Electrical Interview Questions - Part 5
Electrical Interview Questions - Part 5

When a running motor’s supply is shut off, it continues to operate due to inertia. 

To quickly stop it, we apply a load (resistor) over the armature winding, and the motor should have a constant field supply. 

As a result, back EMF voltage is applied across the resistor, causing the motor to stop abruptly due to the load.

This particular method of braking is commonly referred as “Regenerative Braking”.

The voltage equation for DC motors is 

V = Eb-IaRa 

Where

V – Terminal voltage, 

Eb – Back EMF in motor, 

Ia – Armature Current, 

Ra – Armature Resistance. 

At the start, Eb is zero. 

As a result, V=IaRa, and Ia = V/Ra

Where,

Ra is extremely low, such as 0.01Ω

i.e., Ia will be greatly raised. 

The main advantage of employing a star delta starter is that it reduces the current used to start the motor.

The starting current is lowered to 3-4 times the current of direct online starting.

As a result, the beginning current is lowered, and the voltage drops during motor startup in systems are reduced. 

For lighting loads, a neutral conductor is required, hence the secondary need to be star winding. 

The lighting load is constantly imbalanced across all three phases. 

To reduce current unbalance in the primary, we use delta winding. Therefore, Delta-Star transformer is used for lighting loads. 

It depends on R=rho l/A, 

where 

Area (A) – Inversely proportional to resistance (R), 

thus as (A) increases, R reduces, and as R decreases, leakage current takes a low resistance channel, so the earth pin should be thicker. 

It is longer as the earth pin should be connected first and then disconnected last. This ensures the safety of the individual using the electrical instrument. 

Due to the high starting torque, series motors cannot be started without a load. Series motors are utilized in various applications like as trains and cranes. 

The ELCB is used to identify earth leakage faults. 

When the phase & neutral are connected in an ELCB, the current flows through the phase and must return to the neutral, resulting in zero current.

When there is a ground fault on the load side, current from phase passes directly via earth and does not return through neutral via ELCB. 

Once the side current is going but not returning, the ELCB will trigger and protect the other circuits from defective loads. 

Fault current will be quite high if neutral is not grounded, and it will return through the ELCB completely with no current difference.

To generate electricity, we need a prime mover, which provides mechanical power input to the alternator. 

This can be steam turbines or hydro turbines.

When the rotor poles rotate under the stator’s armature conductors, the field flux cuts the conductors, generating a sinusoidal voltage due to the polarity change of the rotor poles.

(i.e., N-S-N-S)

Yes, since the poles shift every half-cycle of alternating current voltage, the polarity of the AC voltage varies continuously. 

Thus, changing terminals in an alternating current system makes no impact. 

So, the AC solenoid attracts the plunger despite having interchangeable terminals.

The current currying of cables will vary according on the 

  • Site temperature (location), 
  • Type of run (duct, trench, buried, etc.), 
  • Number of tray, 
  • Depth of trench, and 
  • Distance between the cables. 

Derating occurs when the real present currying capacity of a cable is less than the current currying capacity (as specified in the cable catalogue).

Bus bars & isolators are rated for the continuous power flow, which implies they can carry high currents, raising their temperature. 

Thus, it is vital to test these devices for the temperature rise.

No. We cannot detect overvoltage by monitoring current alone since current increases not just for overvoltages but also for undervoltages.

Because of this, protection against overvoltage and overcurrent is essentially different. 

Over voltage relays are designed to detect overvoltages and safeguard the system against insulation breakdown and firing.

Over current relays are designed to detect internal short circuits, overload conditions, and ground faults, decreasing system failure and the risk of fire.

So, for improved system security.

It should feature both overvoltage and overcurrent relays.

The lamp will turn on if voltage across 2 phases is the same as the lamp voltage. 

When the voltage difference is large, the lamp is damaged; when the difference is small, the lamp lights up, depending on the type of lamp.

First, compute the load’s electrical current, then derate the electrical current using a derating factor (depending on site conditions and cable laying), and finally select a cable size from a cable catalog while keeping the derating electrical current.

After that, determine the length of cable necessary from the supply point of load to the load point. 

Calculate the maximum voltage drop (based on cable resistance and reactance from the cable catalog). 

If the voltage drop exceeds 3%, use a larger cable size.

The term “HRC” refers to a “high rupturing capacity” fuse that is utilized in electrical transformer distribution systems.

Every base-load power plant has a high load factor. 

We can cut generation costs by using high-efficiency power plants to serve base load.

Hydro power plants are more efficient than thermal and nuclear power plants.

Several methods of starting an induction motor which includes

  • DOL – Direct Online Starter
  • Star Delta Starter
  • Auto Transformer Starter
  • Resistance Starter
  • Series Reactor Starter

A lock-out relay is typically installed before (or) after the e-stop switch to allow the power to be turned off from a central point. 

This relay is powered by the same electrical source as control power & operates via a key lock switch. 

The relay contains a maximum of 24 contact points. 

This permits the control power of many computers to be shut out with the turn of a single key switch.

The angle difference is produced by the synchronous impedance of the alternator when there is no load. It should therefore show zero lagging, just like an inductor.

In electronic circuits, the capacitor tolerance is indicated by a code on the casing. 

The code is typically a letter that follows a 3-digit number.

Ex: 130Z

The first two are the first and second significant digits, while the third is a multiplier code. 

Most of the time, the last digit indicates how many zeros to write after the first two digits, which are read as Pico-Farads.

The standard range for measuring values in any process is 4-20 mA. The reason 4mA was chosen over 0mA is to provide fail-safe operation.

Ex: A pressure instrument outputs 4 mA to signify 0 psi and up to 20 mA indicates 100 psi, (or) full scale. 

Any fault with the instrument (for example, a broken wire) causes the output to drop to 0 mA. So, if the range is 0-20 mA, we can tell if it’s due to a broken wire or 0 psi.

Because two bulbs are connected in series, they will get an identical amount of electrical current. 

However, the supply voltage is constant across the bulb 

(P=V2/R)

As a result, the resistance of a 40W bulb is greater, and the voltage across 40W is greater (V=IR), causing the bulb to glow brighter.

Knee point voltage is determined for electrical current transformers and is a significant consideration in selecting a CT. 

It represents the voltage at which a CT becomes saturated.

Note: (CT = current transformer).

Reverse power flow relays are utilized for generating station protection. A generating station is designed to feed power to the grid; however, if the generating units are turned off and there is no generation in the plant, the plant may draw power from the grid. 

To block the flow of power from the grid to the generator, we employ a reverse power relay.

Free wheeling diode decreases harmonics, sparking, and arching across the mechanical switch, hence reducing the voltage spike seen in an inductive load.

Previous articleWhat is an On-Load Tap Changing Transformer (OLTC)?
Rabert T
As an electrical engineer with 5 years of experience, I focus on transformer and circuit breaker reliability in 110/33-11kV and 33/11kV substations. I am a professional electrical engineer with experience in transformer service and maintenance. I understand electrical principles and have expertise troubleshooting, repairing, and maintaining transformers, circuit breakers, and testing them.