NGR Calculator
Neutral Grounding Resistor — All Equipment Types
Enter line-to-line voltage in kilovolts
Full load current in Amperes
Rated capacity in MVA
Maximum allowable ground fault current (typically 5 – 1000 A)
Time the NGR must sustain the fault current
📐 Key Formulas Used
Phase-Neutral Voltage:Vn = VLL / √3
NGR Resistance:R = Vn / Ifault
Continuous Power:P = Vn × Ifault (W)
Short-Time Energy:E = P × t / 1000 (kJ)
Zero Sequence Current:I0 = Ifault / 3

Click here for more Electrical Calculators

You can also follow us on Facebook and Linkedin to receive daily updates.

Its purpose is to limit ground fault current to a safe and controlled level while providing a reliable path for fault detection relays.

NGRs are essential in 

  • Generators, 
  • Transformers, 
  • Motors and 
  • Bus/switchgear installations 

across industrial, utility and commercial power systems worldwide.

Fault Current Control

Fault current control limits ground fault current to a predetermined safe level

Equipment Protection 

Equipment protection reduces mechanical and thermal stress on windings and cores

Continuous Operation

HRGN systems can run through a single ground fault without shutdown

Arc Flash Reduction

Lower fault current directly reduces arc flash incident energy

Relay Sensitivity

Relay sensitivity provides a controlled reference for 51G / 64 ground protection relays

Standards Compliance

It satisfies IEEE Std 142, IEC 60034, IEC 60364 and NEC Article 250

The NGR Calculator covers 4 principal equipment categories. 

Each has distinct grounding considerations set out in the relevant IEEE and IEC standards.

Equipment TypeTypical VoltagePreferred Method
Generator0.4 kV – 25 kVHRGN (unit-connected)
Transformer (HV / LV)0.4 kV – 33 kVLRGN or HRGN
Motor3.3 kV – 13.8 kVHRGN (continuous process)
Bus / Switchgear3.3 kV – 33 kVLRGN with 51G relay

Power Factor is only applicable when the equipment type is generator (or) motor.

Input ParameterDescription and Typical Values
System Voltage VLL (kV)Line-to-line voltage in kilovolts, e.g. 0.415 / 3.3 / 6.6 / 11 / 33 kV
Rated Current (A)Full load current of the equipment in Amperes
Rated Power (MVA)Rated capacity of the equipment in Megavolt-Amperes
Ground Fault Current Limit (A)Max allowable fault current: typically 5–10 A (HRGN) or 200–1000 A (LRGN)
Fault Duration (s)Seconds the NGR must sustain fault current; typical 10 s (HRGN), 1–2 s (LRGN)
Power FactorEquipment PF from 0.10 to 1.00; required for generators and motors only
Grounding MethodHigh Resistance Grounding (HRGN) or Low Resistance Grounding (LRGN)

The calculator applies the following standard electrical engineering formulas assuming a balanced three-phase system.

Phase-to-Neutral Voltage

The NGR sits between the neutral point and earth so its operating voltage equals the phase-to-neutral voltage.

Vn  =  VLL÷√3

Example: For an 11 kV system, Vn = 11000 ÷ 1.7321 = 6351 V

NGR Resistance

The resistance is selected to limit the ground fault current to the specified maximum:

R = Vn÷Ifault(Ω)

Continuous Power Rating

Power continuously dissipated in the NGR during a sustained fault:

P = Vn x Ifault   (W)

Short-Time Energy Rating

Total thermal energy the NGR must absorb within the fault duration. This determines the thermal withstand class required when ordering:

E = P x t ÷ 1000(kJ)

Zero Sequence Current

The zero-sequence current flowing through the NGR is used to set the 51G relay pickup threshold:

I₀ = Ifault ÷ 3 (A)

Fault Current as Percentage of Rated Current

This ratio indicates protection sensitivity: typically less than 1% for HRGN and 5–25% for LRGN:

%If = (Ifault ÷ Irated) x 100(%)

OutputSignificance and Application
Phase-to-Neutral Voltage Vn (V)Voltage rating of the NGR that is used for insulation co-ordination and purchasing spec
NGR Resistance R (Ω)Core resistor specification; primary ordering parameter
Continuous Power Rating (W)Wattage the NGR must withstand indefinitely during a sustained fault (HRGN)
Short-Time Energy Rating (kJ)Thermal energy the NGR must absorb within the specified fault duration
Zero Sequence Current I₀ (A)Set point for 51G relay pickup, where I₀ = Ifault ÷ 3
Ground Fault Current Igf (A)Confirms the design fault current limit selected by the engineer
NGR Voltage Rating (V)Equal to Vn that specifies the dielectric withstand level for the resistor
Fault Current % of Rated (%)Protection sensitivity indicator: < 1% for HRGN, 5-25% for LRGN
CharacteristicHRGNLRGN
Fault Current< 10 A200 – 1000 A
Continued OperationYes - operate through faultNo - rapid clearance required
Arc Flash RiskVery LowModerate to High
Relay Type59G / 64 (alarm)51G (trip)
Fault DetectionHigh sensitivityLower sensitivity
Typical ApplicationGenerators, continuous motorsBus, switchgear, transformers
Typical Fault Duration10 s (or) longer1 – 2 s
Standards ReferenceIEEE 142, IEC 60034-3IEEE 142, IEC 60364-4-41
Neutral Grounding Resistor (NGR) Single Line Diagram (SLD)
Neutral Grounding Resistor (NGR) Single Line Diagram (SLD)

11 kV Generator with HRGN, fault current limited to 10 A.

Input Values

  • Equipment: Generator
  • VLL: 11 kV
  • Rated Current: 524 A
  • Rated Power: 10 MVA
  • Fault Current Limit: 10 A
  • Fault Duration: 10 seconds
  • Power Factor: 0.85
  • Grounding Method: High Resistance Grounding (HRGN)

Calculated Results

ParameterCalculated Value
Phase-to-Neutral Voltage Vn6350.9 V
NGR Resistance R635.09 Ω
Continuous Power Rating63,509 W  (63.5 kW)
Short-Time Energy Rating635.09 kJ
Zero Sequence Current I₀3.33 A
Ground Fault Current Igf10.0 A
NGR Voltage Rating6350.9 V
Fault Current % of Rated1.91%

At 1.91% of rated current, the fault current is well within HRGN limits (< 10 A). The NGR should be rated for 635.09 Ω, 6.35 kV and capable of absorbing 635 kJ within 10 seconds. The 51G relay should be set to detect zero sequence current above approximately 3.33 A.