Soft Starter Selection Procedure: Step-by-Step Method to Choose the Right Soft Starter for Your Motor Load

0
402
Soft Starter Selection Procedure: Step-by-Step Method to Choose the Right Soft Starter for Your Motor Load
Soft Starter Selection Procedure: Step-by-Step Method to Choose the Right Soft Starter for Your Motor Load

Soft starters are the more important components in current industrial applications providing wide range of advantages such as lowering mechanical stress on the motors and increasing the energy efficiency. 

Choosing the correct soft starter for the particular industrial requirements can have a major impact on the operating efficiency & equipment longevity. 

This in-depth procedure will help you to understand the significant considerations to consider when selecting the appropriate soft starter for the operations.

Soft starters are devices that governs the acceleration of an electric motor resulting in a smooth and also progressive ramp-up of speed. 

Unlike direct-on-line starters soft starts limit the initial surge of current and torque hence reducing mechanical stress and also electrical disturbances.

Choosing the correct soft starter is essential for achieving 

  • Maximum performance, 
  • Efficiency and 
  • Lifetime for the motor and load.

Here is the step-by-step procedure to help you to choose the most suitable soft starter complete with calculations and important factors.

Soft Starter
Soft Starter

Power Rating

To properly manage the load, ensure that the soft starter meets the motor’s power rating (kW or HP).

Voltage & Current

The soft starter must be compatible with the motor’s voltage and current specifications.

Application Type

Determine whether the load is continuous, variable (or) high inertia. Pumps, conveyors and fans may need unique soft starter features.

Starting Conditions

Consider the motor’s starting circumstances such as frequency and load torque.

Ramp Time

Look for the customizable ramp time settings to control the motor acceleration and also slowdown based on the processing requirements.

Current Limiting 

Soft starters with current limiting characteristics helps to avoid overcurrent conditions maintaining both the motor & the electrical network.

Temperature 

Ensure that the soft starter may operate efficiently within the industrial ambient temperature range.

Protection Ratings

Check the IP rating of the soft starter to verify that it can survive adverse environmental conditions including dust, moisture and corrosion.

Connectivity

Modern soft starters usually contain connectivity features that allow for integration with control systems and remote monitoring.

Compatibility

Ensure that existing control systems such as PLCs (or) SCADA systems can be seamlessly integrated and controlled.

Built-in Protections

Check for soft starters that includes overload, short circuit & phase loss protection.

Compliance

Ensure that the soft starter meets the applicable industry standards & certifications for the safety & performance.

Soft Starter Circuit Diagram
Soft Starter Circuit Diagram

Full Load Current (FLC)

The soft starter should need to accommodate the motor’s FLC.

FLC Formula

Full Load Current (FLC) = (P x 1000) / (√3 x V x PF x η)

Example

For a 30 kW motor (400V, PF = 0.85, η = 92%), the FLC is approximately 49.5 A calculated as (30 x 1000) / (√3 x 400 x 0.85 x 0.92).

Locked Rotor Current (LRC)

A soft starter can reduce the inrush current from 6 – 8 x FLC to 2 – 4 x FLC.

Duty Cycle

The thermal performance of the soft starter is impacted by the frequent starts.

Torque Requirements 

The torque requirements vary depending on the load type (for example: pumps, fans and conveyors).

Load Inertia

High-inertia loads require more initial energy and duration.

Voltage and Frequency

Match the motor to the supply voltage (for example, 400V, 50Hz).

Starting Current

Verify that the electrical power supply network is capable of managing the necessary starting current for motor.

Current Limiting and Voltage Ramp

Soft starter helps to reduce startup current while ensuring smooth acceleration.

Bypass Contactor

Bypass Contactor reduces heat dissipation after the motor reaches full speed.

Protection Features

Soft starter prevents overload, overcurrent & phase loss problems.

Full Load Current (FLC) = (P x 1000) / (√3 x V x PF x η)

Example: For a 30 kW motor – FLC ≈ 49.5 A

Starting Current = Full Load Current (FLC) x Starting Factor (eg: 3 for soft starters).

Example: 49.5 x 3 = 148.5 A

Select a soft starter rated ≥ Full Load Current (FLC) (eg: for 49.5 A, select ≥ 50 A).

Ensure that the network can manage the starting current without experiencing significant voltage drop.

Environment

Verify that the ambient temperature and altitude are sufficient for the soft starter operation.

Enclosure 

Enclosure ensure it provides enough protection for the operational environment.

By following these steps and conducting the appropriate calculations you may choose the most suitable soft starter for your motor’s performance, efficiency and safety.