How to select the Correct Accuracy Class for a Current Transformer?

0
5
How to select the Correct Accuracy Class for a Current Transformer?
How to select the Correct Accuracy Class for a Current Transformer?

A current transformer (CT) is an instrument transformer that converts a high primary current into a smaller, standardized secondary current, commonly 1 A (or) 5 A, for meters, instruments and protective relays. 

For example, a 400/5 A CT has a nominal transformation ratio of 80:1.

Ideally, 400 A in the primary circuit generates 5 A in the secondary circuit.

In practice, a small part of the primary ampere-turns supplies the core magnetizing current, creating ratio error and phase displacement.

The CT accuracy class identifies the limits within which its performance is specified. 

Metering CTs are designed to measure normal load current accurately while protection CTs are designed to reproduce high current during system faults with acceptable error. 

Special protection CTs are selected where excitation characteristics, remanence or transient response are important.

Current (ratio) error is the difference between the actual transformation ratio and the rated ratio. 

It is commonly expressed as a percentage of primary current. A commonly used expression is 

ε = [(Kᵣ x Iₛ − Iₚ) / Iₚ] x 100

Where 

Kᵣ – Rated Ratio 

Iₛ – Measured Secondary Current 

Iₚ – Actual Primary Current. 

Follow the sign convention specified by the applicable test standard.

Phase displacement is the angular difference between the primary-current phasor and the reversed secondary-current phasor. 

It is important in power and energy measurement because even a small phase error can affect calculated watts and watt-hours particularly at low power factor. 

Composite error is used for protection CTs and represents the RMS difference between the actual secondary-current waveform and the ideal scaled waveform over a cycle expressed as a percentage of the ideal secondary current.

CT saturation occurs when the magnetic core cannot maintain the required proportional response. 

The secondary waveform becomes distorted and may be lower than the ideal value. 

Saturation depends on 

  • Primary fault current, 
  • Burden, 
  • Secondary winding resistance, 
  • Remanent flux, frequency and 
  • DC component of fault current.
CT Accuracy: Important Parameters
CT Accuracy: Important Parameters
  1. IEC 61869-1:2023 – Instrument Transformers – Part 1: General Requirements.
  2. IEC 61869-2:2012 – Instrument Transformers – Part 2: Additional Requirements for Current Transformers.
  3. IEC 60044-6:1992 – Instrument Transformers – Part 6: Requirements for Protective Current Transformers for Transient Performance (Superseded).
  4. IEEE C57.13-2016 – IEEE Standard Requirements for Instrument Transformers.
  5. IEEE C57.13.5 – IEEE Standard Requirements for Instrument Transformers Operating at System Voltages of 115 kV and Above.

Metering CTs supply 

  • Energy meters, 
  • Ammeters, 
  • Wattmeters, 
  • Power-quality instruments and 
  • Transducers. 

Their class limits ratio error and, for the relevant classes, phase displacement at specified percentages of rated primary current and specified burden conditions. 

IEC 61869-2 lists standard measuring CT classes 0.1, 0.2, 0.2S, 0.5, 0.5S, 1, 3 and 5.

IEC classRatio error limits at 5%, 20%, 100%, 120% rated current
0.1±0.4%, ±0.2%, ±0.1%, ±0.1%
0.2±0.75%, ±0.35%, ±0.2%, ±0.2%
0.5±1.5%, ±0.75%, ±0.5%, ±0.5%
1±3.0%, ±1.5%, ±1.0%, ±1.0%
3±3% at 50% and 120% rated current
5±5% at 50% and 120% rated current

S-class CTs include an additional low-current accuracy test point at 1% rated primary current. 

The IEC limits are 0.2S: ±0.75% at 1%, ±0.35% at 5%, and ±0.2% at 20%, 100% and 120%; 0.5S: ±1.5% at 1%, ±0.75% at 5%, and ±0.5% at 20%, 100% and 120%. 

This makes S-class CTs useful where accurate measurement at low load is important.

  1. For classes 0.1 to 1, IEC also specifies phase-displacement limits. For example, class 0.5 limits phase displacement to 90 minutes at 5% current, 45 minutes at 20%, and 30 minutes at 100% and 120%. 
  2. Class 0.2 limits are 30, 15, 10 and 10 minutes at those same points. Always use the complete applicable standard table for the selected class and test conditions.
  3. Class 0.1 and 0.2 are used where high measurement accuracy is required, including precision or revenue metering; 0.2S and 0.5S provide defined low-current performance; class 0.5 is common in general metering; class 1 is used where less stringent accuracy is acceptable. 
  4. Classes 3 and 5 are less accurate and are suitable only where the measurement specification permits them.

