Transformer Failure Analysis and Troubleshooting

0
139
Transformer Failure Analysis and Troubleshooting
Transformer Failure Analysis and Troubleshooting

Power transformers are designed to operate reliably for several decades.

However, because of electrical faults, thermal stress, mechanical forces, insulation ageing, environmental conditions (or) improper operation, failures may still occur.

Failure analysis is the systematic procedure of identifying the root cause of a transformer problem using inspections, electrical tests, oil analysis, protection records and operational history. 

The objective is not only to repair the transformer but also to prevent similar failures in the future.

A proper analysis assists to improve system reliability, reduce downtime and optimize maintenance planning.

No.FactorCategory it belongs to 
1Electrical faultsElectrical failures
2Thermal stressThermal failures
3Mechanical forcesMechanical failures
4Insulation ageingDielectric failures
5Environmental conditionsMainly external faults and dielectric failures (e.g. moisture, lightning, animal contact)
6Improper operationCan contribute to any category (e.g. overloading, re-energizing without confirming root cause)

The objectives are to:

S.NoObjective Analysis
1Identify the actual cause of failure.Distinguishes the root cause from the visible symptom.
2Prevent recurrence of similar faults.Turns one event into a lesson applied to the whole installation.
3Decide whether repair, overhaul, or replacement is required.Supplies the technical basis for the decision framework in Section 14.
4Improve maintenance practices.Feeds findings back into routine maintenance (e.g. cleaning and insulation testing, Section 11).
5Enhance system reliability.Reduces the chance of repeat outages.
6Reduce downtime and operational losses.Faster, better-targeted diagnosis shortens outage time.

Transformer failures can be classified into 4 categories.

CategoryFailure modes listed in source
A). Electrical FailuresWinding short circuits; Earth faults; Inter-turn faults; Phase-to-phase faults; Flashover; Overvoltage damage
B). Thermal FailuresOverloading; Poor cooling; Hot spots; Insulation overheating; Excessive oil temperature
C). Mechanical FailuresWinding displacement; Loose core clamping; Damaged bushings; Gasket failure; Oil leakage; Broken leads
D). Dielectric FailuresMoisture contamination; Insulation ageing; Oil contamination; Partial discharge; Breakdown of insulation

These originate outside the transformer but affect its operation. 

Examples:

  • Lightning strikes.
  • Short circuits in the switchyard.
  • External line faults.
  • Animal contact (birds, monkeys, snakes).
  • Surge arrester failure.

These faults create high fault currents but do not always damage the transformer internally.

These occur within the transformer. 

Examples:

  • Winding insulation failure.
  • Core faults.
  • OLTC failures.
  • Internal arcing.
  • Loose internal connections.
  • Insulation deterioration.

Internal faults are more serious and often require internal inspection or repair.

AspectExternal faultsInternal faults
OriginOutside the transformerWithin the transformer
EffectCreate high fault currents; do not always damage the transformer internallyMore serious; often require internal inspection or repair
Examples (count)5 listed6 listed
SymptomPossible Cause
High oil temperatureCooling failure, overload
High winding temperatureOverload, blocked oil flow
Oil leakageDamaged gasket, loose flange
Buchholz alarmGas generation, minor internal fault
Buchholz tripSevere internal fault
PRD operationSudden internal pressure rise
Excessive hummingLoose core or magnetic vibration
Low BDVMoisture or contaminated oil
High Tan DeltaDeteriorated insulation
Abnormal vibrationLoose mounting or winding movement
Burning smellInsulation overheating
Unequal phase currentsWinding fault or loose connection

Root Cause Analysis follows these steps:

StepAction (as stated in source)Phase (analysis)
1Collect fault history.Information gathering
2Review relay indications.Information gathering
3Examine SCADA/event records.Information gathering
4Inspect the transformer externally.Field examination & testing
5Perform electrical tests.Field examination & testing
6Analyze transformer oil.Field examination & testing
7Conduct internal inspection (if needed).Internal examination
8Compare results with the factory records.Evaluation and conclusion
9Identify the root cause.Evaluation and conclusion
10Recommend corrective actions.Evaluation and conclusion

DGA is one of the most powerful diagnostic tools for transformers.

