Amp to KVA Calculator

Published on

Single phase amps to KVA calculation:

The apparent power, in kilovolt-amperes (KVA), is calculated by multiplying the voltage, in volts (V), by the current, in amperes (A), and dividing by 1000.

KVA = I x V/1000

3 phase amps to KVA calculation:

Calculation with Line to Line voltage:

Kilovolt-amps equals phase current I in amps times line-to-line RMS voltage VL-L in volts divided by 1000.

KVA = √3 × I × VL-L / 1000

Calculation with Line to Neutral voltage:

Kilovolt-amps equals phase current I in amps times line-to-neutral RMS voltage VL-N in volts divided by 1000.

KVA = 3 × I × VL-N / 1000

Click here for more Electrical Calculators

Latest articles

Troubleshooting MCC and Starter Panels: Common Faults and Fixes (Diagnosis)

Table of ContentsMethods for the Fault Diagnosis1). Phase indicator2). Outgoing Terminal3). Metering Circuits4). Ammeter5)....

Cable Tray Dimensions and Specifications as per NEC

Table of ContentsPurpose of Cable TraysCable Tray norms as per National Electrical Code (NEC)Number...

Understanding the Operational Modes of Industrial UPS Systems

Table of ContentsHow many modes are there in UPS?Single line diagram of UPSNormal operation...

A Step-by-Step guide to run a Three-Phase Motor on Single-Phase Supply using VFD

Table of ContentsConverting Three-Phase Motors: A VFD Solution for Single-Phase PowerFunction of VFDRequired ComponentsHow...

More like this

Troubleshooting MCC and Starter Panels: Common Faults and Fixes (Diagnosis)

Table of ContentsMethods for the Fault Diagnosis1). Phase indicator2). Outgoing Terminal3). Metering Circuits4). Ammeter5)....

Cable Tray Dimensions and Specifications as per NEC

Table of ContentsPurpose of Cable TraysCable Tray norms as per National Electrical Code (NEC)Number...

Understanding the Operational Modes of Industrial UPS Systems

Table of ContentsHow many modes are there in UPS?Single line diagram of UPSNormal operation...