Essential Pre-Commissioning Tests for Electrical Equipment

0
3
Essential Pre-Commissioning Tests for Electrical Equipment
Essential Pre-Commissioning Tests for Electrical Equipment

Pre-commissioning testing is an important step before turning on any electrical equipment (or) system. 

These tests ensure that the equipment was properly installed, is free of manufacturing or installation faults, and satisfies all safety and performance requirements. 

Proper pre-commissioning ensures long-term reliability, reduces the chance of failure, and helps fulfill industry standards such as IEC, IEEE, and IS.

The following is a thorough list of essential pre-commissioning tests for electrical systems and equipment, including 

  • Transformers, 
  • Switchgear, 
  • Motors, 
  • Cables, and 
  • Protective systems.

For a brief period of time measure the insulation resistance (IR) of electrical equipment from 

  • Phase to Phase and 
  • Phase to Ground. 

Determine the voltage and minimum permissible values.

Insulation resistance values less than the manufacturer’s minimum (or) rated voltage plus 1kV in megohms should be analyzed.  

Insulation Resistance Test
Insulation Resistance Test

Over potential or high potential tests should not be conducted unless insulation resistance (IR) levels are equal to (or) greater than the indicated minimum values.

Direct Current (DC)

A DC high potential test is one that requires the amount of applied direct voltage is controlled.  

The measured current is constantly monitored for abnormalities with a purpose of terminating the test prior to breakdown occurs.  

To perform a polarization index test on large rotating equipment, start with one-third of the suggested maximum voltage from the table and keep it constant for 10 minutes. 

The polarization index is obtained by dividing 1-minute resistance value by 10-minute resistance value. 

The index value should be two or more; numbers less than this ought to be explored. 

After the initial ten-minute test, increase the D. C. test voltage in ten uniform steps of one minute each, up to maximum allowed D. C. value.

For high potential cable testing, the direct current (DC) test voltage should be applied in four one-minute stages, each of which should be approximately equal to cable’s rated RMS voltage. The final test voltage, on the other hand, should be maintained for fifteen minutes.

High Potential Test 
High Potential Test 

Alternating Current (AC) 

There is a high potential for testing 

  • phase to ground & 
  • phase to phase.  

The potential application will be for a period of one minute. A voltage test must be performed in accordance with the instructions provided by the manufacturer.  

Increase the voltage at a rate of 1 kV per second till the maximum permissible test voltage is achieved.

The AC high potential test results are assessed on a go, no-go basis by gradually raising the test voltage to the necessary value of the final test voltage and sustaining it for 1 minute.  

Conduct DC High Potential Testing on important wires after installation.  

Test each cable in relation to the ground and nearby cables.  

The test value will be verified with the proponent.  

The DC test voltage cannot exceed 1.4 x (2 x rated voltage + 1000).

Low Voltage Cable Test
Low Voltage Cable Test

For one minute, conduct AC high potential tests on every bus segment, including phase to phase & phase to ground.  The maximum test voltage needs to be as mentioned above.

Take measurements and make a record of the contact resistance of each phase of the line to load, starting with the   

  • Bus, 
  • Breakers, and 
  • Contactors.  

Resistance levels greater than 200 microohms and variations greater than +/- 20% should be studied for equipment rated at 600A or above. 

The contact resistance is determined with the circuit breaker (or) contactor in closed state. 

Contact Resistance Test
Contact Resistance Test

The contactor should be closed & locked, not held tight with manual pressure.

Electrical equipment that is safely accessible and visible, such as 

  • Outside bus connections, 
  • Isolation switches, 
  • Circuit breaker terminations, and 
  • Transformers, 

should be checked for temperature deviations using Thermo-vision. 

The following table contains the Dielectric Fluid Specifications for the new insulating Oil as supplied by the supplier. 

It is important to conduct a test on the oil before starting the process of filling the equipment with oil. 

The results of the test, as well as the voltage at which the equipment operates, will determine whether or not the oil needs to be treated before it is put into the equipment.

  • IS 3043:1987
  • IEEE Std 81-2012 

Pre-commissioning testing is more than simply a mandatory requirement; it’s an important precaution that ensures all electrical equipment & systems work as intended from the initial installation. 

Each test improves system dependability, staff safety, & asset longevity. 

Previous articleHow to Control Motor Speed using a VFD?
Rabert T
As an electrical engineer with 5 years of experience, I focus on transformer and circuit breaker reliability in 110/33-11kV and 33/11kV substations. I am a professional electrical engineer with experience in transformer service and maintenance. I understand electrical principles and have expertise troubleshooting, repairing, and maintaining transformers, circuit breakers, and testing them.