Electrical Testing of Gas Insulated Switchgear (GIS) in High Voltage (HV) Substations

0
221
Electrical Testing of Gas Insulated Switchgear (GIS) in High Voltage (HV) Substations
Electrical Testing of Gas Insulated Switchgear (GIS) in High Voltage (HV) Substations

Electrical testing of (GIS) Gas Insulated Switchgear is essential for ensuring operational safety, dielectric integrity, dependability and conformity with international standards. 

Testing is typically carried out during:

• Factory Acceptance Testing (FAT),

• Site Acceptance Testing (SAT),

• Commissioning and

• Periodic Maintenance.

The primary applicable standards include:

• IEC 62271-203,

• IEC 60270,

• IEC 62271-100 and

• IEEE C37.122.

Circuit Breaker Block Diagram
Circuit Breaker Block Diagram

Purpose

Power frequency withstand test is to verify the dielectric strength of GIS insulation under normal system frequency (50/60 Hz).

Test Voltage

Typically 1.5 to 2.0 times the rated voltage.

Duration

Usually 1 minute.

Reference Standard 

IEC 62271-203

This confirms that the GIS insulation system can withstand the overvoltage conditions without any breakdown or failure.

Purpose

Partial discharge (PD) test is to detect internal defects such as:

• Voids in insulation

• Loose metallic particles

• Surface contamination

• Insulation degradation

Applied Voltage

At (or) slightly above operating voltage.

Typical Acceptance Level

Less than 5 pC

Detection Methods

• Coupling capacitors

• UHF sensors

• Acoustic emission sensors

Reference Standard

IEC 60270

PD testing is one of the most important diagnostics for the GIS condition assessment.

Purpose

Dielectric (insulation resistance) test to measure insulation resistance (IR) of GIS components.

Instrument Used

5 kV (or) 10 kV Megger (Insulation Resistance Tester)

Acceptance Value

Typically >1000 MΩ

Measurement Points

• Phase to ground

• Phase to phase

It is across open breaker contacts.

This test helps to detect moisture ingress (or) insulation deterioration.

Purpose

DC testing is generally not applied to GIS internal insulation but may be used for connected power cables.

Voltage Level

Typically 2–3 times rated DC voltage

Duration

15–60 minutes

Purpose

Circuit breaker timing test is to verify the operating sequence and timing of breaker contacts.

Tests Performed

• Open operation

• Close operation

• Open-Close (O-C)

• Trip-Free operation

Instrument

Breaker timing analyzer (e.g: Omicron CMC)

Typical Criteria

Opening/closing time within manufacturer specifications (commonly 30–60 ms).

It ensures a proper protection coordination and fault interruption performance.

Purpose

Contact resistance measurement is to measure resistance across closed contacts of:

• Circuit breakers,

• Disconnectors and

• Earthing switches.

Instrument

Micro-ohmmeter (200 A or higher)

Typical Acceptance Value

• Less than 100 µΩ

Reference Standard 

IEC 62271-100

The low resistance ensures a minimal heating and energy losses.

GIS
GIS

Testing of instrument transformers (current transformer and voltage transformer) installed within GIS includes:

Ratio Test

Ratio test verifies the correct transformation ratio.

Polarity Test

It ensures a correct phase relationship.

Excitation Test (CT only)

It identifies a saturation characteristics.

Burden/Impedance Test

It confirms compatibility with connected protection relays and meters.

Purpose

SF₆ gas leakage test is to ensure gas tightness of GIS compartments.

Tool Used

SF₆ gas leak detector (sniffer)

Typical Acceptance Criteria

Leakage rate < 0.5% per year

Reference Standard

IEC 60068-2-17

Maintaining gas integrity is critical for dielectric strength and environmental compliance.

Purpose

Functional & interlock tests is to verify the proper operation of:

• Mechanical interlocks,

• Electrical interlocks,

• Safety blocking systems &

• Control logic via SCADA

Testing is performed using the simulated operating commands.

It ensures a safe switching sequences and prevents operator error.

Purpose

GIS earthing continuity test is to verify all metallic enclosures are properly connected to the earth grid.

Instrument

• Low-resistance ohmmeter

Acceptance Value

Typically less than 1 Ω

It is essential for the personnel safety and fault current dissipation.

Purpose

Low frequency (VLF) test is used to provide effective insulation assessment at reduced frequency with lower test power requirements.

Application

It is used primarily for connected XLPE cables not GIS internal insulation.

Electrical testing of GIS in high voltage (HV) substations ensures:

• Dielectric integrity,

• Mechanical reliability,

• Safe operation,

• Environmental compliance and

• Standard adherence.

Proper testing during FAT, SAT, commissioning and maintenance significantly reduces the failure risk and extends equipment life.