PLC Panel FAT Procedure

0
1275
PLC Panel FAT Procedure
PLC Panel FAT Procedure

The Factory Acceptance Test (FAT) is an important quality control process performed at the manufacturer’s facility prior to a PLC (Programmable Logic Controller) panel being shipped to the site. 

The objective is to ensure that the panel is built in accordance with the approved plans, specifications, & functional requirements.

FAT signifies that:

  • All components are properly installed.
  • The wiring is well organized and labeled.
  • The program logic works as anticipated.
  • Communication with the external systems functions properly.
  • Safety interlocks & emergency functions are evaluated.

FAT saves commissioning time, prevents costly onsite repairs, and boosts client confidence.

Before starting the FAT procedure, the subsequent components should be in place:

  • Certified General Arrangement (GA) Drawings
  • Wiring and loop diagrams.
  • PLC I/O list & tag information
  • Finalized PLC program & HMI screens
  • List of test cases or conditions.
  • Required equipment (multimeter, power supply, laptop with the programming software)
PLC Panel
PLC Panel
  • Check the panel for damage, correct paint finish, & IP rating.
  • Check physical dimensions against GA drawings.
  • Ensure that all nameplates, labels, & terminal markers are legible & accurate.
  • Check that the components (PLC, relays, SMPS, MCBs, etc.) match the BOM/specification.
  • Check the wiring for quality, ferrule numbering, & power/control wiring segregation.
  • Match the wiring to the schematic diagram.
  • Check the correct wire diameters, color codes, & terminal numbers.
  • Check the terminal tightness with a torque screwdriver.
  • Earth continuity testing for metal components and door bonding.
  • Turn on the panel even when there are no I/O connections.
  • Check the voltage and power supply that are coming in (for example, 24VDC).
  • PLC, CPU status should be checked (for example, the RUN/STOP mode).
  • Check that the HMI is able to boot up and display the home screen.
  • Toggle switches (or) test buttons can be used to simulate digital inputs (DI).
  • The activation of the associated logic / output (DO) should be monitored.
  • Analog inputs (AI) should be tested with a signal generator (or) simulator that has a range of 4–20mA or 0–10V.
  • Control devices, such as valves and variable frequency drives (VFDs), should have their analogue outputs (AO) checked.
  • The answer of each tag in the I/O list should be recorded.
I/O Simulation Coding
I/O Simulation Coding
  • The final PLC program should be uploaded, and a cross-check should be performed against the logic diagram (or) functional description.
  • Process sequences, such as motor start/stop, interlocks, and alarms, should be rendered in simulation.
  • Check the logic of the timer and counter.
  • It is important to check that safety interlocks such as emergency stop, overload, & power fail are effectively functioning.
  • Analyze the procedure of navigating between screens.
  • Check that the values displayed for the process (tank levels, temps, and statuses) are accurate.
  • Indicators of the current condition, popups, and alert screens should all be checked.
  • In case that it is relevant, verify the password protection & access levels.
HMI Functionality Testing
HMI Functionality Testing
  • Ensure that the PLC is communicating with the SCADA, DCS, or any other third-party systems (such as Profibus, Ethernet/IP, or Modbus).
  • Test the exchange of data and the activation of alarms.
  • Make use of simulation tools in order to test the flow of data in both ways.
PLC Terminals, I/O Modules
PLC Terminals, I/O Modules
  • Observe the alert messages displayed on the HMI while simulating fault conditions.
  • Test the system’s ability to shut down or respond to fail-safe conditions when simulated interlock violations occur.

Make sure that all of the panel papers, including the schematics, cable schedule, GA drawing, and FAT report, are up to date and the real panel is the same.

Make sure that backups of the software for the PLC and HMI programs are accessible.

S.NoTest DescriptionStatus (Yes/No)Remarks
1Panel physical condition checked  
2Components as per BOM  
3Terminal numbers and ferrules verified  
4Control and power wiring checked  
5Earth continuity tested  
6Power ON test successful  
7PLC in RUN mode  
8Digital I/Os simulated and verified  
9Analog I/Os simulated and verified  
10PLC logic sequence validated  
11HMI screens and buttons tested  
12Alarm and interlocks tested  
13Communication with SCADA/DCS verified  
14Documentation reviewed  
15Final program backups taken  
FAT Checklist
FAT Checklist

The FAT procedure for a PLC panel is an important quality assurance step that ensures the system functions as intended before it arrives on site. 

It lowers installation problems, shortens site commissioning time, and boosts credibility in both the vendor & the client. 

A thorough FAT consists of hardware inspection, logic simulation, connectivity tests, and document validation. 

Following a thorough checklist ensures that no steps are overlooked as well as the panel is properly prepared for delivery.