Fault gases include:

GasChemical formulaIndicates
HydrogenH₂Partial discharge
MethaneCH₄Low-temperature overheating
EthaneC₂H₆Moderate overheating
EthyleneC₂H₄High-temperature overheating
AcetyleneC₂H₂Arcing
Carbon MonoxideCOPaper insulation degradation
Carbon DioxideCO₂Cellulose ageing
AspectAlarm onlyTrip
Possible causesSmall amount of gas generation; Air trapped after oil filling; Minor insulation degradationSevere internal fault; Winding short circuit; Internal arcing; Major insulation failure
ActionCollect gas sample; Perform DGA; Inspect oil level; Monitor the transformerKeep the transformer isolated; Perform detailed testing; Consider internal inspection

If the PRD operates:

  • Internal arcing.
  • Rapid gas generation.
  • Sudden pressure rise.

Actions

  • Do not re-energize immediately.
  • Inspect for oil discharge.
  • Check relay records.
  • Perform DGA & insulation tests.
Common failuresSymptoms
Contact wearIncorrect voltage regulation
Carbon depositsTap position mismatch
Motor failureFailure to change taps
Mechanical jammingExcessive arcing
Low OLTC oil level—
Control circuit faults—

Corrective action includes inspection, contact replacement (if required), oil replacement, and mechanism servicing.

Typical causesSigns
Moisture ingressOil leakage
Cracked porcelain or composite housingCorona discharge
Internal insulation breakdownFlashover marks
Surface contaminationAbnormal heating
Loose connections—

Routine cleaning and insulation testing help prevent failures.

SymptomsPossible causes
High oil temperatureFan motor failure
High winding temperatureOil pump failure
Fan or pump alarmsClosed radiator valves
Reduced transformer loading capabilityBlocked radiators
—Faulty temperature controller

Immediate repair is essential to prevent overheating.

Common oil issuesCorrective actions
Moisture contaminationOil filtration
OxidationOil dehydration
Low BDVOil regeneration
High acidityOil replacement (when necessary)
Sludge formation—
Particle contamination—

Repair, Overhaul (or) Replacement

DecisionSuitable / Required for
Repair (suitable for)Minor oil leaks; Faulty accessories; Fan or pump replacement; Gasket replacement
Overhaul (suitable for)Winding repair; Core tightening; OLTC refurbishment; Internal cleaning
Replacement (required when)Severe winding damage; Extensive insulation failure; Economically unrepairable condition

The analysis should be based on technical assessment, safety, reliability, and cost.

  • Isolate the transformer from all power sources.
  • Follow Lock-Out/Tag-Out (LOTO) procedures.
  • Discharge any of the stored electrical energy.
  • Wear appropriate Personal Protective Equipment (PPE).
  • Handle transformer oil safely.
  • Vent gas carefully prior to opening the transformer.
  • Ensure adequate fire protection measures are in place.
TermMeaning
BDVBreakdown Voltage (of insulating oil)
CT / PTCurrent Transformer / Potential (Voltage) Transformer
DGADissolved Gas Analysis
FATFactory Acceptance Test
LOTOLock-Out/Tag-Out
LVLow Voltage
OLTCOn-Load Tap Changer
ONAN / ONAFOil Natural Air Natural / Oil Natural Air Forced (cooling methods)
PPEPersonal Protective Equipment
PRDPressure Relief Device
RCARoot Cause Analysis
SCADASupervisory Control and Data Acquisition
Tan DeltaDielectric dissipation factor, an insulation condition test

Failure analysis is an essential engineering activity that goes beyond repairing damaged equipment. 

It is a structured procedure of understanding the sequence of faults, identifying the root cause, and implementing corrective and preventive actions to improve system reliability.

Combining visual inspection, electrical testing, transformer oil diagnostics, protection records and engineering judgement allows engineers to make informed decisions regarding repair, overhaul, or replacement.