Specification Checklist: Limiting Values for Substation Components

0
953
Specification Checklist: Limiting Values for Substation Components
Specification Checklist: Limiting Values for Substation Components

It is essential to have a thorough understanding of the allowable test limits for substation electrical equipment and to adhere to them in order to ensure that the operation is both reliable and safe. 

This organized post that follows provides a description of standard test parameters and permitted values for a wide range of substation components. 

These parameters and values are based on national & international standards.

Test ParameterConditionLimitReference
BDV (Breakdown Voltage)First Charging≥ 60 kV (2.5 mm gap)IS 1866
 During O&M≥ 50 kV (2.5 mm gap)IS 1866
Moisture ContentFirst Charging≤ 15 ppmIS 1866
 During O&M≤ 25 ppmIS 1866
Resistivity @ 90°C≥ 0.1 x 10¹² Ohm-cmIS 1866
Acidity≤ 0.2 mg KOH/gIS 1866
Interfacial Tension (IFT) @ 27°C≥ 0.018 N/mIS 1866
Tan Delta @ 90°C≤ 0.20IS 1866
Flash Point≥ 126°CIS 1866
ParameterConditionLimitReference
Dew Point (SF₆ Gas)See detailed table belowVaries
Dew Point (Operating Air)≤ -45°C @ atmospheric pressure
Voltage LevelClosing TimeTrip TimePhase DiscrepancyBreak-Break Time
400 kV≤ 150 ms≤ 25 ms≤ 3.33 ms≤ 2.5 ms
220 kV≤ 200 ms≤ 35 ms≤ 3.33 ms≤ 2.5 ms
MakePIR Time (ms)Reference
BHEL12–16OEM
ABB, NGEF, M&G, TELK8–12OEM
ABB (HVDC)8–12OEM
ParameterLimitReference
PIR-to-Main Contact Overlap≥ 6 msOEM
PIR Opening Time Before Main≥ 5 msOEM
Tan Delta (Grading Capacitor @ 20°C)≤ 0.007IEC 359
Capacitance Variation-2IEC 359
CB Contact Resistance≤ 150 µΩ
Terminal Connector Resistance≤ 10 µΩ per connectorNGC UK
Test PointLimitReference
Phase to Earth≥ 1000 MΩ @ 5/10 kV
Across Contacts≥ 1000 MΩ @ 5/10 kV
Control Cables≥ 50 MΩ @ 0.5 kV

It is essential that all pressure switches, including SF₆, air, and oil, remain within a range of ±0.1 bar of their predetermined values.

ConditionLimitReference
At Filling≥ 40 kV (2.5 mm gap)OEM
During O&M≥ 20 kV (2.5 mm gap)OEM
ParameterLimitReference
IR (Primary to Earth)≥ 1000 MΩ @ 5/10 kV
IR (Secondary to Earth)≥ 50 MΩ @ 0.5 kV
IR (Control Cables)≥ 50 MΩ @ 0.5 kV
Tan Delta (@ 20°C)≤ 0.007
Connector Resistance≤ 10 µΩ per connectorNGC UK
CT Ratio Error – Protection±3%IS 2705
CT Ratio Error – Metering±1%IS 2706
ParameterLimitReference
Tan Delta (@ 20°C)≤ 0.007IEC 358
Capacitance Variation-2IEC 358
Connector Resistance≤ 10 µΩ per connectorNGC UK
IR (Primary to Earth)≥ 1000 MΩ @ 5/10 kV
IR (Secondary to Earth)≥ 50 MΩ @ 0.5 kV
ParameterLimitReference
BDV≥ 30 kV (2.5 mm gap)IS 1866
Moisture Content≤ 35 ppmIS 1866
Resistivity @ 90°C≥ 0.1 x 10¹² Ohm-cmIS 1866
Acidity≤ 0.5 mg KOH/gIS 1866
IFT @ 27°C≥ 0.018 N/mIS 1866
Tan Delta @ 90°C≤ 1.0IS 1866
Flash Point≥ 125°CIS 1866
Core TypeToleranceReference
Protection±5%IEEE C93.1
Metering±0.5%IEC 186

The station earth resistance equals or less than 1 ohm.

Temperature Rise Above AmbientCondition
≤ 15°CNormal
15°C – 50°CAlert
> 50°CImmediate Attention Required
EquipmentMinimum IR
Electric Motors50 MΩ
Control Cables50 MΩ
LT Transformers100 MΩ
LT Switchgear100 MΩ
ParameterLimitReference
Terminal Connector Resistance≤ 10 µΩ + 20%IEEE 450
Specific Gravity1200 ± 5 gm/L @ 27°C

Utilize the following formula in order to adjust Tan Delta to 20 degrees Celsius:

Corrected Tan Delta (20°C) = Measured Tan Delta/Correction Factor (K)

Temperature (°C)K Factor
100.8
150.9
201
251.12
301.25
351.4
401.55
451.75
501.95
552.18
602.42
652.7
703
MakeRated Pressure Dew PointAtmospheric Pressure Dew PointRemarks
BHEL-15°C-36°CCommissioning
 -7°C-29°CO&M
 -5°C-27°CCritical
M&G-39°CCommissioning
 -32°CO&M
CGL-15°C-35°CCommissioning
 -10°C-31°CO&M
ABB-15°C-35°CCommissioning
 -5°C-26°CO&M
NGEF-15°C-36°CCommissioning
 -7°C-29°CO&M

Note: Take note that the dew point varies depending on the pressure that is being measured. If readings are taken at the rated gas pressure, make sure they are adjusted to reflect the pressure of the atmosphere.

Substation equipment limiting values and test requirements must be followed to ensure electrical asset dependability, safety, and longevity. Regular testing, diagnostics & maintenance based on these standard parameters assist in determining faults, avoid equipment failure, and reduce unplanned outages.

National & international standards including IS, IEC, IEEE, and OEM establish essential test values for transformers, circuit breakers, CTs, CVTs, isolators, surge arresters, and auxiliary systems like batteries and earthing. Understanding and utilizing these values during commissioning, maintenance, and condition monitoring optimizes substation performance.

A planned approach to monitoring these characteristics improves power transmission and distribution network stability, efficiency, asset management, and regulatory compliance.