Bus bars are the essential components in the electrical distribution systems (EDB) serving as primary conductors that carry current between
2). Transformers and
3). Equipment.
Proper sizing is the essential for safety, efficiency and compliance with international electrical codes (IEC).
This post covers all details you required to know about the bus bar sizing and how to use this professional calculation tools to ensure your systems meet IEC 61439 and NEC (NFPA 70) standards.
What is a Busbar?
A bus bar is a strip of copper (or) aluminum metal that conducts the electricity in switchboards and also distribution equipment.
Proper sizing ensures the safe current conduction without any overheating, minimizes the voltage drop, prevents mechanical stress and guarantees the regulatory compliance.
Undersized bus bars can overheat causing
1). Insulation degradation,
2). Fire hazards and
3). Equipment failure.
that is creating hazardous safety risks & liability issues.
Bus Bar Sizing Fundamentals
Current Calculation
For three-phase (3 phase) systems:
I = P / (V x √3 x PF)
Where
P – Power (kW)
V – Voltage (Volts) (V)
PF – Power Factor (typically 0.95)
Safety Factor
Always apply the safety factor (typically 125%) to account for future
1). Load development,
2). Temporary overloads and
3). Manufacturing tolerances.
Design Current = Required Current x 1.25
Material Selection
Copper
Conductivity of 58 MS/m is the best for high current applications that is requiring compact spaces.
Aluminum
Conductivity of 35 MS/m is lighter and also cheaper but needs larger physical dimensions.
IEC 61439/NEC Compliance Standards
IEC 61439 (International Standard) specifies:
1). Current capacity without any exceeding safe operating temperature.
2). Voltage drop limits: Maximum 3%.
3). Temperature rise limits: Maximum 50°C above ambient.
4). Mechanical strength for the short-circuit forces.
NEC Article 366 (United States) requires:
1). Proper ampere ratings suitable for the circuit load.
2). Copper & aluminum conductors that is meeting ASTM standards.
3). Voltage drop not exceeding (<) 3% for feeders and branch circuits.
4). Proper spacing, fire rating and grounding provisions.
Bus Bar Calculation Step-to-Step Procedure
Step-1: Determine the required current (by directly or from power/voltage).
Step-2: Apply the given safety factor [multiply by 1.25(x 1.25)].
Step-3: Calculate the cross-section area based on the conductivity and temperature rise (increase in temperature).
Step-4: Round up to the nearest (close value) standard size (10 mm², 16 mm², 25 mm², 32 mm², 40 mm², 50 mm², 63 mm², 80 mm², 100 mm², 125 mm², 160 mm², 200 mm², 250 mm², 320 mm², 400 mm², 500 mm² and 630 mm²)
Step-5: Determine the width & thickness dimensions.
Step-6: Calculate the voltage drop (VD%) percentage.
Step-7: Verify the thermal (heat) limits.
Step-8: Confirm the compliance with all the applicable standards.
The Bus Bar Size Calculator automates this entire procedure.
Simply enter:
1). Continuous current (or) power (in kW and voltage),
2). Material type (copper or aluminum),
3). Safety factor (adjustable 100-200%) and
4). Maximum temperature rise.
The calculator instantly provides:
1). Design current and cross-section area,
2). Physical dimensions (width & thickness),
3). Voltage drop percentage &
4). Compliance verification (IEC 61439 & NEC standards).
Results used to display as PASS/FAIL indicators for the immediate (quick) compliance assessment.
Common Mistakes
1). Ignoring Safety Factors: Always use to apply 1.25 minimum.
2). Neglecting Voltage Drop: Verify it stays below 3% (< 3%).
3). Wrong Material Selection: Use copper for tight spaces & aluminum for weight concerns.
4). Overlooking Future Loads: Size for development/growth not just current demand.
5). Inadequate Documentation: Record all the calculations for compliance and maintenance.
Practical Example
How to calculate the cross section of copper busbars for a 3 phase, 50 kW, 400 V system?
Solution
Required Current (I) = 50000 / (400 x 1.732 x 0.95) = 75.6A
Design Current (ID) = 75.6 x 1.25 = 94.5A
Cross Section = 25 mm² (Standard Size)
Result
5 x 5mm copper busbar
Conclusion
Proper bus bar sizing ensures a safe, efficient and compliant electrical systems (power system).
Using professional online calculation tools which eliminates manual errors, guarantees standards compliance and also provides professional documentation.
Whether designing the small distribution boards (SDB) (or) large industrial installations the Bus Bar Size Calculator ensures accuracy and confidence in your electrical system design.