RMU Standard Operating Procedure (RMU SOP)

0
6
RMU Standard Operating Procedure (RMU SOP)
RMU Standard Operating Procedure (RMU SOP)

The objective of this procedure statement is to explain the work sequences and procedures that will be used to ensure the proper & safe operation of the RMU and Transformer.

Ensure safe operation of RMU & Transformer.

  1. Project Manager
  2. Electrical Engineer
  3. Safety Engineer
  1. Project specifications & approved drawings.
  2. Project Quality Plan.
  3. Health, safety, & environment manual.
  1. Ensure all personnel have proper PPE (Personal Protective Equipment).
  2. Electrical Safety Shoes
  3. Flame-Resistant Clothing
  4. Safety Glasses or Goggles
  5. Insulated Tools

Ensure that the RMU & the space surrounding it are free of any impediments for inspection.

  • Visually check the RMU in search for any indications of damage, leakage, or conditions that are not typical.
  • Analyze the RMU for any unnecessary objects which may be present.
  • It is important to adhere to the switching sequence that is specified in the operation handbook.
  • When working with switches, make sure you use insulated tools.
  • Before starting any work, make sure that proper isolation has been arranged.
  • Before starting any type of maintenance or switching procedures, make sure that the RMU has been properly earthed.
  • Determine whether or not the earthing system is operating appropriately.
  • Ensure that there is free and open communication with all of the personnel participating in the operation.
  • When it comes to coordination, make use of the existing communication protocols.

Turn On

  • In the direction indicated by the arrow, turn the earthing switch so that it is disconnected.
  • It is clear from the second panel that earthing switch is not connected.
  • Place the handle on the panel of the circuit breaker & rotate it in the direction of the arrow, which indicates the direction of the energy storage.
  • The final step is to finish the process of closing the ring main unit by pushing the green close button located in upper right corner of the screen.

Turn Off

  • The first step is to disconnect low-voltage (LV) main circuit breaker. 
  • The next step is to click the red stop button that is located in the upper right corner of the circuit breaker. 
  • It has been determined that the circuit breaker has been disconnected, & the panel indicator of circuit breaker room has displayed the disconnected state. 
  • The next step is to press the handle into the earthing switch room after inserting it. 
  • The action of disconnecting ring network cabinet is finished when the arrow rotates in the direction of closing, which indicates that the earthing switch has been closed. 
  • The panel also indicates that the earthing switch has been closed.
  • Verify that the primary load switch on the transformer’s output is off before turning it on.
  • Remove the “No Switching On” warning sign and open earthing knife lock.
  • To open earthing knife, turn counterclockwise.
  • Verify that the earthing indication is in the “floating” or off position.
  • The earthing knife lock should be locked.
  • Unlock the load knife.
  • To close the switch, turn it clockwise.
  • Verify the three indication lights’ condition.
  • Lock the load knife lock.
  • The transformer’s output total load switch needs to be unplugged before the transformer is turned off.
  • Check the three indication lights’ condition.
  • Unlock the load knife.
  • Manually press the red “OFF” stop button until the switch sounds.
  • Verify that all three of the indicator lights are white and not flickering.
  • Lock the load knife lock.
  • Open the earthing knife lock.
  • Close the earthing knife by rotating it clockwise.
  • Hang up a warning sign that reads “No Switching On” and make sure the earthing indicator is in earthing state.
  • Lock the earthing knife lock.
  • In the case that any unusual conditions arise, you should be conversant with the emergency shutdown procedures.
  • Every member of the staff should be informed of the protocols for responding to emergencies.

Post Operation Inspection

  • Once the process has been finished, it is necessary to perform a visual inspection to ensure that all of the switches are in the appropriate position.
  • Ensure that all of the precautionary measures have been carried out in the appropriate manner.
  • Please make sure to document all of the pertinent information pertaining to the operation, particularly any deviations from standard operating procedure.
  • Ensure that records are kept for future use and for the purposes of auditing.
  • Make sure that all of the staff who are involved in the RMU operations have received sufficient training and are capable.
  • Refresher training courses should be offered on a regular basis in order to emphasize safe operating procedures.
  • Protect the RMU & the area immediately surrounding it.
  • Make sure that all of the tools & equipment are stored in the appropriate manner.
  • Complete any paperwork or reporting that may otherwise be required.
Previous articleReactor Switching Voltage Drop Calculator
Rabert T
As an electrical engineer with 5 years of experience, I focus on transformer and circuit breaker reliability in 110/33-11kV and 33/11kV substations. I am a professional electrical engineer with experience in transformer service and maintenance. I understand electrical principles and have expertise troubleshooting, repairing, and maintaining transformers, circuit breakers, and testing them.