Underground Cables (UG) Test Procedure

0
9
Underground Cables (UG) Test Procedure
Underground Cables (UG) Test Procedure

The objective is to verify the electrical integrity of 

  • Cable insulation, 
  • Screen continuity and 
  • Sheath condition 

following installation thereby ensuring safe and reliable operation of the cable system.

This procedure applies to all types of underground power cables installed for

  • Low Voltage (LV), 
  • Medium Voltage (MV) and 
  • High Voltage (HV) 

distribution and transmission systems which includes:

  • Single core and multi core XLPE (or) EPR insulated cables,
  • Armoured & unarmoured cable systems,
  • Direct buried, ducted and trough installed cables and
  • Cable joints, terminations & sealing ends.
Standard / CodeDescription
IEC 60502Power cables with an extruded insulation & their accessories.
IEC 60229Tests on cable oversheath / outer sheath.
IEEE 400Guide for the field testing of shielded power cable systems.
IS 7098Cross linked polyethylene insulated thermoplastic sheathed cables.
OSHA 1910.333Electrical safety — Selection and use of work practices.

All testing shall be performed by a qualified electrical engineer (or) a licensed cable testing technician. 

A minimum of 2 persons should be present at all times during high voltage (HV) testing.

  • Insulating rubber gloves rated for the test voltage,
  • Safety goggles / face shield,
  • Arc flash rated clothing (minimum Category 2),
  • Insulating rubber mat at the test station and
  • Safety boots with electrical hazard rating.
  • Isolate all cable ends from the live conductors and confirm the absence of voltage using an approved voltage detector.
  • Post warning signs as ‘High Voltage (HV) Testing in Progress’ at all cable ends & access points.
  • Erect temporary barriers to avoid unauthorised access within the test zone.
  • Ensure the cable is discharged and earthed before connecting (or) removing any test equipment.
  • Maintain radio communication between the team at the test set & the team at the far end.
  • Obtain & display a valid Permit to Work (PTW) before the process of commencing.
EquipmentSpecification / RangeCalibration Required
Insulation Resistance (IR) Tester500 V / 1 kV / 5 kV / 10 kV DCYes / Annual
High Voltage DC Test Set0-80 kV DC, 20 mAYes / Annual
Very Low Frequency (VLF) Test Set0.1 Hz, 0-52 kV ACYes / Annual
Continuity Tester / Low-Ohm MeterResolution: 0.01 mOhm (mΩ)Yes / Annual
Sheath Fault LocatorPulse reflection / TDR typeRecommended
Calibrated Measuring TapeAs requiredNo
Earth Resistance Tester0-2000 Ohm (Ω)Yes / Annual

Before any electrical test is performed a thorough visual inspection shall be conducted:

  • Confirm the cable route markers, joint bays and termination chambers are accessible & correctly identified.
  • Inspect cable terminations and joints for any physical damage, moisture ingress, oil leaks (or) incorrect assembly.
  • Check armour wire bonding & earthing connections at both ends.
  • Verify the cable identification labels/tags match the single line diagram.
  • Record any defects with photographs & report immediately for the rectification before testing.

To verify that conductor connections are complete with no open circuits.

  • Short circuit and earth all the conductors at the far end of the cable.
  • Using a continuity tester / low ohm meter measure the conductor resistance for each phase (L1, L2, L3) & neutral at the near end.
  • Compare the measured resistance against the calculated value: R = rho x L / A (where rho – resistivity of conductor material, L – cable length, A – cross sectional area).
  • Measured the values must not exceed the manufacturers specified resistance by more than 5%.
  • Record all the results in the test datasheet.

To assess the condition of cable insulation before applying a high voltage.

System VoltageTest Voltage (DC)Min. Acceptable IR
Up to 1 kV1000 V DC100 MΩ
1 kV – 11 kV5000 V DC1000 MΩ
11 kV – 33 kV10000 V DC10000 MΩ
  • Ensure all the conductors are isolated and deenergised.
  • Connect the IR tester across each conductor and earth by testing each combination: L1-E, L2-E, L3-E & L1-L2, L2-L3, L3-L1.
  • Apply the test voltage for a time duration of 1minute (60 seconds) & record the reading.
  • Polarisation Index to be calculated (PI = IR at 10 min/IR at 1 min). PI must be greater than 2.0 (> 2.0) for the acceptable insulation.
  • Discharge the cable for at least 4 times the test duration before proceeding.

To confirm the dielectric integrity of the cable insulation under a stress conditions.

Method A: DC Withstand (for cables up to 33 kV)

  • Apply DC voltage at a ramp rate not exceeding 1 kV/s up to the specified test voltage (typically 3 x U0 for 15 minutes).
  • Monitor leakage current throughout. A stable or decreasing current is acceptable. A rising (or) fluctuating current indicates a fault.
  • If the cable withstands the testing voltage for the full complete duration without breakdown, it passes.

Method B: VLF Withstand (preferred for XLPE/EPR cables)

  • Connect the VLF test set at 0.1 Hz. Apply 3 x U0 AC voltage for 1 hr (60 minutes).
  • Monitor for partial discharge activity and if PD measurement is integrated in the test set.
  • Failure (flashover/breakdown) at any point constitutes a test rejection.
  • To verify that the outer sheath & bedding are intact & provide adequate protection for the metallic screens and armour.
  • Disconnect all the screen and armour earth connections at both ends.
  • Apply 5 kV DC between the metallic screen/armour & earth for 1 minute (60 seconds).
  • Minimum acceptable insulation resistance of the outer sheath: 1 MΩ per km of cable length.
  • If a sheath fault is indicated utilize a TDR (or) sheath fault locator to pinpoint the fault location for repair.
TestParameterAcceptance Criteria
ContinuityConductor ResistanceWithin 5% of calculated value
IR TestInsulation ResistancePer voltage class (see 6.3)
IR TestPolarisation IndexPI > 2.0
HV / VLF WithstandWithstand (no breakdown)No flashover / leakage stable
Sheath IntegritySheath IRMin. 1 MΩ/km

All test results shall be recorded on the UG Cable Test Report Form. 

The report shall include:

  • Cable identification, rating, length and installation date.
  • Test equipment details, serial numbers and calibration certificates.
  • Ambient temperature & humidity at time of testing.
  • Individual test readings for every phase & each test type.
  • Pass (or) Fail status for each test.
  • Name & signature of Test Engineer & Witnessing Authority.

Completed test reports shall be submitted to the Project Engineer within 24 hours of testing & archived in the project quality file for the duration of the cables service life.

Previous articlePartial Discharge (PD) Testing
Rabert T
As an electrical engineer with 5 years of experience, I focus on transformer and circuit breaker reliability in 110/33-11kV and 33/11kV substations. I am a professional electrical engineer with experience in transformer service and maintenance. I understand electrical principles and have expertise troubleshooting, repairing, and maintaining transformers, circuit breakers, and testing them.