CT & VT Testing during Commissioning

0
46
CT & VT Testing during Commissioning
CT & VT Testing during Commissioning

Current Transformers (CTs) and Voltage Transformers (VTs) are important in ensuring accurate measurement, reliable protection and safe operation of electrical power systems. 

During the commissioning phase of substations and industrial installations, thorough testing of CTs and VTs is essential to verify their performance, detect installation errors and ensure compliance with standards.

  1. Current Transformers (CT) and 
  2. Voltage Transformers (VT/PT) 

are essential components in electrical power systems. 

They are used for measurement, protection and control purposes by stepping down high current and voltage levels into safe and measurable values.

A Current Transformer converts high primary current (e.g., 1000 A) into a low secondary current (1 A or 5 A). It is widely used in:

  • Protection relays and
  • Metering systems.

CT operates on the principle of electromagnetic induction. 

When current flows through the primary conductor it induces a proportional current in the secondary winding.

Current transformers (CTs) are important power systems that measure and protect against overcurrent. Their accuracy class determines the accuracy with which they convert primary current to secondary current. IEC 61869-2 specifies standards for their performance & testing procedures.

A Voltage Transformer converts high voltage (e.g., 11 kV) into low voltage (e.g., 110 V). It is used in:

  • Voltage measurement
  • Protection and control circuits

Similar to a power transformer, it works on mutual induction converting high voltage to a proportional low voltage.

CT testing ensures proper performance, safety and accuracy.

Primary Tests:

a). Polarity Test

Polarity Test ensures correct current direction (P1→P2 and S1→S2). Incorrect polarity can lead to relay malfunction.

b). Ratio Test

Ratio Test verifies CT ratio (e.g., 1000/5). It ensures correct scaling between primary and secondary.

c). Insulation Resistance Test

Insulation Resistance Test performed using a megger to check insulation:

  • Primary to Secondary
  • Secondary to Earth

d). Continuity Test

Continuity Test ensures secondary winding is not open. Open circuit in CT secondary can generate dangerous high voltage.

e). Burden Test

Burden Test checks whether connected load (relay/meter) is within CT rated burden.

f). Magnetization / Excitation Test

Magnetization / Excitation Test determines CT core characteristics and helps identify knee point voltage.

CT & VT Testing during Commissioning
CT & VT Testing during Commissioning

The knee point is the voltage at which a small increase in voltage causes a large increase in current.

Standard Criteria

10% increase in voltage results in 50% increase in excitation current.

Practical Consideration

Below knee point: CT operates in linear region.

Above knee point: CT saturates → protection failure possible.

  • Disconnect CT secondary from all equipment
  • Connect test kit to CT secondary
  • Apply increasing AC voltage gradually
  • Record voltage and current readings
  • Plot V-I curve

a). Polarity Test

Polarity Test ensures correct phase relationship

b). Ratio Test

Ratio Test verifies transformation ratio (e.g., 11kV/110V)

c). Insulation Resistance Test

Insulation Resistance Test checks insulation between windings and earth

d). Burden Test

Burden Test ensures load is within rated capacity

e). Secondary Voltage Check

Secondary Voltage Check verify output voltage with applied input

f). Phase Angle Error Test

Phase Angle Error Test is important for accurate metering systems.

  1. Never open circuit CT secondary.
  2. Always short CT before disconnection.
  3. Ensure proper earthing.
  4. Knee point testing is critical for protection CTs.
  5. Accuracy is important for metering CTs.

Proper CT and VT testing during commissioning ensures system reliability, protection accuracy and operational safety. 

Following these correct procedures helps prevent failures and ensures compliance with standards.