HV – High Voltage Cable Sizing Calculator

0
2100
HV - High Voltage Cable Sizing Calculator

Sizing high voltage cables involves determining the proper parameters for cables used to carry or distribute power at high voltages.

  • Voltage rating,
  • Current carrying capability,
  • Insulation type,
  • Conductor material,
  • Environmental conditions, and
  • Regulatory criteria

are all taken into consideration. Proper size enables safe & efficient transmission while reducing losses and preserving system reliability.

When calculating the cross sectional area of a high-voltage cable, the result found using the following formula:

S = (ISC X √t ) / K

Where,

S – The conductor’s nominal cross-sectional area in mm2

ISC – Short circuit current or fault current value in KA

T – Fault clearing time in seconds

K – Factor based on conductor material resistivity, temperature co-efficient, heat capacity, initial and final temperature.

BS 7671 defines K as

  • 0.094 for XLPE-insulated Aluminium cables,
  • 0.143 for Copper cables, and
  • 0.076 for PVC-Insulated Aluminium cables.

When the formula yields a non-standard size, a conductor with the next higher standard cross section area must be utilized.

The short circuit duration for cables should correspond to the tripping time of the feeder’s protection devices.

Click here for more Electrical Calculators

You can also follow us on Facebook and Linkedin to receive daily updates.