PurposeÂ
The objective of this procedure statement is to explain the work sequences and procedures that will be used to ensure the proper & safe operation of the RMU and Transformer.
Table of Contents
Scope of Work
Ensure safe operation of RMU & Transformer.
Responsibility
- Project Manager
- Electrical Engineer
- Safety Engineer
ReferenceÂ
- Project specifications & approved drawings.
- Project Quality Plan.
- Health, safety, & environment manual.
Equipment Required
- Ensure all personnel have proper PPE (Personal Protective Equipment).
- Electrical Safety Shoes
- Flame-Resistant Clothing
- Safety Glasses or Goggles
- Insulated Tools
Precaution
Ensure that the RMU & the space surrounding it are free of any impediments for inspection.
Procedure
Visual Inspection
- Visually check the RMU in search for any indications of damage, leakage, or conditions that are not typical.
- Analyze the RMU for any unnecessary objects which may be present.
Switching Operation
- It is important to adhere to the switching sequence that is specified in the operation handbook.
- When working with switches, make sure you use insulated tools.
- Before starting any work, make sure that proper isolation has been arranged.
Earthing
- Before starting any type of maintenance or switching procedures, make sure that the RMU has been properly earthed.
- Determine whether or not the earthing system is operating appropriately.
Normal Voltage | Medium Voltage | Low Voltage | Light Current |
5 Ω | 2 Ω | 2 Ω | 0.5 Ω |
Communication
- Ensure that there is free and open communication with all of the personnel participating in the operation.
- When it comes to coordination, make use of the existing communication protocols.
Operation Steps of RMU
Turn On
- In the direction indicated by the arrow, turn the earthing switch so that it is disconnected.
- It is clear from the second panel that earthing switch is not connected.
- Place the handle on the panel of the circuit breaker & rotate it in the direction of the arrow, which indicates the direction of the energy storage.
- The final step is to finish the process of closing the ring main unit by pushing the green close button located in upper right corner of the screen.
Turn Off
- The first step is to disconnect low-voltage (LV)Â main circuit breaker.Â
- The next step is to click the red stop button that is located in the upper right corner of the circuit breaker.Â
- It has been determined that the circuit breaker has been disconnected, &Â the panel indicator of circuit breaker room has displayed the disconnected state.Â
- The next step is to press the handle into the earthing switch room after inserting it.Â
- The action of disconnecting ring network cabinet is finished when the arrow rotates in the direction of closing, which indicates that the earthing switch has been closed.Â
- The panel also indicates that the earthing switch has been closed.
Power Transmission Procedure
- Verify that the primary load switch on the transformer’s output is off before turning it on.
- Remove the “No Switching On” warning sign and open earthing knife lock.
- To open earthing knife, turn counterclockwise.
- Verify that the earthing indication is in the “floating” or off position.
- The earthing knife lock should be locked.
- Unlock the load knife.
- To close the switch, turn it clockwise.
- Verify the three indication lights’ condition.
- Lock the load knife lock.
Power Failure Operating Procedure
- The transformer’s output total load switch needs to be unplugged before the transformer is turned off.
- Check the three indication lights’ condition.
- Unlock the load knife.
- Manually press the red “OFF” stop button until the switch sounds.
- Verify that all three of the indicator lights are white and not flickering.
- Lock the load knife lock.
- Open the earthing knife lock.
- Close the earthing knife by rotating it clockwise.
- Hang up a warning sign that reads “No Switching On” and make sure the earthing indicator is in earthing state.
- Lock the earthing knife lock.
Emergency Procedure
- In the case that any unusual conditions arise, you should be conversant with the emergency shutdown procedures.
- Every member of the staff should be informed of the protocols for responding to emergencies.
Post Operation Inspection
- Once the process has been finished, it is necessary to perform a visual inspection to ensure that all of the switches are in the appropriate position.
- Ensure that all of the precautionary measures have been carried out in the appropriate manner.
Documentation
- Please make sure to document all of the pertinent information pertaining to the operation, particularly any deviations from standard operating procedure.
- Ensure that records are kept for future use and for the purposes of auditing.
Training
- Make sure that all of the staff who are involved in the RMU operations have received sufficient training and are capable.
- Refresher training courses should be offered on a regular basis in order to emphasize safe operating procedures.
Closure
- Protect the RMU & the area immediately surrounding it.
- Make sure that all of the tools & equipment are stored in the appropriate manner.
- Complete any paperwork or reporting that may otherwise be required.