Magnetic Balance Test Procedure for Transformers

0
26
Magnetic Balance Test Procedure for Transformers
Magnetic Balance Test Procedure for Transformers

This Method of Statement (MOS) describes the safe working procedure and technical methodology for conducting the Magnetic Balance Test on the power and distribution transformers prior to energization (or) as part of periodic/commissioning electrical testing. 

The test verifies the integrity and symmetry of the transformer magnetic circuit and confirms the absence of inter turn short circuits (or) winding faults on the High Voltage (HV) and where applicable, the intermediate (XV) and tertiary (YV) windings.

This procedure applies to all power and distribution transformers undergoing commissioning tests, periodic maintenance tests (or) post-repair verification tests at site prior to connection to 

  • Upstream (or) downstream cables, 
  • Bus bars or 
  • Switchgear. 

The scope covers isolation requirements, safety precautions, test equipment, step-by-step test procedure, acceptance criteria and documentation of results for the Magnetic Balance Test conducted in accordance with IEC 60076.

  • IEC 60076-1: Power Transformers – General
  • IEC 60076 (applicable parts) – Test procedures for power transformers
  • IEEE C57.152-2013 – Guide for Diagnostic Field Testing of Fluid-Filled Power Transformers
  • CIGRE Technical Brochure TB445 – Guide on Transformer Intelligent Condition Monitoring
  • Manufacturers Type Test Certificates and Approved Drawings
  • Project-specific Inspection and Test Plan (ITP)
  1. Obtain a valid Permit to Work (PTW) prior to commencement of the test activities.
  2. Before starting the test, disconnect & ground all HV, XV & YV bushing terminal linkages & isolate the transformer from all upstream and downstream connections.
  3. Use an approved voltage detector to confirm de-energized condition & used to apply temporary earths according to site earthing procedures.
  4. Protect the test area & display suitable warning signs.
  5. Ensure all test staff wear proper personal protective equipment (PPE) such as insulated gloves, safety helmets & footwear.
  6. Use calibrated equipment that have only valid calibration certificate.
  7. Discharge all windings to earth before & after each test utilizing a discharge rod.
  8. Do not touch any winding terminal while the supply is energised; switch off & discharge before making (or) altering connections.
S.NoEquipment / InstrumentRemarks
13-Phase AC Supply Source (415 V AC)Calibrated
2Single Phase AC Supply Source (230 V AC)Calibrated
3Digital / Analog AC VoltmetersCalibrated & valid certificate
4Test / Jumper Leads and ConnectorsRated for test voltage
5Earthing Rods and Discharge SticksSafety equipment
6Personal Protective Equipment (PPE)Helmet, gloves & safety shoes

Prior to commencing the Magnetic Balance Test the following conditions shall be verified and confirmed:

  • Both the primary and secondary windings are confirmed free from any connection to cables (or) bus bars.
  • Oil level, gaskets & external condition of the transformer have been visually inspected & found satisfactory.
  • No parallel test activity (e.g. Insulation Resistance / Winding Resistance test) is in progress on the same winding.
  • No specific pre-conditioning (or) pre-check of the transformer is required prior to this test.

The Magnetic Balance Test is conducted to check for imbalance in the transformers magnetic circuit. 

Normal Condition

Under healthy conditions, the sum of the induced voltages in the 2 unexcited limbs will approximately equal the voltage measured across the excited winding. 

Fault Condition

Any significant deviation from this balance may indicate an inter-turn short circuit (or) other winding fault. 

The test is generally performed on the HV winding (1U, 1V, 1W terminals) using a low voltage single-phase (or) three-phase AC supply as follows:

  • Ensure that both the Primary (HV) and Secondary (LV) windings are completely disconnected from any external cables (or) bus bars.
  • Apply a three-phase supply voltage of 415 V AC (or single-phase 230 V AC, as applicable) across terminals 1U and 1V and measure the corresponding induced voltages across 1U-1V, 1V-1W and 1U-1W.
  • Switch off the supply, discharge the windings and repeat the test by applying the voltage across terminals 1V and 1W. Measure & record the corresponding voltages across 1U-1V, 1V-1W and 1U-1W.
  • Switch off the supply, discharge the windings, and repeat the test a third time by applying the voltage across terminals 1U and 1W. Measure and record the corresponding voltages across 1U-1V, 1V-1W and 1U-1W.
  • Observe & record all readings in the prescribed Test Record Format.
  • Switch off and safely discharge the supply upon completion of all 3 test sequences.

The table below summarizes the terminal pairs across which the test supply is applied and the corresponding terminal pairs at which the resulting voltages are measured for each stage of the test.

Supply Applied AcrossTerminals MeasuredWinding Reference
1U – 1V1U-1V, 1V-1W, 1U-1WHV Winding
1V – 1W1U-1V, 1V-1W, 1U-1WHV Winding
1U – 1W1U-1V, 1V-1W, 1U-1WHV Winding

Test set-up (typical): A regulated 415 V AC 3-phase (or 230 V AC single-phase) supply is connected through a suitably rated ammeter and switch to the HV bushing terminals of the transformer under test (1U, 1V, 1W). Voltmeters are connected across the respective terminal pairs to record the induced voltages during each stage of energization as summarized in the table above.

The transformer magnetic circuit is considered to be in a satisfactory and balanced condition if the sum of the two lower induced voltages is approximately equal, within ±5% to the third (higher) measured voltage in each test sequence. 

Any deviation beyond this tolerance shall be investigated further & reported to the site engineer/client representative prior to proceeding with subsequent tests.

All readings shall be recorded in the format below duly signed by the testing engineer & countersigned by the client/consultant representative.

Sl. NoVoltage Applied AcrossV (1U-1V) VoltsV (1V-1W) VoltsV (1U-1W) VoltsResult
11U – 1V
21V – 1W
31U – 1W
  • Record all test data, ambient temperature and humidity at the time of testing.
  • Attach calibration certificates of instruments utilized as an annexure to the test report.
  • Obtain joint sign-off from the testing agency & client/consultant representative on the test format.

The Magnetic Balance Test when carried out in accordance with the procedure outlined above and referenced standards (IEC 60076, IEEE C57.152-2013, CIGRE TB445) provides a reliable preliminary check on the health of the transformer magnetic circuit and winding integrity prior to energization.

Satisfactory results with other routine electrical tests such as Insulation Resistance, Winding Resistance and Turns Ratio tests provide confidence that the transformer is fit for safe energization and service.