Air Circuit Breaker (ACB) Sizing Calculator

0
193
ACB Sizing Calculator
ACB Sizing Calculator

The Air Circuit Breaker (ACB) Sizing Calculator is a online calculator tool designed to assist electrical engineers, panel designers and technical personnel in sizing Air Circuit Breakers (ACBs) for low voltage (LV) power distribution systems.

⚡ ACB Sizing Calculator

Air Circuit Breaker Sizing  |  IEC 60947  /  NEC  /  IS 13947

▶ System Configuration
▶ Load Parameters
▶ Protection & Derating
⚠ Error message here
✓   Calculation Results
Full Load Current (FLC)
Temperature Derating Factor
Altitude Derating Factor
Harmonic Derating Factor
Combined Derating Factor
Derated FLC
Design Current (FLC × multiplier)
⚡ Recommended ACB Rating
ACB Frame Size
Required Breaking Capacity
Overload Relay (LTPU) Setting
Short-Circuit Pickup (STPU)
Ground Fault Protection (GFP)
ACB Utilization Level
⚠ This tool is for preliminary guidance only. All final designs must be verified by a licensed electrical engineer in accordance with applicable standards (IEC 60947 / NEC / IS 13947).

Click here for more Electrical Calculators

You can also follow us on Facebook and Linkedin to receive daily updates.

The calculator supports three international standards:

  • IEC 60947: International Electrotechnical Commission (global)
  • NEC / ANSI: National Electrical Code (North America)
  • IS 13947: Bureau of Indian Standards (India)

It accounts for full load current, system voltage, power factor, efficiency, demand factor, temperature and altitude derating, harmonic distortion, and short-circuit current requirements to get at a properly sized ACB with appropriate protection settings.

The calculator is organised into 3 input sections. 

System Type

Select 3-Phase (Three-Phase AC) (or) 1-Phase (Single-Phase AC). This determines the FLC formula used.

System Voltage (V)

Line-to-line voltage in Volts (e.g. 415 V for Indian/European systems, 480 V for USA).

System Frequency

50 Hz (India/Europe/Asia) (or) 60 Hz (USA/Canada). 

Design Standard

The applicable standard governs naming conventions and recommendations in the output report.

Connected Load / Power (kW)

Total rated load power in kilowatts.

Power Factor (PF)

Ratio of real to apparent power (0.1–1.0). Typical: 0.8–0.9 for industrial loads.

Load / Motor Efficiency (%)

Equipment efficiency (1–100%). Typical motors: 90–96%. Use 100% for resistive loads.

Demand Factor

Ratio of maximum actual demand to installed capacity (0.1–1.0). Use 1.0 for full-load design.

Load Type

It affects the Short-Circuit Pickup (STPU) calculation. Select Motor Load to reveal the starting current factor field.

Motor Starting Current Factor

It is visible only for motor loads. Typical values: 6x for DOL starting and 3x for Star-Delta starting.

Safety Multiplier

It is applied to derated FLC to determine design current. 1.25x is the NEC/IEC standard. Use 1.5x for essential services.

Ambient Temperature (°C)

Make installation as per environment temperature. Derating applies above 40°C: 0.95 at 50°C, 0.90 at 60°C, 0.85 above 60°C.

Installation Altitude (m)

Altitude derating: 0.97 at 1001–2000 m, 0.94 at 2001–3000 m, 0.91 above 3000 m.

Harmonic Derating Factor

It accounts for additional heating due to harmonic currents (0.5–1.0). Use 1.0 if no harmonic analysis is available.

Prospective Short-Circuit Current (kA)

The maximum fault current at the installation point. The ACB should have a breaking capacity equal to or greater than this value.

Reference table of all input parameters:

The calculator selects the next standard rating above the computed design current from the following table:

ACB Rating (A)Frame SizeTypical Application
100 A630A FrameSmall distribution panels
125 A630A FrameSmall distribution panels
160 A630A FrameLV motor control centers
200 A630A FrameLV motor control centers
250 A630A FrameCommercial distribution
315 A630A FrameCommercial distribution
400 A630A FrameIndustrial feeders
500 A630A FrameIndustrial feeders
630 A630A FrameMain LV switchboards
800 A1600A FrameMain LV incomer
1000 A1600A FrameLarge industrial plants
1250 A1600A FrameLarge LV switchgear
1600 A1600A FrameMV/LV transformer secondary
2000 A2500A FrameMain HV/LV switchboards
2500 A2500A FrameGrid substation LV side
3200 A4000A FrameHeavy industry / data centres
4000 A4000A FrameUtility / generation
5000 A6300A FrameExtra-large industrial
Ambient TempDerating FactorRemark
≤ 40°C1.00No derating
41 – 50°C0.955% reduction
51 – 60°C0.9010% reduction
> 60°C0.8515% reduction
AltitudeDerating FactorRemark
≤ 1000 m1.00No derating
1001 – 2000 m0.973% reduction
2001 – 3000 m0.946% reduction
> 3000 m0.919% reduction
ParameterFormula
FLC (3-Phase)P × 1000 ÷ (√3 × V × PF × η × DF)
FLC (1-Phase)P × 1000 ÷ (V × PF × η × DF)
Combined Derating Factor (CDF)Temperature Factor × Altitude Factor × Harmonic Factor
Derated FLCFLC ÷ CDF
Design CurrentDerated FLC × Safety Multiplier
ACB RatingNext standard rating ≥ Design Current
LTPU SettingFLC × 1.05
STPU (General Load)FLC × 10
STPU (Motor Load)FLC × Starting Factor × 1.1
GFP SettingFLC × 0.20
Utilization Level (%)(FLC ÷ ACB Rating) × 100

Note: P is the connected load in kW, V is the line voltage in Volts, PF is the power factor, η (eta) is the efficiency fraction and DF is the demand factor.

