Conductor Continuity and Phasing Test Procedure for 132 kV Underground Cable

0
352
Conductor Continuity and Phasing Test Procedure for 132 kV Underground Cable
Conductor Continuity and Phasing Test Procedure for 132 kV Underground Cable

The Conductor Continuity and Phasing Test is an important pre-commissioning procedure for 132 kV underground cable systems. 

This test assures that each phase conductor is appropriately recognized and that the phase sequence remains unchanged between the testing and remote ends of the cable circuit. 

Correct phasing is necessary for avoiding major system failures, equipment damage and operational risks during energization.

The primary objective of this test is to validate proper phase identification and phase sequence throughout the wire length. 

It confirms that the R-Y-B (or equivalent) phases at one end are identical to the phases at the other end as per the approved drawings and system design.

1). Megger Insulation Resistance Tester (5 kV DC)

2). Digital Multimeter 

3). Good Earthing and Safety gear

This test will be performed only after:

1). All cable joins and terminations have been entirely completed.

2). Cable metallic screens/sheaths are correctly grounded via connection boxes or terminations.

3). The cable circuit is completely separated, discharged and confirmed safe for testing.

Make sure that all phase conductors at the cable’s remote end are separated from ground. 

This eliminates incorrect readings and ensures proper phase identification.

Install suitable physical barriers and warning signs (or) station a watchman at the remote end to prevent unexpected human contact with exposed conductors. 

Before starting the test make sure that all phases are free of ground.

Select one phase conductor at the remote end & strongly ground it leaving the other two phases isolated.

At the testing end connect the Megger to one conductor and ground. Apply a 1 kV DC test voltage & note the insulating resistance result.

The conductor grounded at the remote end will have zero or near-zero resistance indicating phase continuity.

Carefully record the phase color (or) identification.

Repeat the test for the remaining steps. 

Non-grounded conductors will have an extremely high insulation resistance (usually in giga-ohms – GΩ) indicating that they are not connected to the ground.

Note: Ensure safety discharge & ground the tested conductor prior to removing the Megger’s high-voltage lead.

Ground each phase sequentially at the remote end and then repeat the test till all three phases are positively detected and matched on both ends of the circuit.

1). At both the testing sites and the remote locations each step has been accurately identified.

2). It is completely consistent with the approved labels, single-line diagrams (or) as-built drawings that the phase sequence is used.

3). In terms of phase continuity or identification there is no space for error.

The Conductor Continuity and Phasing Test for 132 kV UG Cables is a basic but important verification step before cable energization. 

Proper execution assures proper phase alignment, increases system reliability and considerably lowers the chance of catastrophic failures when commissioning. 

Accurate documenting of test results improves long-term maintenance and operational safety.