Symmetrical vs Asymmetrical Fault Currents (IEC 60909 Standard)

0
1452
Symmetrical vs Asymmetrical Fault Currents (IEC 60909 Standard)
Symmetrical vs Asymmetrical Fault Currents (IEC 60909 Standard)

Short-circuit currents are important considerations in power system design, protection, and equipment specifications. 

When a fault occurs, such as a 

  • Line-to-Line Fault or 
  • Line-to-Ground Fault 

there are no simple & uniform waveforms associated with the current.

Instead, it is made up of complicated components that vary with time. These are generically classified as 

  • Symmetrical short-circuit currents & 
  • Asymmetrical short-circuit currents, 

with different characteristics in electrical engineering applications.

International standards such as 

  • IEC 60909 and 
  • IEEE 141/399 

define these currents exactly for their accurate short-circuit diagnosis, resulting in safety and effectiveness in the system operation. 

Understanding the fundamental difference between these 2 types is essential for:

  • Selecting the suitable breaker ratings.
  • Performing accurate and reliable relay coordination.
  • Defining the resist capability of the cables, busbars & other switchgear.

Symmetrical short-circuit current (Ik) is the RMS value of the entire alternating current (AC) component after the transient DC component has got dissipated.

Symmetrical Short-Circuit Current
Symmetrical Short-Circuit Current

Characteristics:

  • A pure sinusoidal waveform with the zero axis at its center.
  • Begins with the decline of the exponential DC offset, which typically takes three to five cycles.
  • Constant in size while the fault condition is steady-state.

Standard:

  • Ik (IEC 60909)
  • IAC (IEEE)

Applications:

  1. Used to coordinate relays, particularly following DC filtering.
  2. Equipment, busbars, and conductors are rated mechanically and thermally.
  3. Determining the available fault MVA in system studies.

The asymmetrical short-circuit current consists of a symmetrical AC component and a DC offset caused by the fault initiation angle and system impedance characteristics.

Asymmetrical Short-Circuit Current (ASC)
Asymmetrical Short-Circuit Current (ASC)

Components:

AC Component: the symmetrical part (Ik).

DC Component: The DC offset is a transient that is non-repetitive and exponentially decreasing. It depends on the following:

  • Fault inception angle
  • System X/R ratio (reaction/resistance)

Magnitudes: 

  • RMS asymmetrical current at 1/2 cycle = 1.6 x Ik
  • Peak asymmetrical current (Ip) = 2.5-2.7 x Ik.

Application: 

  1. Determines breaker making & breaking capacity.
  2. During a fault, magnetic forces act on the equipment.
  3. Specifies the transitory mechanical stress conditions.

The time constant for the DC decay is determined by the system’s L/R ratio, where:

  • L – System Inductance
  • R – System Resistance

It is essential to the safety and dependability of electrical systems to understand the distinction between symmetrical & asymmetrical short-circuit currents; it is not merely academic. 

In the case of a malfunction, the asymmetrical current is responsible for determining the peak stress that occurs within milliseconds. On the other end, the symmetrical current is responsible for determining the long-term current that the equipment must consistently experience.

Symmetrical vs Asymmetrical Fault Currents
Symmetrical vs Asymmetrical Fault Currents

Applications:

  • Asymmetrical peaks must be able to be ignored and eliminated by switchgear in order for it to be considered appropriate.
  • The implementation of symmetrical RMS heating is the objective of conductors and busbars.
  • Protection relays are configured with the help of filtered symmetrical RMS currents during the configuration procedure.

Given the guidelines made by the IEEE and the International Electrotechnical Commission (IEC) 60909, it is therefore necessary to conduct a comprehensive evaluation of both elements in order to design the substation, conduct protection studies, and choose the equipment.