Protection CTs feed relays such as overcurrent, earth-fault and differential protection. 

Their performance must be adequate at elevated current, particularly during short circuits. 

IEC class P CTs are designated by the maximum permissible composite error, the letter P and an Accuracy Limit Factor (ALF). 

Standard protection classes include 5P and 10P; standard ALF values include 5, 10, 15, 20 and 30.

DesignationRatio error at rated currentComposite error at accuracy-limit currentInterpretation
5P10±1%5%Accuracy limit at 10 x rated primary current
5P20±1%5%Accuracy limit at 20 x rated primary current
10P10±3%10%Accuracy limit at 10 x rated primary current
10P20±3%10%Accuracy limit at 20 x rated primary current

For a 400/5 A, 15 VA, 5P20 CT, the nominal ratio is 80:1 and the accuracy-limit primary current is 20 x 400 = 8000 A at rated burden. 

The 5P designation means the composite error must not exceed 5% at that accuracy-limit condition. 

It does not mean zero error up to 20 times rated current or guarantee performance at any burden.

IEEE relaying CTs use designations such as C100, C200, C400 and C800.

The number indicates the standard secondary terminal voltage the CT can develop at 20 times rated secondary current while meeting the specified relaying accuracy criterion. 

The letter C identifies a class for which ratio correction can be calculated, associated with low-leakage-reactance construction.

ClassTerminal voltageEquivalent burden impedance for 5 A secondary at 20 × current (100 A)
C100100 V1 Ω
C200200 V2 Ω
C400400 V4 Ω
C800800 V8 Ω

Example: A 5 A secondary C200 CT is evaluated at 100 A secondary current; 200 V divided by 100 A equals 2 Ω. This is the basis of the C200 burden relationship. 

It is not an IEC ALF designation. 

For a 1 A CT, the 20-times test current is 20 A, so the impedance calculation is different. 

PX CTs are used in applications such as high-impedance differential and restricted earth-fault protection where excitation characteristics and CT matching are important. 

Specifications normally include rated turns ratio, knee-point e.m.f. (Eₖ), maximum exciting current at a stated voltage and maximum secondary winding resistance (Rct). 

The knee point is defined by the applicable standard’s excitation-curve criterion; do not use an informal knee-point definition in place of the standard.

PXR is a low-remanence variant of PX. PR denotes a low-remanence protection CT class. 

TPX, TPY and TPZ are transient performance classes intended for applications where CT response to fault transients including the DC component. 

Special Protection CTs: PX, PXR, PR and TP
Special Protection CTs: PX, PXR, PR and TP

Selection depends on system X/R ratio, primary time constant, fault inception angle, remanence, protection operating time and required secondary time constant. 

These classes cannot be ranked simply by a percentage accuracy number.

Burden is the load connected to the CT secondary normally expressed in volt-amperes (VA) at rated secondary current and a specified power factor. 

It includes connected instrument or relay impedance and secondary lead impedance. 

For a resistive external circuit, burden 

S = Iₛ²R

For a general impedance, use S = Iₛ²|Z| and consider power factor.

Example: a 5 A CT secondary circuit has 0.10 Ω relay input resistance and 0.20 Ω total lead-loop resistance. External resistance is 0.30 Ω and burden is 5² × 0.30 = 7.5 VA. 

The CT winding resistance also contributes to the internal voltage requirement and should be included in appropriate excitation and protection calculations. 

The actual ALF can differ from the rated ALF when the connected burden differs from rated burden; use manufacturer excitation data for essential applications.

ALF is the multiple of rated primary current at which a protection CT meets its specified accuracy limit at rated burden. 

The continuous thermal current rating factor states the multiple of rated current the CT can carry continuously under stated thermal conditions. 

  • Do not interpret a class number as the maximum error at every current and burden; limits apply at specified test points.
  • Do not equate 5P20 with C200. The IEC and IEEE/ANSI systems use different definitions and test methods.
  • Do not treat rating factor and ALF as interchangeable.
  • Do not calculate CT burden using only the relay input; include the complete outgoing and return lead path and all connected devices.
  • Do not assume a correct ratio proves correct polarity, phase displacement, insulation or protection performance.