Electrical & Instrumentation (E&I) QA&QC Interview Questions

0
676
Electrical & Instrumentation (E&I) QA&QC Interview Questions
Electrical & Instrumentation (E&I) QA&QC Interview Questions

Pursuant to NEC 501-5(5) © (6), the fills for the wires shall not exceed 25% of the cross-sectional area of the conduit size. 

PVC – Poly-Vinyl-Chloride

In order to minimize electrostatic noise so that there is no distribution of unnecessary signals. 

Minimum of 50mm (refer to NEC). 

a) For Horizontal – 3 meter (10 of feet) 

b) For Vertical – 6 meter (20ft.) 

According to SAES-P-111 – the cross sectional area no less than 70mm2 (2/0 AWG) / for stranded bare copper cable – 4/0 kcmil 

1/0 AWG / 50mm2 / per NFPA art. 250. 122 

Per NFPA art. 250. 122 minimum of 120mm2 (4/0 AWG) / 350 kcmil 

a) By Thermite Welding 

b) By mechanical compression approved. 

 a). Exd – Equipment Standard Symbols 

b). IIB – Gas Classification Group 

c). T5 – Temperature Classification Group

a). Underwriter Laboratories (UL)

b). CSA- Canadian Standard Association

Hazardous Location 

a). Classified Location 

  • Class 1; Zone 0, 1 & 2

b). Unclassified Locations

  • Class I, Division. 1 & 2
  • Class II, Div. 2
  • Class Ill, Wet Location

In terms of degrees shall not be shall not be more than 270 degrees to avoid straining the cables and consequent damage.

The National Electrical Code, Article 501-4 (A), stipulates that there must be five (5) complete threads engaged. 

a). Conductors in phase A are black.

b). Neutral is White,

c). Grounding is Green

90°C dry, 75°C wet.

a). Power cables for medium voltage-Megger test and DC high potential test.

b). Cathodic protection cables- Holiday Test.

c). Low voltage cables–Resistance Test & Megger Test

d). Cable related to Musical instruments – Megger Test, Continuity Test.

a). Type Test on oil – Winding Test, Turns Ratio Test and Transformer Oil tester

b). Electrical Motors – Winding test, the DC Resistance test, Megger test and Phase rotation test

c). Batteries – Voltage/Current Test, Specific Gravity (G) Test.

d). Circuit Breakers – Megger Test, Primary Current Inspection Test, and Ductor Test.

  • Indoor  – NEMA 1
  • Outdoor – NEMA 3 (or) 4.
  • Corrosive Environment – NEMA 4X 

No.

Lighting fixture shall be used only as a lamp shade to the light bulb etc. 

The locations covered by each division are: 

  • Class 1, Zone O – Flammable gasses (or) vapor (vapour) are always present in the area. 
  • Class 1, Division 1 –Arrangements of non-ventilated areas where flammable gasses or vapor gasses could exist at normal operating condition. 
  • Class 1, Zone 2- In this area flammable gas or vapor is not expected normally or for a short time during their working shifts. 

a). Type – Class 1, Zone O – where in w/c ignitable concentration of flammable gasses or vapors are always present (flammable mixture always present, 10%). 

b). Safety Factor – Class 1, Zone 1 – in which, under normal operation condition, flammable gasses or vapor having a w/c ignitable concentration are often present or may exist in the air, flammable mixture present 0. 1 to 10%. 

c). Flame tight – Class 1, Zone 2 – in w/c ignitable concentration of flammable gasses or vapor are not likely to occur in normal operation and if they do occur are likely to exist only for a short time (normal 0. 01 to 0. 1 % area – unclassified; normal 0. 01 %). 

Not Greater Than 0. 1 ohm. 

In the case of house construction NEC stands for National Electrical Code. 

  • NAFB- National Association of Fire Chiefs,
  • UL – Underwriters laboratory, 
  • NEMA – National Electrical Manufacturers Association, 
  • NETA – National Electrical Testing Association 

Report to the respective QA/QC manager / Supervisor or file a Raised Non Conformance Report (NCR) to the respective and concerned production unit who will take necessary and corrective action.