Circuit Breaker testing is important for keeping electrical systems safe and reliable, and the timing test is sometimes the most useful test you can run. Whether you manage power distribution at a substation, an industrial plant (or) a utility network, recognizing breaker timing is important for
- What is Circuit Breaker Timing Test?
- Circuit Breaker Timing Test Procedure Importance
- 1). Reducing Damage during Faults
- 2). Relay Coordination
- Equipment Requirement
- Required Connections
- Step-by-Step Connections
- Test Procedure
- Accepted Results
- What is the distinction between open & close time in the circuit breaker testing?
- Preventing fault incidence,
- Maintaining equipment &
- Ensuring that the protection system will perform its duty when needed.
In this post, we will look at circuit breaker timing tests, why they are important, how to perform them correctly & what test equipment to use to get the most accurate results.
What is Circuit Breaker Timing Test?
Circuit breaker timing tests determine how long it takes for a breaker’s contacts to open & close when a suitable control signal is received. Timing tests determine how long it takes the breaker to open (or) close upon responding to a trip (or) close order.
The timing test results will assist validate the breaker to ensure that it meets the manufacturer’s standards and trips quickly enough.
This helps isolate failures and protects downstream equipment.
The circuit breaker timing test is one of several maintenance tests that should be performed on a regular basis. It measures the circuit breaker’s mechanical functioning time.
Delays in circuit breaker functioning can have serious consequences for equipment when a fault occurs, making this test crucial.
Operation Time
The circuit breaker’s operation time is defined as the times when the contacts close and open. IEC 56.3.105 defines these operating times as follows.
Closing Time
The period between activating the breaker’s coils (while the CB contacts are open) and the instant the contacts hit each other.
Opening Time
It is the opposite of closing time. It is the time interval involving energizing the trip coil (CB contacts are in open position) & the moment when contacts disengage from it.
Circuit Breaker Timing Test Procedure Importance
Circuit breakers are essential components of any electrical network’s protective system.
The correct operation time is critical for system safety & reliability. The timing test of the circuit breaker is necessary for the following reasons.
1). Reducing Damage during Faults
When a fault occurs, the protective relay senses the abnormal state and issues a trip command to the circuit breaker.
After receiving the signal, the breaker activates its trip coil and opens its connections, isolating the problematic portion from the remainder of the system.
However, this process requires a short but essential amount of time.
Power system components is designed to tolerate fault currents (or) abnormal conditions for a short period of time.
If the circuit breaker fails to work within this time frame, the machine may sustain significant damage (or) perhaps fail completely.
As a result, periodic timing tests are required to guarantee that the breaker operates within minimum time frame, lowering the chance of system damage.
2). Relay Coordination
Circuit breakers are deployed at various locations throughout the power system to offer selected protection.
Ideally, only the problematic section should be separated whereas the healthy parts can continue to operate normally.
This selectivity is attained via relay coordination in which the relay & breaker closest to the problem are configured to trip first.
If that breaker fails to trip within the specified period, the upstream breaker (closer to source) will function instead causing wasteful disconnection of healthy system components.
Accurate circuit breaker activation time is essential for maintaining the relay coordination & isolating only the damaged part.
Equipment Requirement
A circuit breaker’s timing can be tested using a wide range of measuring equipment.

First Generation Devices
Based on the oscillography method of recording curves.
Currently obsolete & not used.
Second Generation Devices
Based on digital timers with time-pulse conversion.
Ex: circuit-breaker timer.
Modern Equipment
Circuit Breaker (CB) Analyzer – Widely used today to execute circuit breaker timing testing.
Required Connections

To conduct a breaker timing test, the subsequent connections must be established:
Input and Output Connections: Connect each circuit breaker phase’s input and output to the Circuit Breaker Analyzer (CBA).
DC Supply: Connect an external DC power source to the breaker’s tripping coil.
Trigger Circuit: Connect the breaker’s tripping circuit to the CBA.
Step-by-Step Connections
Connect the entering terminals of each phase of breaker from the CBA with red, yellow and blue wires.
Connect the outgoing terminals with the black wire.
To power the triggering circuit, connect the positive (+) & negative (-) terminals of an external battery.
Test Procedure
Step-1: After making the connections verify the breaker state indicator to see if the circuit breaker is ON (or) OFF.
Step-3: The test findings can be:
- Printed on a thermal printer.
- Downloaded onto a USB flash drive,
- Viewed on a PC using the USB interface.
Step-4: Repeat the procedure for opening and closing the breaker.

Accepted Results
The manufacturer provides the exact working time (which is usually specified on the nameplate).
As an overall guideline:
High-Tension (HT) breakers (more than 11kV)
- Opening time: 1-2 cycles (20-40 milliseconds)
- Closing time: 2-5 cycles (40-100 milliseconds).
Low-Tension (LT) breakers (below 11kV or 11kV)
- Opening time: 2-3 cycles (40 – 60 milliseconds)
- Closing time: 3-6 cycles (60-120 milliseconds).
These values are approximate and may differ based on the breaker design.
What is the distinction between open & close time in the circuit breaker testing?
The open time is the time between the trip signal and the contact separation, whereas the close time is the time between the close signal and the contact touch.