Table of Contents
Purpose
This procedure is designed to conduct a systematic series of pre-commissioning tests on isolators to make sure the equipment’s functionality and health.
Scope
The pre-commissioning test for isolators is addressed in this procedure, as follows:
- Insulation Resistance Test
- Contact Resistance Test
- Infrared Test of Isolator Motor Winding
Responsibility
Unit Heads/Regional Managers
- Planning and scheduling of activities to ensure the successful execution of the projectÂ
- Identifying and addressing significant health and safety hazardsÂ
- Meeting all legal &Â statutory requirements
- Assist the safety team in conducting the safety training and audit at the sites.Â
- Ensure that all safety rules &Â regulations are adhered to at the work sites.
Site Engineers
- Site engineers responsibilities include reporting any health and safety concerns at work sites to the regional manager, unit head, or safety team.
- Coordinate with customers to obtain and return work permits.Â
- Communicate work content and hazards to working groups through toolbox meetings before each day’s start.Â
- Implement proactive measures to reduce accidents.
- Report incidents in detail.Â
- Use proper PPE.Â
- Maintain job quality without compromising safety.Â
- “Stop Work” for significant safety violations.
Safety Engineers
- Safety engineers responsibilities include ensuring the application of occupational health and safety instructions and procedures.
- Communicate safety rules, regulations, and practices to site engineers, regional managers, and unit heads. – Follow up on audit non-conformances and assist regional managers/unit heads in taking corrective and preventive action.
- Report and investigate incidents and near misses to top management.
- Organize frequent training programs and raise awareness among site engineers and regional managers.
- Conduct daily toolbox discussion sessions to ensure workers are aware of workplace hazards.
- Ensure the use of PPE and safety equipment at work sites.Â
- Report any health and safety issues to the unit head or regional managers. – Provide basic first aid facilities on-site.
- Ensure no harmful acts are undertaken on any site.
- Eliminating harmful conditions on-site promptly.Â
- Issuing safety challans for violations.
Work Activity
Pre-Testing Checks
- Examine the operating status of the ELCB (30 mA).
- Inspect power cable insulation for equipment.
- Ensure that adequate earthing & rubber matting are available on the jobsite.
- Utilize calibrated testing equipment & report calibration results to engineers.
- Check the technician’s insulation hand tools.
- Check test leads for insulation damage.
- Make sure suitable PPE is accessible at the site.
Equipment Required
For IR Test
- Insulation Tester (500 and 5000 V)
- Test Leads.
- Insulated Hand Tools
For Contact Resistance Measurement Test
- This package includes a contact resistance meter with test leads ranging from 200µΩ to 2000µΩ for measuring motor winding resistance.Â
- A multimeter with test leads.
For Motor Insulation Resistance Test
- Insulation resistance tester (500/5000V)/megger
- Test leads.
Test Procedure
Insulation Resistance (IR) Test for Isolators
- Obtain the work permit from the customer.
- Test equipment for zero energy before starting work.
- Place isolators in close positions.
- Connect the megger’s positive lead to the isolator pole.Â
- Connect the earth lead to the ground.Â
- Turn on the megger & press the test button to record the data.
- Connect positive lead to one pole & negative lead to another while isolator is open.Â
- Turn ON the megger.Â
- Inject the voltage &Â record the readings.
Motor Winding IR Test (with 500V Megger)
IR Test from Phase to Phase
- Connect the megger to the motor terminals “U1 & V1”.Â
- Turn on the megger and click the test button to record the data.
- Discharge potential from “U1 & V1” terminal to earth.Â
- Turn off the megger.Â
- Repeat for remaining terminals (V1 & W1 and W1 & U1).
IR Test between Phases and Earth
- Shorten the motor terminals (U2, V2, and W2).Â
- Connect the megger to the motor terminal “U1” and Earth.Â
- Turn on the megger and click the test button to record the data.
- Discharge potential from “U1” terminal to earth.Â
- Turn off the megger.Â
- Repeat for other terminals (V1 and W1).
Contact Resistance Measurement Test
- Obtain work permit from customer.
- Test equipment for zero energy before starting work.
- Connect CRM kit to Isolators’ moving and fixed contacts when they are closed.
- To test the CRM kit, turn it on and click the test button.Â
- Record the readings.
- Connect the CRM kit to the connectors of the isolators when they are open.
- Turn on the CRM kit, test the press button, and record the readings.
Control Measures
- Testing engineers provide OCP (Over Current Protection)Â for IR & CRM for Isolators.
- Make sure PTW system in place for the specific bay.
- Make sure all equipment is turned off.Â
- No unauthorized individuals should be allowed to enter the testing area.Â
- Use warning tape to barricade the area.Â
- Use a normal insulated ladder for heights less than 2 meters.
- Inspect ladders before work.Â
- Keep both feet below the third rung from the top.Â
- Use one hand on the ladder at all times.Â
- Proper supervision, including job-specific toolbox meetings and barricades.
- To ensure safety, utilize calibrated equipment, insulated hand tools, avoid power cable joints, and supply via ELCB.Â
- Avoid working alone and wear proper insulated gloves.
Final Check & Restoration of Work
- Disconnect the temporary supply & remove barricades.Â
- Remove any unsecured tools from the area.Â
- Maintain a tidy and clean environment after leaving.