Calculator
The CT Sizing Calculator is an online based engineering calculator tool designed for power system protection engineers.
⚡ CT Sizing Calculator
51NS Ground Overcurrent | 64R Restricted Earth Fault | Transformer Secondary Protection
Note: The governing Vk is the higher of the calculated value and the project minimum of 500 V. CT must be specified with Vk equal to or greater than the governing value.
Click here for more Electrical Calculators
It automates the sizing verification of Current Transformers (CTs) connected to the neutral of a power transformer secondary winding.
The calculator evaluates two important protection functions:
• Core I – 51NS: Definite Time Ground Overcurrent Protection
• Core II – 64R: Restricted Earth Fault (REF) Protection
Terms
| Term | Definition |
|---|---|
| CT | Current Transformer – a measuring transformer that produces a reduced secondary current proportional to the primary current. |
| 51NS | ANSI device number for a time-overcurrent relay applied to the neutral-to-ground current (ground overcurrent, definite or inverse time). |
| 64R | ANSI device number for a Restricted Earth Fault relay that operates for internal transformer winding faults. |
| REF | Restricted Earth Fault – a high-impedance or low-impedance differential protection scheme sensitive to earth faults within a defined zone. |
| Knee Point Voltage (Vk) | The point on the CT magnetization curve at which a 10% increase in voltage results in a 50% increase in magnetizing current. Required parameter for Class PS/PX CTs. |
| Class PS / PX | IEC accuracy class for protection CTs defined by Vk and Rct, rather than accuracy at rated burden. Used for differential and REF schemes. |
| Rct | Secondary winding resistance of the CT, measured at 75°C. A key parameter in knee point voltage calculations. |
| Through Fault Current | The maximum fault current that flows via the CT primary without the fault that is being in the protected zone. Used for stability calculations. |
| Loop Resistance (RL) | The total resistance of the pilot cable circuit including outgoing and return conductors. |
| %Z | Transformer impedance expressed as a percentage of base impedance. Used to calculate maximum through-fault current. |
Core I: 51NS Definite Time Ground Overcurrent
Purpose
The 51NS function provides definite time overcurrent protection against ground faults by measuring the residual current at the transformer neutral.
The CT should be adequately rated to accurately regenerate the fault current under maximum via fault conditions without saturating.
Input Parameters
| Parameter | Unit | Description | Default |
|---|---|---|---|
| CT Primary Ratio | A | Primary current rating of the CT | 900 A |
| CT Secondary Ratio | A | Secondary current rating of the CT | 1 A |
| Accuracy Class | – | IEC accuracy class of the CT (e.g., 5P10, 5P20) | 5P10 |
| CT Rated Burden | VA | Nameplate rated burden of the CT | 15 VA |
| IDMT Relay Burden | VA | VA burden of the overcurrent relay at rated secondary current | 0.1 VA |
| Cable Length (one-way) | m | One-way cable route length from CT to relay panel | 150 m |
| Cable Size | mm² | Cross-sectional area of pilot cable conductors | 4 mm² |
| Resistivity at 75°C | Ω/km | Conductor resistivity at 75°C operating temperature | 5.41 Ω/km |
Calculation Procedure
Step-1: Loop Resistance
Loop Resistance Formula:
R‹L› = 2 x L(m) x ρ(Ω/km) ÷ 1000
Factor of 2 accounts for the outgoing and return conductors of the pilot cable loop.
Step-2: Loop Burden
Loop Burden (at rated secondary current):
Loop Burden (VA) = R‹L› (Ω) x I²‹sec›
At rated secondary current (e.g., 1 A or 5 A) and this is the VA drop across the cable resistance.
Step-3: Total Burden & Safety Check
Total Connected Burden:
Total Burden = Loop Burden + Relay Burden
The CT rated burden must be ≥ Total Burden for the CT to operate within its accuracy class
| Condition | Result |
|---|---|
| CT Rated Burden ≥ Total Burden | ✔ SAFE – CT is adequately rated |
| CT Rated Burden < Total Burden | ✘ NOT SAFE – Select a higher-rated CT or reduce burden |
Core II: 64R Restricted Earth Fault Protection
Purpose
The 64R (Restricted Earth Fault) scheme provides high speed, sensitive protection against internal earth faults in the transformer winding zone bounded by the differential current transformers.
It uses Class PS (or PX) CTs which must meet a minimum Knee Point Voltage (Vk) to maintain stability under maximum through-fault current.
