience, I focus on transformer and circuit breaker reliability in 110/33-11kV and 33/11kV substations. I am a professional electrical engineer with experience in transformer service and maintenance. I understand electrical principles and have expertise troubleshooting, repairing, and maintaining transformers, circuit breakers, and testing them.