What is Overload Current?
Overload current is the current that flows through a motor (or) electrical equipment when it is operated above its rated capacity for an extended length of time.
It frequently exceeds the Full Load Current (FLC) while being below short-circuit limits.
If not appropriately handled, it may result in:
- Overheating,
- Insulation deterioration,
- Reduced equipment life,
- Unnecessary journey (or) failure.
Why do you need a Calculator for Overload Current?
When choosing protective equipment like:
- Thermal Overload Relays
- Circuit Breakers to protect Motors
- Contactors (or) Fuses
Accurately determining the Overload Current (OLC) is essential for effective protection and minimizing disturbance trips.
Using common methods, this calculator allows you to rapidly determine the optimum overload setting.
Overload Current Formula
OLC = FLC x (RS/100)
Where,
OLC – Overload Current,
FLC – Full Load Current
RS – Rated Service Factor (RS)
Points to Remember
- FLC – Current drawn at full load (100%)
- RS – The motor manufacturer suggests a safety (or) service factor (1.0–1.25).
This result can be used to:
- The motor control centers should be configured with overload relays.
- Determine the appropriate contactor ratings.
- Motor Protection Circuit Breakers (MPCBs) should be fine-tuned properly.
- Using SCADA, you may set alarm thresholds.
Advantages of using Calculators
- Prevents manual calculating errors.
- Saves engineering time during design and troubleshooting.
- Ensures equipment protection & compliance.
- Can be included in motor starter selecting tools and mobile apps.
Overload Current Reference Chart
| Motor Power (kW) | Voltage (V) | FLC (A) | Service Factor (RS) | OLC (A) |
| 5.5 kW | 415 V | 11 A | 1.15 | 12.65 A |
| 15 kW | 415 V | 28 A | 1.2 | 33.6 A |
| 30 kW | 415 V | 57 A | 1.15 | 65.55 A |
| 75 kW | 415 V | 140 A | 1.1 | 154 A |
Note: FLC varies depending on the motor efficiency, speed, & type (IE2, IE3, etc.).
Standards & References
- IEC 60947-4-1: Low-Voltage (LV) switchgear & control gear – contactors & motor starters.
- IEEE Standard 242: Protecting & Coordinating the Industrial & Commercial Power Systems.
- NEMA MG1: Motor & Generator Standards (RS values).
- IS 12615: Energy-Efficient Induction Motors.
Solved Example
How do you calculate the Overload Current (OLC) for a motor with a Full Load Current (FLC) of 40 amps and a Rated Service Factor (RS) of 115%?
Given
Full Load Current (FLC) = 40 A
Rated Service Factor (RS) = 115%
Formula
Overload Current (OLC) = FLC x (RS/100)
Solution
Overload Current (OLC) = FLC x (RS/100)
Overload Current (OLC) = 40 x (115/100)
Overload Current (OLC) = 40 x 115/100
Overload Current (OLC) = 40×1.15 = 46 A
Answer
The computed Overload Current (OLC) is 46 Amps.
To eliminate nuisance tripping and ensure safe operation, the overload protection relay (or) breaker should operate at 46 A after a suitable time delay.
FAQ’s
1). What is the importance of calculating Overload Current in the Electrical Systems?
Calculating overload current is essential for planning & protecting the electrical systems.
It assist in choosing of the appropriate size of the
- Circuit breakers,
- Fuses, and
- Additional protective devices
to prevent equipment damage and ensure safety from fire threats caused by high current.
2). How does the Relay setting affect the computation of Overload Current?
The relay setting, stated as a percentage, specifies the threshold that triggers the relay will trip to safeguard the circuit from overload.
A higher level of relay setting allows for the higher load current before tripping, that can be beneficial in applications requiring high start-up currents but may increase the danger of damage under extended overload conditions.
3). Can Overload Current (OLC) calculations be used for any type of Electrical Circuit?
Yes, overload current (OLC) calculations can be applied to a wide range of electrical circuits, which includes residential, commercial, & industrial systems.
However, the specific factors and considerations may differ based on the circuit’s complexity, the type of the load, & the regulatory regulations governing the installation.
Applications of Over Load Current Calculator
- Overload current calculations assist in determining the appropriate size & rating for protective devices such as circuit breakers & fuses.
- Protecting motors from high current to avoid overheating and damage.
- Transformer safety refers to protecting transformers from the overload conditions in order to ensure reliability and longevity.