This document explains the standard test procedure for underground (UG) power cables prior to energization.
- Objective
- Scope
- References & Standards
- Safety Precautions
- Qualified Personnel
- Personal Protective Equipment (PPE)
- Safety Precautions
- Test Equipment Required
- Test Procedures
- Visual Inspection
- Continuity Test
- Insulation Resistance (IR) Test
- High Voltage DC / VLF Withstand Test
- Sheath Integrity Test
- Acceptance Criteria
- Documentation
Objective
The objective is to verify the electrical integrity of
- Cable insulation,
- Screen continuity and
- Sheath condition
following installation thereby ensuring safe and reliable operation of the cable system.
Scope
This procedure applies to all types of underground power cables installed for
- Low Voltage (LV),
- Medium Voltage (MV) and
- High Voltage (HV)
distribution and transmission systems which includes:
- Single core and multi core XLPE (or) EPR insulated cables,
- Armoured & unarmoured cable systems,
- Direct buried, ducted and trough installed cables and
- Cable joints, terminations & sealing ends.
References & Standards
| Standard / Code | Description |
| IEC 60502 | Power cables with an extruded insulation & their accessories. |
| IEC 60229 | Tests on cable oversheath / outer sheath. |
| IEEE 400 | Guide for the field testing of shielded power cable systems. |
| IS 7098 | Cross linked polyethylene insulated thermoplastic sheathed cables. |
| OSHA 1910.333 | Electrical safety — Selection and use of work practices. |
Safety Precautions
Qualified Personnel
All testing shall be performed by a qualified electrical engineer (or) a licensed cable testing technician.
A minimum of 2 persons should be present at all times during high voltage (HV) testing.
Personal Protective Equipment (PPE)
- Insulating rubber gloves rated for the test voltage,
- Safety goggles / face shield,
- Arc flash rated clothing (minimum Category 2),
- Insulating rubber mat at the test station and
- Safety boots with electrical hazard rating.
Safety Precautions
- Isolate all cable ends from the live conductors and confirm the absence of voltage using an approved voltage detector.
- Post warning signs as ‘High Voltage (HV) Testing in Progress’ at all cable ends & access points.
- Ensure the cable is discharged and earthed before connecting (or) removing any test equipment.
- Maintain radio communication between the team at the test set & the team at the far end.
- Obtain & display a valid Permit to Work (PTW) before the process of commencing.
Test Equipment Required
| Equipment | Specification / Range | Calibration Required |
| Insulation Resistance (IR) Tester | 500 V / 1 kV / 5 kV / 10 kV DC | Yes / Annual |
| High Voltage DC Test Set | 0-80 kV DC, 20 mA | Yes / Annual |
| Very Low Frequency (VLF) Test Set | 0.1 Hz, 0-52 kV AC | Yes / Annual |
| Continuity Tester / Low-Ohm Meter | Resolution: 0.01 mOhm (mΩ) | Yes / Annual |
| Sheath Fault Locator | Pulse reflection / TDR type | Recommended |
| Calibrated Measuring Tape | As required | No |
| Earth Resistance Tester | 0-2000 Ohm (Ω) | Yes / Annual |
Test Procedures
Visual Inspection
Before any electrical test is performed a thorough visual inspection shall be conducted:
- Confirm the cable route markers, joint bays and termination chambers are accessible & correctly identified.
- Inspect cable terminations and joints for any physical damage, moisture ingress, oil leaks (or) incorrect assembly.
- Check armour wire bonding & earthing connections at both ends.
- Record any defects with photographs & report immediately for the rectification before testing.
Continuity Test
To verify that conductor connections are complete with no open circuits.
- Short circuit and earth all the conductors at the far end of the cable.
- Using a continuity tester / low ohm meter measure the conductor resistance for each phase (L1, L2, L3) & neutral at the near end.
- Compare the measured resistance against the calculated value: R = rho x L / A (where rho – resistivity of conductor material, L – cable length, A – cross sectional area).
- Measured the values must not exceed the manufacturers specified resistance by more than 5%.
- Record all the results in the test datasheet.
Insulation Resistance (IR) Test
To assess the condition of cable insulation before applying a high voltage.
| System Voltage | Test Voltage (DC) | Min. Acceptable IR |
| Up to 1 kV | 1000 V DC | 100 MΩ |
| 1 kV – 11 kV | 5000 V DC | 1000 MΩ |
| 11 kV – 33 kV | 10000 V DC | 10000 MΩ |
- Ensure all the conductors are isolated and deenergised.
- Connect the IR tester across each conductor and earth by testing each combination: L1-E, L2-E, L3-E & L1-L2, L2-L3, L3-L1.
- Apply the test voltage for a time duration of 1minute (60 seconds) & record the reading.
- Polarisation Index to be calculated (PI = IR at 10 min/IR at 1 min). PI must be greater than 2.0 (> 2.0) for the acceptable insulation.
- Discharge the cable for at least 4 times the test duration before proceeding.
High Voltage DC / VLF Withstand Test
To confirm the dielectric integrity of the cable insulation under a stress conditions.
Method A: DC Withstand (for cables up to 33 kV)
- Apply DC voltage at a ramp rate not exceeding 1 kV/s up to the specified test voltage (typically 3 x U0 for 15 minutes).
- Monitor leakage current throughout. A stable or decreasing current is acceptable. A rising (or) fluctuating current indicates a fault.
- If the cable withstands the testing voltage for the full complete duration without breakdown, it passes.
Method B: VLF Withstand (preferred for XLPE/EPR cables)
- Connect the VLF test set at 0.1 Hz. Apply 3 x U0 AC voltage for 1 hr (60 minutes).
- Monitor for partial discharge activity and if PD measurement is integrated in the test set.
- Failure (flashover/breakdown) at any point constitutes a test rejection.
Sheath Integrity Test
- To verify that the outer sheath & bedding are intact & provide adequate protection for the metallic screens and armour.
- Disconnect all the screen and armour earth connections at both ends.
- Apply 5 kV DC between the metallic screen/armour & earth for 1 minute (60 seconds).
- Minimum acceptable insulation resistance of the outer sheath: 1 MΩ per km of cable length.
- If a sheath fault is indicated utilize a TDR (or) sheath fault locator to pinpoint the fault location for repair.
Acceptance Criteria
| Test | Parameter | Acceptance Criteria |
| Continuity | Conductor Resistance | Within 5% of calculated value |
| IR Test | Insulation Resistance | Per voltage class (see 6.3) |
| IR Test | Polarisation Index | PI > 2.0 |
| HV / VLF Withstand | Withstand (no breakdown) | No flashover / leakage stable |
| Sheath Integrity | Sheath IR | Min. 1 MΩ/km |
Documentation
All test results shall be recorded on the UG Cable Test Report Form.
The report shall include:
- Cable identification, rating, length and installation date.
- Test equipment details, serial numbers and calibration certificates.
- Ambient temperature & humidity at time of testing.
- Individual test readings for every phase & each test type.
- Pass (or) Fail status for each test.
Completed test reports shall be submitted to the Project Engineer within 24 hours of testing & archived in the project quality file for the duration of the cables service life.