Medium Voltage (MV) Switchgear Operation: Safety Precautions and Procedures

0
1206
Medium Voltage (MV) Switchgear Operation: Safety Precautions and Procedures

To be safe while using Medium Voltage equipment, we must adhere to the safety standards and operating requirements. This post discusses general safe operations on the medium voltage equipment, including 

  • Switching, 
  • Isolating, 
  • Testing, and 
  • Earthing, 

and also, the numerous types of medium voltage testers and their applications.  

There are five various types of hazards linked with the use of electrical equipment.  

1). Electric shock. 

2). Electric Burns. 

3). Fire & explosion. 

4). Increase in Heat 

5). Mechanical Hazards.  

It is impossible to detect whether an electrical conductor (or) terminal is alive simply by looking at it; it must be examined with an appropriate approved tester. Then it should be kept safe in such a way that it cannot be electrified by anybody else while being worked on.  

Medium Voltage does not require contact with a conductor (or) terminal to cause burns. Air does not ordinarily conduct electricity; but, when a human comes too close to an improperly insulated electrical wire, the air can break down & establish a conducting channel between them and the earth.  Coils & capacitors store electrical energy & release it once the power is switched off; consequently, they should be depleted before work gets started.  

Working with Medium Voltage equipment carries a high risk of fire and explosion due to the huge fault currents that may pass through the system.  Oil Circuit Breakers (OCBs), Oil Mini Sub Stations (MSS), & Ring Main Units (RMUs) provide a specific risk. Operator errors may additionally cause faults, such as energizing a wire when the other end is earthed.  

Heat can accumulate in wires.  When a lightweight extension lead is utilized for heavy-duty applications, it becomes hot.  Whenever possible, avoid utilizing extension leads.  If they must be used, make sure they can handle the current without overheating.  Do not string them overhead, across hallways, or beneath mats, where heat might accumulate and fully stretch them. 

Electricity is frequently utilized to power machinery; rotating machinery & moving parts are a constant source of risk; constantly maintain protections in place.  Ensure that the machine that are working on cannot be turned on without prior authorization.

Because there is a considerable risk of 

  • Flashover, 
  • Shock, 
  • Arcing, and 
  • Other hazards 

when operating in a Medium Voltage setting, lower voltages are often regarded with neglection.  

Asphyxia and/or cardiac muscle fibrillation can occur at voltages as low as 50 volts and currents of ± 30 milliamps.  

The most dangerous aspect of electricity is that live & dead apparatus are unrecognizable.  

As a result, never assume that apparatus is dead; instead, assume that it is alive. This can only be determined by safety testing with the relevant certified tester or the presence of a visible earth connection.  

Electricity can leap gaps; thus, you don’t even have to contact a Medium Voltage conductor to get wounded.  Approaching too close can be fatal, therefore keep close proximity distances.

Close Proximity is the shortest distance that any portion of a person’s body or work tool can come into contact with an unearthed LV conductor or an unearthed & unscreened MV/HV conductor.

When working in a potentially hazardous environment, always wear the PPE listed below, as mandated by the Code of Safe Practices.

  • Flame-resistant apparel (FR)
  • Hood and smock
  • Hand protection
  • Eye protection
  • Hard Hat

Code of Safe Procedures describes potentially unsafe conditions.

Some enclosures keep powered, high-voltage equipment in easy reach.

Access enclosures containing energized, high-voltage equipment for visual examination only.

Maintain a safe working distance from the energized equipment as prescribed in the Code of Safe Practices, Section 809, “Approach and Working Distance.”

Before unlocking and accessing any compartments, consider all equipment inside as electrified, unless and until it has been cleared, high-voltage tested when de-powered, and the property grounded.

Remote racking devices enable the removal & insertion of the metal-clad breakers from an electrified bus while the equipment operator remains beyond the arc-flash boundary. 

Remote racking equipment, like metal-clad switchgear, vary, thus understanding their individual properties is essential. Before using remote racking equipment, follow the instructions provided by the manufacturer. 

The maintenance slow-closing device should not be used to manually close any type of circuit breaker that is powered at the primary voltage. The slow-closing device lacking enough force & speed to ensure safe & proper operation.

Although the maintenance methods for the vacuum metal-clad switchgear are identical to those for other electrical devices, two regions demand additional care.

Medium Voltage (MV) Switchgear Operation: Safety Precautions and Procedures

During normal operation & high-pot (HIPOT) tests, the primary shield in an interrupter, along with other high-voltage components, can accumulate electrical charges. 

The shield is linked to the insulating bottle’s external mid-band ring. These charges typically stay after high voltage is withdrawn.

To remove charge before touching 

  • Interrupter, 
  • Connections, 
  • Circuit breaker studs, 
  • Bushings, 
  • Ground the bushings and 
  • Mid-band ring with a clip jumper.

Don’t depend on the insulation covering the connectors & bus conductors in the metal-clad equipment to protect employees from excessive voltage.

Always assume high-voltage equipment is energized until it has been tested dead & subsequently grounded.

Cleared bus portions in certain indoor stations might extend across multiple cubicles or levels.