Step-1: Full Load Current (FLC) is calculated from the load power, voltage, power factor, efficiency and demand factor.

Step-2: Temperature Derating Factor is determined from the ambient temperature input.

Step-3: Altitude Derating Factor is determined from the installation altitude input.

Step-4: Combined Derating Factor (CDF) is the product of the three individual derating factors.

Step-5: Derated FLC is the FLC divided by the CDF representing the effective current under derated conditions.

Step-6: Design Current is the Derated FLC multiplied by the chosen Safety Multiplier.

Step-7: Recommended ACB Rating is the next standard catalogue rating at or above the design current.

Step-8: Protection settings (LTPU, STPU, GFP) are calculated as multiples of FLC per standard practice.

After clicking Calculate ACB Size the results panel displays all calculated values with a summary recommendation.

Output ParameterDescription
Full Load Current (FLC)Calculated full load current (FLC) in Amperes
Temperature Derating FactorDerating multiplier based on the ambient temperature
Altitude Derating FactorDerating multiplier based on installation altitude
Harmonic Derating FactorUser entered harmonic derating value
Combined Derating FactorProduct of all 3 derating factors
Derated FLCFLC adjusted for all derating conditions
Design CurrentDerated FLC x safety multiplier
Recommended ACB Rating (A)Next standard rating above design current
ACB Frame SizeStandard ACB frame classification
Required Breaking CapacityMinimum short circuit breaking capacity in kA
Overload Relay / LTPU SettingLong-Time Pickup setting (~105% of FLC)
Short-Circuit Pickup (STPU)Short-Time Pickup setting (10x FLC or motor factor)
Ground Fault Protection (GFP)Ground fault pickup (~20% of FLC)
ACB Utilization LevelFLC as percentage of ACB rated current

Utilization Level is flagged with a warning badge if it exceeds 80% indicating the ACB may be undersized for adequate operational margin.

1). Open the ACB Sizing Calculator.

2). Fill in the System Configuration section: select System Type & enter System Voltage.

3). Fill in the Load Parameters section: enter kW, Power Factor, Efficiency & select Load Type.

4). For Motor loads enter the Starting Current Factor (6 for DOL, 3 for Star Delta).

5). Fill in the Protection & Derating section: select the Safety Multiplier, enter Ambient Temperature & Altitude.

6). Select the prospective short circuit current (kA) from the dropdown.

7). Click the "Calculate ACB Size" button.

8). Review the results panel. Note the Recommended ACB Rating, Frame Size and protection settings.

9). If the Utilization Level exceeds 80% consider selecting the next higher ACB rating.

10). Use the "Reset All Fields" button to clear all inputs and start a new calculation.

Size an ACB for a 3 phase, 415 V, 75 kW induction motor (DOL starting), PF = 0.85 and efficiency = 94%, installed in an industrial plant at 45°C ambient, 500 m altitude with no harmonics, SCC = 36 kA.

StepCalculationResult
Full Load Current (FLC)75000 ÷ (√3 × 415 × 0.85 × 0.94 × 1.0)137.6 A
Temperature Derating (45°C)Between 40–50°C → 0.950.95
Altitude Derating (500 m)Below 1000 m → 1.001.00
Harmonic DeratingNo harmonics → 1.001.00
Combined Derating Factor0.95 × 1.00 × 1.000.950
Derated FLC137.6 ÷ 0.95144.8 A
Design Current (×1.25)144.8 × 1.25181.0 A
Recommended ACB RatingNext standard rating ≥ 181 A200 A
ACB Frame Size≤ 630 A630A Frame
LTPU Setting137.6 × 1.05144.5 A
STPU Setting (DOL, 6×)137.6 × 6 × 1.1907.6 A
GFP Setting137.6 × 0.2027.5 A
Utilization Level(137.6 ÷ 200) × 10068.8% ✓ OK

Result: Install a 200 A / 36 kA ACB in a 630A Frame. Set LTPU at 145 A, STPU at 908 A, GFP at 28 A.

This calculator is intended for preliminary guidance only. It does not replace a full engineering study. The following limitations apply:

  1. The tool does not account for cable impedance, upstream protection coordination, or selectivity (discrimination) studies.
  2. Motor starting methods beyond DOL and Star-Delta (e.g. soft starters, VFDs) require separate analysis.
  3. The harmonic derating factor must be determined from a separate power quality study; the tool accepts a user-supplied value only.
  4. Ground fault protection settings shown are indicative; TN, TT and IT system earthing arrangements may require different approaches.
  5. Breaking capacity requirements may be higher when upstream sources can feed fault current independently.
  6. The results are for single-feeder ACB sizing; bus-tie and coupler ACBs require additional selectivity verification.

Points to Remember

All final designs should be verified and approved by a licensed electrical engineer in accordance with applicable local standards and regulations (IEC 60947, NEC, IS 13947 or equivalent). 

StandardTitleScope
IEC 60947-2Low-Voltage Switchgear & Control gear - Part 2: Circuit BreakersInternational standard for LV circuit breakers
NEC (NFPA 70)National Electrical CodeUSA electrical installations
ANSI / IEEE C37Switchgear StandardsUSA switchgear ratings
IS 13947-2Low Voltage Switchgear & Control gearIndian equivalent of IEC 60947
IEC 60364Low Voltage Electrical InstallationsInstallation wiring & protection