Automatic Voltage Regulator (AVR) Inspection Checklist

0
12
Automatic Voltage Regulator (AVR) Inspection Checklist
Automatic Voltage Regulator (AVR) Inspection Checklist

The Automatic Voltage Regulator (AVR) regulates the excitation current to keep the generator’s voltage output in the required range. A complete inspection of the AVR system is required to ensure its safe and effective operation. 

The inspection activities are described in detail below:

1). Safety Checks

2). Check the Auxiliary Power Supply

3). Power Supply & Excitation Panel Status 

4). Bus Ducts & Cooling systems

5). Check the Carbon Brush & Protection Panel

6). Excitation Transformers

7). MCB (Miniature Circuit Breaker) Function

8). Checks on the Alarm and Display Panels

9). Indications for the LDP & Mimic Panel

10). System Readiness

11). NGT Switch Position

Begin by checking that there are no pending PTWs (Permits to Work) for the equipment. This makes sure the system is safe for operation and that maintenance staff are not jeopardized. In addition, ensure that no one is operating on the machinery to avoid any potential hazards during the inspection.

Check that the Motor Control Center’s (MCC) auxiliary power supply is working properly. This is necessary to ensure that control systems & auxiliary devices function properly.

Ensure all power and control supplies at the excitation panel are functional. An interruption in a power supply may cause the AVR system to malfunction.

To avoid electrical dangers, ensure that all bus duct doors are properly closed. Check the air cooler’s cooling water system to confirm it is operational. Cooling systems are essential for avoiding the excitation system from overheating.

Check that all carbon brush contacts are working properly, as they are crucial to ensuring uniform excitation. Ensure that the generator protection panels (Panels A and B) are receiving appropriate power supply, and that the DC power supply in the Generator Transformer (GT) protection panel is turned on.

Check that the excitation transformer’s cooling fan & temperature monitoring systems are working. It is essential that the excitation transformer doors be firmly closed & that the excitation transformer protection relay (also known as the GT protection relay) function properly.

Examine the PT cubicle MCBs to ensure that they are operational. Similarly, verify all power & control MCBs in the excitation panel to ensure they are working properly, protecting the system from electrical overloads.

Look for any active alarms on the Local Display Panel (LDP). Check the Mimic panel and the Distributed Control System (DCS) for any alarms, as these could indicate an issue with the AVR system. Confirm that the Generator excitation channel’s AVR (CH 01 & CH 02) is in CH 01 mode.

On the LDP, check that the following indicators are correct:

  • CH-1 ON: green
  • AVR on: green
  • EXC OFF – Red
  • FCB OFF: RED
  • REMOTE: yellow

Make that the system is in CH-01 mode, the AVR ON light is illuminated, & the REMOTE lamp is switched off.

After all of the checks have been done and certified as satisfactory, ensure that all systems are operational, and the system is now ready for use.

Finally, make sure the Neutral Ground Transformer (NGT) Switch is closed, which completes the system’s safety tests prior to operation.

This checklist outlines a systematic approach to ensure that the AVR system is operational & that all important safety and performance standards are verified prior to usage.

Previous articleElectrical License Test: Key Questions and Answers
Rabert T
As an electrical engineer with 5 years of experience, I focus on transformer and circuit breaker reliability in 110/33-11kV and 33/11kV substations. I am a professional electrical engineer with experience in transformer service and maintenance. I understand electrical principles and have expertise troubleshooting, repairing, and maintaining transformers, circuit breakers, and testing them.