Before operating on or near equipment in cubicles (or) on floors where the ground is not visible, make sure it is deenergized.

Install grounds as close to the work site as possible.

Certain circumstances necessitate numerous ground sites to ensure personal safety.

Before reporting off and turning on the equipment, make sure that the grounds have been cleared from all areas.

I – Determine the correct operational location & correct operating device. 

S – Switch

I – Isolate 

T- Test 

E – Earth

  • Identify the appropriate substation/MSS, etc.
  • Select the correct circuit breaker or isolator. 
  • Open circuit breaker/isolator. 
  • To isolate the circuit breaker, rack it out or down. 
  • Test with an authorized voltage detector. 
  • Connect effectively to the earth using the suitable methods.

Circuit breakers are able to be opened in a variety of ways; remote operation is preferable.  

Local: 

Electrically, use an open/close switch. Mechanically, press the trip button. Some circuit breakers include emergency trip buttons (or) foot pedals.  

Remote: 

Utilizing remote operating panel, remote operating device, and SCADA (Supervisory Control and Data Acquisition).  

Circuit breakers must be opened remotely whenever possible.  If the procedure will take place locally at the panel, it is advised that the proper Personal Protective Equipment (PPE) be worn (Flash Suit).

  • Mini Sub Stations (MSS) & 
  • Ring Main Units (RMU) 

are manually opened with the appropriate operational handle. 

The ‘T’ Off to the transformer can be equipped with a circuit breaker (or) fuse as activated by pressing a button on the unit’s front.  

They can also be equipped with an electrical remote operating mechanism, similar to a circuit breaker.

The authorized Person will carry out necessary isolations using personal locks in accordance with the rules and regulations.  Following that, do safety tests utilizing an appropriate approved tester to make sure that the mains (or) equipment is dead, and place danger tags at all control points.  

 A location on the system where a main (or) equipment can be switched, isolated, and grounded.  

When isolating, the equipment needs to be disconnected from all potential sources of energy, not simply electricity.  

As a result, we must evaluate the sources of harmful energy and compounds listed below.  

  • Electrical, pneumatic, hydraulic, 
  • Stored (springs, batteries). Potential (because of position), 
  • Heat (hot water, steam),
  • Radiation.  
  • Gases, vapours, liquids, & dusts that have the potential to induce injury or sickness, such as toxic, corrosive, or combustible.  
  • All plant and equipment require written isolation procedures; these procedures will outline a step-by-step process for isolating and keeping the system, plant, or equipment safe.  
  • In conditions of electrical isolation, a voltage test must be performed using an appropriate authorized tester to check that the mains and/or device are dead.  
  • Authorized Isolation is performed in accordance with rules and regulations. Control points need to be locked with personal locks. 
  • Danger tags need to be placed at all sites of isolation.  

Note: The locking of the control points & the application of danger tags are required for safe isolation, and isolation will not be considered complete until those conditions are completed.  

All live shutters must be locked with a personal lock. 

Cable shutters must be classified as live shutters since the cable might be back fed, for example, through an open point on a ring; thus, both bus bar & cable shutters must be locked.

Before applying earthing equipment, the conductor must be examined to ensure it is dead.  

Any certified Medium Voltage equipment should be visually examined for faults prior to use.  

When testing Medium Voltage, use the three-point test: test the tester on a known live source (or) a manufacturer-supplied test box, test all three phases, and then retest the tester.  

There are various varieties of voltage testers on the market, and each has a specific use:  

Used to determine the existence of voltage. A live tester must touch the conductor being tested in order to identify whether it is alive or dead.  There are two types of live testers: S and L. 

  • S type – for use with switchgear.
  • L-type – for use on overhead lines.  

Used to ensure that circuits remain in phase with one another. A phase comparator must be used to compare phases rather than to detect voltages.  Ring feeds are being phased in. 

It is necessary to phase in medium voltage equipment before energizing cable circuits to ensure proper phase rotation when cable networks are maintained and extended. 

Electrical phasing is necessary for new equipment installations that require breaking into a ring feed, such as new substations. 

After repairing a ring feed cable, or while terminating one. · Connecting and/or terminating an existing cable that will be returned to service.  

Used for overhead lines. This tester does not need to make contact with conductor under test to identify whether it is alive or dead; it detects the magnetic field and so only operates on bare and unscreened conductors.

Connected to the earth’s main mass in such a way that an immediate and safe discharge of the electricity is always possible.  There are various distinct earthing methods:

  • Integral Earthing
  • Earthing Carriage 
  • Earthing Truck  
  • Portable Earths  

The circuit breaker includes integral earthing, which eliminates the need for additional attachments to earth the circuit. There is no electrical tripping in earth position of a circuit breaker with inherent earthing, hence the manual trip button must be turned off.  

Earthing Carriages are typically used to ground bus bars and use the circuit breaker which has been disconnected.  

Earthing Trucks are typically utilized to ground the circuit racks after the circuit breaker has been completely removed.  

Portable earths are typically utilized on overhead wires (or) as working earths when work is being done distant from wherever the control point earths have been installed, such as capacitor banks.