The Factory Acceptance Test (FAT) procedure for Low Voltage (LV) switchboards entails checking the design and functionality prior to installation.
Inspections, functional testing of components & systems, and assuring specification and standard compliance are all part of the process. This procedure assures that the switchboards meet performance & safety standards prior to installation.
Purpose
The purpose of this post is to define the FAT (Factory Acceptance Test) procedure for the Low Voltage Main Switchboard.
- Visual Inspection TestÂ
- Insulation TestÂ
- High Voltage Injection TestÂ
- Primary Current Injection TestÂ
- Metering Current Transformer Polarity Test
- Secondary Current Injection TestÂ
Working Location
Equipment to be Used
- Digital insulation Continuity TesterÂ
- High Voltage / Flash TesterÂ
- Primary Current Injection Test SetÂ
- Secondary Current Injection Test Set
- Elcometer Thickness GaugeÂ
- Torque WrenchÂ
- Dial Caliper Range (0-150mm)
FAT Procedure
Visual Inspection Test
- Check fitting component layout.
- Check switchboard dimensions, busbar and cable sizes, earthing conductors, and feeder entry point placement.
- Verify the brand, model, and circuit identification of installed components, including breakers, fuses, current transformers, voltmeters,  ammeters, power meters, and protection relays.
- Inspect paint work, door locking mechanism, gasket, hinges, and cut-out holes.
- Check busbar & cable tightening, markings, clearance, base angle bar, and plinth.
- Check the labels, nameplate, and phase identification.
Insulation Test
Perform a 500V megger test for
- Phase to Earth,Â
- Neutral to Earth,Â
- Phase to Neutral, andÂ
- Phase to PhaseÂ
to determine insulation resistance with all breakers in the ‘ON’ position.
High Voltage Injection Test
- Perform a 500V megger test between each stressed phase &Â all other phases connected to exposed conductive elements, with all breakers in the ‘ON’ state.
- Apply 2.5kV AC voltage to each strained phase and any other phases connected to exposed conductive elements for 60 seconds, then measure the leakage current.
Primary Current Injection Test
- Temporarily short the R, Y, B, and N primary bars on one side of the protective current transformers.
- Connect the primary injection test set to R-phase and N to primary bars on other side of current transformers.
- Connect an ammeter to CT’s R-phase to monitor the secondary current.
- To monitor the spill current, connect a milliamp meter to earth-fault relay current coil.
- Inject 50% & 100% of CT ratio via the primary bars, and record the spill current. At the same time, record the R-phase’s secondary current.
- Repeat the above-mentioned test with both Y and B phases.
Secondary Current Injection Test
- Set the current plug setting of the IDMTL relay to 5A rated current and 0.1 TMS for the 3/10 characteristic.
- Inject 5A of secondary current into R-phase, then adjust the pickup current to 5A.
- Inject 10A, 15A, and 25A into R-phase &Â record the tripping time, correspondingly. The time should be between +30% & -10% of the normal timing.
- Choose the intended current setting and then modify the pickup current appropriately.
- Repeat the test using Y and B phases.
Metering Current Transformer Polarity Test
- Temporarily short the R, Y, B, and N primary bars on one side of protective current transformers.
- Connect the primary injection test set to the R-phase and Y-phase primary bars on the opposite side of metering current transformers.
- Connect an ammeter to CT’s R-phase to monitor the secondary current.
- To monitor the leakage of current, connect a milliamp meter to the earth line.
- Inject 50% & 100% of CT ratio via the primary bars, and measure the spill current accordingly. At the same time, record the secondary current in the R-phase.
- Repeat the test described using Y-phase by connecting the principal injection test set on Y-phase & B-phase.
- Repeat the test indicated using B-phase, linking the principal injection test set on B-phase & R-phase.
Safety & Risk Control
- To control the hazards during the FAT, the following arrangements will be made.
- Safety barriers will be constructed around the area where the FAT will take place.
- Danger signs will be hung to warn those who approaches the FAT region.
- The RED color warning lamp will be made to flash while delivering electricity to the board for testing.
- Fire extinguishers will be positioned for emergency use at the FAT area.
- A first aid kit will be placed in the FAT area for the emergency purposes.