CT Sizing Calculator

0
283
CT Sizing Calculator
CT Sizing Calculator

The CT Sizing Calculator is an online based engineering calculator tool designed for power system protection engineers.

⚡ CT Sizing Calculator

51NS Ground Overcurrent  |  64R Restricted Earth Fault  |  Transformer Secondary Protection

🔵 Core I 51NS — Definite Time Ground O/C
1.1 Basic CT Data
1.2 Connected Burden
🟢 Core II 64R — Restricted Earth Fault
1.1 Transformer & CT Data
1.2 Burden & CT Parameters
🔵 Core I Results — 51NS Definite Time Ground O/C Protection
CT Ratio
Accuracy Class
CT Rated Burden
Step-by-Step Working
Loop Resistance R‹L› = 2 × L(m) × ρ(Ω/km) / 1000
Loop Burden = R‹L› × I²‹sec› (at rated secondary current)
Relay Burden
Total Burden = Loop Burden + Relay Burden
Check: CT Rated Burden ≥ Total Burden?
🟢 Core II Results — 64R Restricted Earth Fault Protection
CT Ratio
Accuracy Class
Step-by-Step Working
Step 1: Max Through Fault MVA = (Transformer MVA × 100) / %Z
Step 2: Fault Current at Primary I‹f› = (Fault MVA × 10⁶) / (√3 × V‹primary›)
Step 3: Fault Current at CT Secondary I‹fs› = I‹f› / CT Ratio
Step 4: Loop Resistance R‹L› = 2 × L(m) × ρ(Ω/km) / 1000
Step 5: CT Internal Resistance R‹ct›
Step 6: Knee Point Voltage V‹k› ≥ 2 × I‹fs› × (R‹ct› + 2R‹L›)
Required Knee Point Voltage V‹k› (calculated)
Project Minimum Specification V‹k›
≥ 500 V
Governing (Adopted) V‹k› for CT procurement

Note: The governing Vk is the higher of the calculated value and the project minimum of 500 V. CT must be specified with Vk equal to or greater than the governing value.

Click here for more Electrical Calculators

It automates the sizing verification of Current Transformers (CTs) connected to the neutral of a power transformer secondary winding.

The calculator evaluates two important protection functions:

• Core I – 51NS: Definite Time Ground Overcurrent Protection

• Core II – 64R: Restricted Earth Fault (REF) Protection

TermDefinition
CTCurrent Transformer – a measuring transformer that produces a reduced secondary current proportional to the primary current.
51NSANSI device number for a time-overcurrent relay applied to the neutral-to-ground current (ground overcurrent, definite or inverse time).
64RANSI device number for a Restricted Earth Fault relay that operates for internal transformer winding faults.
REFRestricted Earth Fault – a high-impedance or low-impedance differential protection scheme sensitive to earth faults within a defined zone.
Knee Point Voltage (Vk)The point on the CT magnetization curve at which a 10% increase in voltage results in a 50% increase in magnetizing current. Required parameter for Class PS/PX CTs.
Class PS / PXIEC accuracy class for protection CTs defined by Vk and Rct, rather than accuracy at rated burden. Used for differential and REF schemes.
RctSecondary winding resistance of the CT, measured at 75°C. A key parameter in knee point voltage calculations.
Through Fault CurrentThe maximum fault current that flows via the CT primary without the fault that is being in the protected zone. Used for stability calculations.
Loop Resistance (RL)The total resistance of the pilot cable circuit including outgoing and return conductors.
%ZTransformer impedance expressed as a percentage of base impedance. Used to calculate maximum through-fault current.

The 51NS function provides definite time overcurrent protection against ground faults by measuring the residual current at the transformer neutral.

The CT should be adequately rated to accurately regenerate the fault current under maximum via fault conditions without saturating.

ParameterUnitDescriptionDefault
CT Primary RatioAPrimary current rating of the CT900 A
CT Secondary RatioASecondary current rating of the CT1 A
Accuracy ClassIEC accuracy class of the CT (e.g., 5P10, 5P20)5P10
CT Rated BurdenVANameplate rated burden of the CT15 VA
IDMT Relay BurdenVAVA burden of the overcurrent relay at rated secondary current0.1 VA
Cable Length (one-way)mOne-way cable route length from CT to relay panel150 m
Cable Sizemm²Cross-sectional area of pilot cable conductors4 mm²
Resistivity at 75°CΩ/kmConductor resistivity at 75°C operating temperature5.41 Ω/km

Loop Resistance Formula:

R‹L› = 2 x L(m) x ρ(Ω/km) ÷ 1000

Factor of 2 accounts for the outgoing and return conductors of the pilot cable loop.