Input Parameters
| Parameter | Unit | Description | Default |
|---|---|---|---|
| CT Primary Ratio | A | Primary current rating of the CT | 900 A |
| CT Secondary Ratio | A | Secondary current rating of the CT | 1 A |
| Primary Voltage | kV | Transformer primary (HV) winding voltage | 33 kV |
| Secondary Voltage | kV | Transformer secondary (LV) winding voltage | 6.6 kV |
| Transformer Rating | MVA | Transformer nameplate MVA rating | 8 MVA |
| Transformer Impedance | %Z | Positive sequence impedance as percentage | 8.35% |
| Accuracy Class | – | Must be Class PS or PX for REF schemes | PS |
| REF Relay Burden | VA | VA burden of the REF relay | 1.0 VA |
| Cable Length (one-way) | m | One-way pilot cable route length | 150 m |
| Cable Size | mm² | Pilot cable conductor cross-section | 4 mm² |
| Resistivity at 75°C | Ω/km | Conductor resistivity | 5.41 Ω/km |
| CT Secondary Resistance Rct | Ω | Internal winding resistance of CT secondary | 2 Ω |
Calculation Procedure
Step-1: Maximum Through-Fault MVA
Through-Fault MVA:
Fault MVA = (Transformer MVA x 100) ÷ %Z
Represents the maximum short-circuit power that can flow through the transformer.
Step-2: Through Fault Current at Primary
Primary Fault Current:
I‹f› = (Fault MVA x 10⁶) ÷ (√3 x V‹primary›)
Three phase fault current referred to the transformer primary (HV) side.
Step-3: Fault Current Referred to CT Secondary
Secondary Fault Current:
I‹fs› = I‹f(primary)› ÷ CT Ratio
Cross-check: (Fault MVA x 10⁶) ÷ (√3 x V‹secondary› x CT Ratio)
Step-4: Loop Resistance
Loop Resistance:
R‹L› = 2 x L(m) x ρ(Ω/km) ÷ 1000
Step-5: Required Knee Point Voltage
Knee Point Voltage Formula (IEC 60044-1 / BS 3938):
V‹k› ≥ 2 x I‹fs› x (R‹ct› + 2 x R‹L›)
The factor of 2 provides stability margin.
The factor 2xR‹L› accounts for the outgoing and return leads.
Step-6: Governing Vk
The governing (adopted) Vk for CT procurement is the higher of:
- The calculated Vk from Step 5, and
- The project minimum specification (typically ≥ 500 V)
Governing Vk = max(Calculated Vk, Project Minimum Vk)
Vk‹govern› = max(V‹k(calc)›, 500 V)
The CT should be procured with a Vk equal to or > the governing value.
Input Parameters Quick Reference
| Symbol | Description | Unit |
|---|---|---|
| Rp | CT primary ratio (rated current) | A |
| Rs | CT secondary ratio (rated current) | A |
| ρ | Conductor resistivity at 75°C (Cu: 5.41 Ω/km; Al: 8.93 Ω/km) | Ω/km |
| L | One-way cable length from CT to relay | m |
| R‹L› | Pilot cable loop resistance = 2 × L × ρ / 1000 | Ω |
| Rct | CT secondary winding resistance (Class PS requirement) | Ω |
| V‹k› | CT knee point voltage (Class PS specification parameter) | V |
| MVA | Transformer nameplate MVA rating | MVA |
| %Z | Transformer positive sequence impedance | % |
| V‹p› | Transformer primary (HV) voltage (line-to-line) | kV |
| V‹s› | Transformer secondary (LV) voltage (line-to-line) | kV |
| I‹f› | Maximum through-fault current at primary | A |
| I‹fs› | Maximum through-fault current at CT secondary | A |
Applicable Standards & References
| Standard | Title | Relevance |
|---|---|---|
| IEC 60044-1 | Instrument Transformers: Current Transformers | CT accuracy classes 5P, 10P, PS |
| IEC 61869-2 | Additional requirements for current transformers | Class PX definition (replaces IEC 60044-1) |
| BS 3938 | Specification for Current Transformers | Class X (Knee Point Voltage) definition |
| IEC 60255 | Measuring relays and protection equipment | Relay burden and performance |
| ANSI/IEEE C37.110 | Guide for the Application of CTs used for PRM | CT sizing methodology |
| IEEE C37.91 | Guide for Protecting Power Transformers | REF protection philosophy |