Electrical QA/QC Inspector Interview Question Answers

0
42
Electrical QA/QC Inspector Interview Question Answers
Electrical QA/QC Inspector Interview Question Answers

The tests performed on an electrical cable are the Insulation Resistance (IR) Test and the Continuity Test. 

For medium voltage (MV) cables, a Hi-Pot Test is additionally performed.

A wire is a single conductor that carries a signal, whereas a cable is a bundle of two or more wires that are surrounded and protected by an insulation sheath.

A cable is made up of the conductor, insulation, inner sheath, armor, and PVC outer sheath.

XLPE (Cross-Linked Polyethylene) insulated cables are used for both High Tension (HT) and Low Tension (LT) applications whereas PVC (Polyvinyl Chloride) insulated cables are used only for Low Tension (LT) applications.

The two international standards for cables are the 

As per SAES-P-104, the temperature rating for a cable is 90% dry and 75% wet for a 600V NEC-rated cable, and 85% for a 450/750V IEC-rated cable with 70% for IEC-rated cables in wet conditions.

Armored cables and metal-clad cables can be used in exposed locations because they provide mechanical protection against physical damage.

  • Low Voltage (LV) cables are rated below 1kV while 
  • Medium Voltage (MV) cables are rated below 35kV.

The SAMSS reference for a power cable is 15-SAMSS-502.

The SAES reference for a power cable is SAES-P-104.

As per the Pre-Commissioning Form, the test voltage injected is 

  • 500V for cables rated 100–250V, 
  • 1000V for cables rated 251–600V, 
  • 2500V for cables rated 601–5000V and 
  • 5000V for cables rated over 5000V.

DC voltage is injected for one minute for LV cables (1kV) and for MV cables (5kV) while the Hi-Pot test is carried out for 15 minutes in order to check the condition of the cable insulation.

The minimum acceptable resistance value for the LV test is 50 megaohms as per the NETA ATS standard.

DC is used for the megger test because AC does not give an accurate insulation resistance value whereas DC provides a stable and accurate reading.

The main components of a megger device are the 

  • Digital meter, 
  • Wire leads, 
  • Discharge stick and 
  • Selection switch.

As per NEC Article 300, the maximum bend radius is 8 times the cable diameter for non-shielded cables and 12 times the cable diameter for shielded cables.

For AC power cables, the color coding is black and white while for DC power cables, the color coding is red and white.

The cable size is selected as per SAES-P-104, Table 1.

The cable is tested twice using the megger test and once using the Hi-Pot test.

The tests required for a transformer during pre-commissioning are the 

  • Winding Resistance Test, 
  • Winding Insulation Test, 
  • Turn Ratio Test, 
  • Polarization Index (PI) Test, 
  • Tap Changer Setting Check, 
  • Phase-to-Phase Distance Check, 
  • Lightning Arrestor Test and
  • Core-to-Ground and Tank-to-Ground Test, 

Pressure Relief Device Check and a tightness check of all connections as per the manufacturer’s recommendations.

The PI test is the ratio of the insulation resistance (IR) measured at 10 minutes to the insulation resistance measured at 1 minute during a megger test. 

PI test is performed to assess the dryness and overall condition of the cable insulation; a PI value greater than 2 (PI Value >2) is generally considered a good indication of healthy insulation.

A cable fault locator test is performed to identify the exact location of a fault, such as an open circuit, short circuit (or) earth fault along the cable route that is typically using a Time Domain Reflectometer (TDR) (or) a similar fault locating device.

Before performing a Hi-Pot test, the cable must be fully isolated from the system and both ends should be properly discharged and grounded before and after the test, personnel should be kept clear of the test area and appropriate PPE along with warning signs and barricades should be used.

As per IEC standards, three phase cable cores are typically identified using Brown, Black, and Grey for the three phases (L1, L2, L3), Blue for the neutral conductor & Green/Yellow for the earth conductor.

Shielded CableUnshielded Cable
A shielded cable has a metallic screen, such as a copper tape or braid, wrapped around the insulation to block electromagnetic interference and to provide a controlled path for fault (or) leakage current; such cables are commonly used for MV applications. An unshielded cable does not have this metallic screen and is generally used for LV applications where interference and fault-current control are less essential.