Loop Burden (at rated secondary current):

Loop Burden (VA) = R‹L› (Ω) x I²‹sec›

At rated secondary current (e.g., 1 A or 5 A) and this is the VA drop across the cable resistance.

Total Connected Burden:

Total Burden = Loop Burden + Relay Burden

The CT rated burden must be ≥ Total Burden for the CT to operate within its accuracy class

ConditionResult
CT Rated Burden ≥ Total Burden✔ SAFE – CT is adequately rated
CT Rated Burden < Total Burden✘ NOT SAFE – Select a higher-rated CT or reduce burden

The 64R (Restricted Earth Fault) scheme provides high speed, sensitive protection against internal earth faults in the transformer winding zone bounded by the differential current transformers. 

It uses Class PS (or PX) CTs which must meet a minimum Knee Point Voltage (Vk) to maintain stability under maximum through-fault current.

ParameterUnitDescriptionDefault
CT Primary RatioAPrimary current rating of the CT900 A
CT Secondary RatioASecondary current rating of the CT1 A
Primary VoltagekVTransformer primary (HV) winding voltage33 kV
Secondary VoltagekVTransformer secondary (LV) winding voltage6.6 kV
Transformer RatingMVATransformer nameplate MVA rating8 MVA
Transformer Impedance%ZPositive sequence impedance as percentage8.35%
Accuracy ClassMust be Class PS or PX for REF schemesPS
REF Relay BurdenVAVA burden of the REF relay1.0 VA
Cable Length (one-way)mOne-way pilot cable route length150 m
Cable Sizemm²Pilot cable conductor cross-section4 mm²
Resistivity at 75°CΩ/kmConductor resistivity5.41 Ω/km
CT Secondary Resistance RctΩInternal winding resistance of CT secondary2 Ω

Through-Fault MVA:

Fault MVA = (Transformer MVA x 100) ÷ %Z

Represents the maximum short-circuit power that can flow through the transformer.

Primary Fault Current:

I‹f› = (Fault MVA x 10) ÷ (√3 x V‹primary›)

Three phase fault current referred to the transformer primary (HV) side.

Secondary Fault Current:

I‹fs› = I‹f(primary)› ÷ CT Ratio

Cross-check: (Fault MVA x 10) ÷ (√3 x V‹secondary› x CT Ratio)

Loop Resistance:

R‹L› = 2 x L(m) x ρ(Ω/km) ÷ 1000

Knee Point Voltage Formula (IEC 60044-1 / BS 3938):

V‹k› ≥ 2 x I‹fs› x (R‹ct› + 2 x R‹L›)

The factor of 2 provides stability margin. 

The factor 2xR‹L› accounts for the outgoing and return leads.

The governing (adopted) Vk for CT procurement is the higher of:

  • The calculated Vk from Step 5, and
  • The project minimum specification (typically ≥ 500 V)

Governing Vk = max(Calculated Vk, Project Minimum Vk)

Vk‹govern› = max(V‹k(calc)›, 500 V)

The CT should be procured with a Vk equal to or > the governing value.

SymbolDescriptionUnit
RpCT primary ratio (rated current)A
RsCT secondary ratio (rated current)A
ρConductor resistivity at 75°C (Cu: 5.41 Ω/km; Al: 8.93 Ω/km)Ω/km
LOne-way cable length from CT to relaym
R‹L›Pilot cable loop resistance = 2 × L × ρ / 1000Ω
RctCT secondary winding resistance (Class PS requirement)Ω
V‹k›CT knee point voltage (Class PS specification parameter)V
MVATransformer nameplate MVA ratingMVA
%ZTransformer positive sequence impedance%
V‹p›Transformer primary (HV) voltage (line-to-line)kV
V‹s›Transformer secondary (LV) voltage (line-to-line)kV
I‹f›Maximum through-fault current at primaryA
I‹fs›Maximum through-fault current at CT secondaryA
StandardTitleRelevance
IEC 60044-1Instrument Transformers: Current TransformersCT accuracy classes 5P, 10P, PS
IEC 61869-2Additional requirements for current transformersClass PX definition (replaces IEC 60044-1)
BS 3938Specification for Current TransformersClass X (Knee Point Voltage) definition
IEC 60255Measuring relays and protection equipmentRelay burden and performance
ANSI/IEEE C37.110Guide for the Application of CTs used for PRMCT sizing methodology
IEEE C37.91Guide for Protecting Power TransformersREF protection philosophy