Nuclear Power Plant Electrical Engineer Interview Questions

0
17
Nuclear Power Plant Electrical Engineer Interview Questions
Nuclear Power Plant Electrical Engineer Interview Questions

The generator uses electromagnetic induction to transform the steam turbine’s mechanical energy into electrical energy.

  • Unit auxiliary transformers (UAT), 
  • Station transformers, & 
  • Switchgear 

provide power to auxiliaries and the grid.

  • Metal-clad, 
  • Gas-insulated (GIS), & 
  • Air-insulated switchgear (AIS) 

are commonly employed based on voltage levels and reliability requirements.

Class 1E systems are electrical systems that ensure the plant’s safe shutdown & emergency operations.

  • Differential protection, overcurrent relays, 
  • Earth fault, under/overvoltage relays, &
  • Reverse power relays 

are frequently employed.

During power outages, the UPS delivers continuous DC/AC power to important instruments and control equipment.

Redundancy guarantees that safety systems continue to operate without interruption, preventing failure during grid outages (or) internal failures.

The Primary Electrical Components of a Nuclear Reactor Building includes

  • MCCs, 
  • Motor drives, 
  • Control cables, 
  • Transformers, 
  • Lighting, 
  • Grounding, and 
  • Instrument panels.

Grounding provides fault current paths, protects personnel, & guarantees that protective systems operate correctly.

VRLA (or) Ni-Cd batteries are employed due to their dependability, lengthy backup time, & low maintenance.

They provide mechanical support & routing for power, control, & instrumentation cables while ensuring fire zones and isolation.

Nuclear plant ensure the integrity of its cable insulation using megger testing, high-potential testing (Hi-Pot), & insulation resistance monitoring.

An MCC is a centralized system that manages several electric motors and comprises starters, overload relays, & breakers.

Transformers tested in nuclear power plants Includes 

  • IR testing, 
  • Turns ratio testing, 
  • Vector group verification, 
  • Oil testing, and 
  • Temperature increase testing.

EDGs offer backup power to safety-related systems in the case of a grid breakdown or blackout.

Motors classified in nuclear plants according to its application (safety-related or not), enclosure type (TEFC, WP), & voltage rating.

Servo (or) stepper motors with position feedback are used for accurately positioning valves.

CTs & PTs are used for metering & protection, reducing high voltage/current to quantifiable values.

RPS monitors reactor conditions and executes a safe shutdown in abnormal situations, using Class 1E systems.

IEEE, IEC, and NRC regulations govern the design, testing, & maintenance of electrical systems in the nuclear plants.

To ensure electrical isolation during maintenance: 

  • By implementing Lockout/Tagout (LOTO) procedures, 
  • Isolators, and 
  • Validating the absence of voltage.

The function of the primary transformer in a nuclear power plant is to increases the voltage generated by the generator to transmission levels for grid distribution.

A TN-S or TT system with mesh and rod earthing is used to protect equipment, neutral, and lightning.

In critical zones, normal, emergency, & task lighting systems are installed.

Ex: LED (or) explosion-proof fixtures.

Arc flash is a high-energy failure that causes an explosion; it is minimized by 

  • Arc-resistant gear, 
  • Relays, 
  • Personal protective equipment (ppe), and 
  • Maintenance practices.