Protection System & Measuring Equipment – Top 25 Interview Questions and Answers

0
231
Protection System & Measuring Equipment - Top 25 Interview Questions and Answers
Protection System & Measuring Equipment - Top 25 Interview Questions and Answers

A Circuit Breaker (CB) is an automatic switching device that protects electrical circuits from the damage caused by overload, short circuit and earth faults. 

It detects abnormal current and interrupts the electrical supply safely.

Key Functions:

  • Protects electrical equipment,
  • Prevents fire hazards, 
  • Allows manual and automatic switching &
  • Can be reset after tripping. 

Common types of circuit breakers include:

  • MCB (Miniature Circuit Breaker): Domestic and commercial applications 
  • MCCB (Moulded Case Circuit Breaker): Industrial distribution systems 
  • ACB (Air Circuit Breaker): Low-voltage high-current applications 
  • VCB (Vacuum Circuit Breaker): Medium-voltage systems 
  • OCB (Oil Circuit Breaker): Older medium/high-voltage installations 
  • SF₆ Circuit Breaker: High-voltage substations 
  • RCB/RCCB: Earth leakage protection 
  • ELCB: Earth leakage protection (older technology) 
TypeFull FormApplication
ACBAir Circuit BreakerLV switchboards (up to 690 V)
MCBMiniature Circuit BreakerHomes and offices
MCCBMoulded Case Circuit BreakerIndustrial feeders
OCBOil Circuit BreakerOlder substations
VCBVacuum Circuit Breaker3.3–36 kV systems
SF₆ CBSulphur Hexafluoride Circuit BreakerHV/EHV substations

A fuse that protects electrical circuits by melting its fuse element when current exceeds the safe limit.

Purpose

  • Overload protection,
  • Short-circuit protection, 
  • Prevents equipment damage and 
  • Fire prevention.

A fuse contains a low melting-point metal wire.

When excessive current flows:

  • Heat is produced (I²R loss),
  • Fuse element melts,
  • Circuit opens and
  • Current stops flowing. 

Unlike a circuit breaker a fuse should be replaced after operation.

Minimum fusing current is the lowest current that causes the fuse element to melt.

Typically

Minimum Fusing Current = 1.25 to 2 times the rated current

Example:

  • Fuse rating = 10 A 
  • Minimum fusing current ≈ 12.5 – 20 A (depends on fuse type) 

A relay is an automatic protective device that detects abnormal electrical conditions and sends a trip command to the circuit breaker.

It protects:

  • Transformers 
  • Motors 
  • Generators 
  • Feeders 
  • Transmission lines 
FuseRelay
Directly interrupts currentSends trip signal to breaker
One-time operationReusable
Simple constructionIntelligent protection device
Fast operationWorks with circuit breaker
Needs replacementReset after fault clearance

A reverse power relay protects generators from operating as motors.

It trips the generator if power flows from the busbar back into the generator which may occur due to prime mover failure.

Typical setting:

  • 2-10% of generator rated power 

Working principle:

Step-1: CT/PT measures electrical quantities. 

Step-2: Relay continuously monitors current and voltage. 

Step-3: If settings are exceeded.

Step-4: Relay energizes trip coil. 

Step-5: Circuit breaker opens. 

Step-6: Fault is isolated. 

When a fault occurs:

  • Relay detects the fault. 
  • Relay energizes trip coil. 
  • Contacts separate. 
  • Arc forms. 
  • Arc is extinguished using air, oil, vacuum (or) SF₆. 
  • Circuit becomes isolated. 

Neutral earthing means connecting the transformer (or) generator neutral to earth.

Advantages

  • Limits fault current, 
  • Stabilizes system voltage,
  • Protects equipment,
  • Reduces overvoltage, 
  • Improves personnel safety and
  • Enables protective relays to detect earth faults. 

Common generator protections:

  • Differential protection (87G) 
  • Overcurrent (50/51) 
  • Earth fault (64) 
  • Reverse power (32) 
  • Under voltage (27) 
  • Over voltage (59) 
  • Under frequency (81U) 
  • Over frequency (81O) 
  • Loss of excitation (40) 
  • Negative sequence (46) 
  • Stator earth fault 
  • Rotor earth fault 
  • Overload 

Motor protections include:

  • Overload 
  • Short circuit 
  • Earth fault 
  • Phase failure 
  • Phase reversal 
  • Locked rotor 
  • Stall protection 
  • Under voltage 
  • Over voltage 
  • Thermal protection 
  • Bearing temperature 
  • Winding temperature 

Overcurrent protection uses:

  • Current Transformer (CT),
  • Overcurrent Relay (50/51),
  • Circuit Breaker. 

When current exceeds the relay setting the relay trips the breaker.

IDMT relay operating time decreases as fault current increases.

Characteristics

  • Small overload → Longer operating time 
  • Heavy fault → Faster tripping 

This allows coordination between upstream & downstream protective devices.

An overload trip occurs when current exceeds the rated value for a prolonged period.

Example:

A 100 A motor drawing 130 A continuously will eventually trip due to overload.

Purpose:

  • Prevents overheating 
  • Protects insulation 
  • Extends equipment life 
Short Circuit TripOverload Trip
Very high currentSlightly above rated current
InstantaneousTime delay
Severe faultNormal overload
Magnetic protectionThermal protection
Prevents equipment damagePrevents overheating

Preferential trip is a load shedding system that disconnects non-essential loads first during overload (or) low generator capacity.

Essential loads remain energized.

Used in:

  • Ships, 
  • Power plants, 
  • Emergency generators and 
  • Hospitals. 

Reverse current (or) reverse power trip protects generators from receiving power instead of supplying it.

It prevents:

  • Generator motoring, 
  • Prime mover damage, 
  • Turbine damage and
  • Diesel engine damage. 

Under voltage trip disconnects equipment when voltage falls below a preset limit.

Importance of Protective Trips

  • Equipment protection, 
  • Personnel safety, 
  • Prevents overheating, 
  • Prevents fire, 
  • Maintains power system stability and 
  • Reduces downtime. 
InstrumentMeasures
AmmeterCurrent (A)
VoltmeterVoltage (V)
WattmeterPower (W or kW)
MeggerInsulation Resistance (MΩ or GΩ)
AmmeterVoltmeter
Measures currentMeasures voltage
Connected in seriesConnected in parallel
Very low internal resistanceVery high internal resistance
Unit: AmpereUnit: Volt

Megger testing measures the insulation resistance of electrical equipment using a high DC test voltage.

Common test voltages:

  • 250 V – Electronic circuits,
  • 500 V – LV motors and cables, 
  • 1000 V – Industrial LV equipment and
  • 2500–5000 V – MV/HV equipment (as specified) 

Applications:

  • Motors, 
  • Transformers, 
  • Power cables, 
  • Switchgear and
  • Generators. 

Higher insulation resistance generally indicates better insulation condition.

CT (Current Transformer)PT (Potential Transformer)
Reduces high current to a standard value (typically 1 A or 5 A)Reduces high voltage to a standard value (typically 110 V or 63.5 V)
Connected in series with the circuitConnected in parallel with the circuit
Used for current measurement and protectionUsed for voltage measurement and protection
Secondary should never be open circuited while energizedSecondary should never be short circuited while energized
Used with ammeters, energy meters and protection relaysUsed with voltmeters, wattmeters, synchronizing equipment and protection relays