Earthing Interview Questions and Answers

0
1153
Earthing Interview Questions and Answers
Earthing Interview Questions and Answers

Earthing is the technique of connecting non-current carrying elements of electrical equipment or systems to the ground in order to assure safety by discharging fault current into the earth.

The earthing is necessary to:

  • Protects individuals from electric shock.
  • Protects electrical devices from damage during a fault.
  • Assists in the proper operation of the protection systems.

The different types of earthing are:

  • Plate Earthing
  • Pipe Earthing
  • Rod Earthing
  • Strip Earthing
  • Chemical Earthing

The standard value for earth resistance are

  • Power stations and grid substations: < 0.5 Ohm.
  • Major substation: ≤1 ohm.
  • Small substation (≤ 2 ohm)
  • Residential: ≤ 5 Ohm.

The variables that influence earth resistance are:

  • Soil resistivity
  • Moisture content
  • Temperature
  • Depth of electrode
  • Type & size of electrodes

Soil resistivity is the soil’s resistance to the flow of electric current. It is measured in Ohm-meters (Ω·m).

Using an Earth Tester/Megger (3- or 4-point technique).

Neutral is grounded via a high resistance to limit fault current (often utilized in industrial systems).

The function of an earth electrode is to creates a low-resistance path for fault current to safely enter the ground.

Chemical earthing use a salt, bentonite (or) conductive compound mixture to reduce resistance and increase conductivity surrounding the electrode.

  • TT system: Neutral earthed; consumer has independent earthing.
  • TN system: The neutral and protective earths are related.
  • IT system: Neutral isolation or impedance-based connection.

The purpose of Grounding in Lightning Protection is to properly discharge lightning surges into the earth while also protecting equipment and buildings.

The material utilized for Earthing Electrodes are

  • Copper
  • Galvanized iron (GI)
  • Stainless Steel

The depth of an earth electrode is generally between 2.5 and 3 meters depending on soil conditions and requirements.

R= ρ​/2πL

Where

ρ – Soil Resistivity (Ω/m)

L – Rod Length (Meters)

d – Rod Diameter (Meters)

The purpose of a ground mat (or) earth grid is to equalize potential and lower step and touch voltages in substations.

They increase soil conductivity while maintaining low resistance around the electrode.

Multiple Earthing occur to lower earth resistance while improving grounding reliability.

Earthing Conductor is a conductor that links the equipment body to the ground electrode.

When a live conductor unintentionally makes touch with the earth or a grounded component is called as ground fault.

The maximum safe touch voltage is 50 V AC (in dry conditions).

  • Increase the electrode depth.
  • Connect many electrodes in parallel.
  • Improve soil conductivity (salt, charcoal, and chemical compounds).

Mesh Voltage

Mesh voltage refers to the maximum touch potential within the substation ground grid.

Step Voltage

Step voltage is the potential difference between steps of a person strolling in the yard during a fault.