Power transformers are designed to operate reliably for several decades.
However, because of electrical faults, thermal stress, mechanical forces, insulation ageing, environmental conditions (or) improper operation, failures may still occur.
- 6 Stress Factors
- Objectives of Failure Analysis
- Classification of Transformer Failures
- External Faults
- Internal Faults
- Comparison: External vs Internal Faults
- Common Symptoms & their Possible Causes
- Root Cause Analysis (RCA)
- Dissolved Gas Analysis (DGA)
- Buchholz Relay Case Analysis
- Pressure Relief Device (PRD) Operation
- OLTC Failure Analysis
- Bushing Failure Analysis
- Cooling System Failure
- Transformer Oil Problems
- Safety Precautions during Failure Analysis
- Terms
- Conclusion
Failure analysis is the systematic procedure of identifying the root cause of a transformer problem using inspections, electrical tests, oil analysis, protection records and operational history.
The objective is not only to repair the transformer but also to prevent similar failures in the future.
A proper analysis assists to improve system reliability, reduce downtime and optimize maintenance planning.
6 Stress Factors
| No. | Factor | Category it belongs to |
|---|---|---|
| 1 | Electrical faults | Electrical failures |
| 2 | Thermal stress | Thermal failures |
| 3 | Mechanical forces | Mechanical failures |
| 4 | Insulation ageing | Dielectric failures |
| 5 | Environmental conditions | Mainly external faults and dielectric failures (e.g. moisture, lightning, animal contact) |
| 6 | Improper operation | Can contribute to any category (e.g. overloading, re-energizing without confirming root cause) |
Objectives of Failure Analysis
The objectives are to:
| S.No | Objective | Analysis |
|---|---|---|
| 1 | Identify the actual cause of failure. | Distinguishes the root cause from the visible symptom. |
| 2 | Prevent recurrence of similar faults. | Turns one event into a lesson applied to the whole installation. |
| 3 | Decide whether repair, overhaul, or replacement is required. | Supplies the technical basis for the decision framework in Section 14. |
| 4 | Improve maintenance practices. | Feeds findings back into routine maintenance (e.g. cleaning and insulation testing, Section 11). |
| 5 | Enhance system reliability. | Reduces the chance of repeat outages. |
| 6 | Reduce downtime and operational losses. | Faster, better-targeted diagnosis shortens outage time. |
Classification of Transformer Failures
Transformer failures can be classified into 4 categories.
| Category | Failure modes listed in source |
|---|---|
| A). Electrical Failures | Winding short circuits; Earth faults; Inter-turn faults; Phase-to-phase faults; Flashover; Overvoltage damage |
| B). Thermal Failures | Overloading; Poor cooling; Hot spots; Insulation overheating; Excessive oil temperature |
| C). Mechanical Failures | Winding displacement; Loose core clamping; Damaged bushings; Gasket failure; Oil leakage; Broken leads |
| D). Dielectric Failures | Moisture contamination; Insulation ageing; Oil contamination; Partial discharge; Breakdown of insulation |
External Faults
These originate outside the transformer but affect its operation.
Examples:
- Lightning strikes.
- Short circuits in the switchyard.
- External line faults.
- Animal contact (birds, monkeys, snakes).
- Surge arrester failure.
These faults create high fault currents but do not always damage the transformer internally.
Internal Faults
These occur within the transformer.
Examples:
- Winding insulation failure.
- Core faults.
- OLTC failures.
- Internal arcing.
- Loose internal connections.
- Insulation deterioration.
Internal faults are more serious and often require internal inspection or repair.
Comparison: External vs Internal Faults
| Aspect | External faults | Internal faults |
|---|---|---|
| Origin | Outside the transformer | Within the transformer |
| Effect | Create high fault currents; do not always damage the transformer internally | More serious; often require internal inspection or repair |
| Examples (count) | 5 listed | 6 listed |
Common Symptoms & their Possible Causes
| Symptom | Possible Cause |
|---|---|
| High oil temperature | Cooling failure, overload |
| High winding temperature | Overload, blocked oil flow |
| Oil leakage | Damaged gasket, loose flange |
| Buchholz alarm | Gas generation, minor internal fault |
| Buchholz trip | Severe internal fault |
| PRD operation | Sudden internal pressure rise |
| Excessive humming | Loose core or magnetic vibration |
| Low BDV | Moisture or contaminated oil |
| High Tan Delta | Deteriorated insulation |
| Abnormal vibration | Loose mounting or winding movement |
| Burning smell | Insulation overheating |
| Unequal phase currents | Winding fault or loose connection |
Root Cause Analysis (RCA)
Root Cause Analysis follows these steps:
| Step | Action (as stated in source) | Phase (analysis) |
|---|---|---|
| 1 | Collect fault history. | Information gathering |
| 2 | Review relay indications. | Information gathering |
| 3 | Examine SCADA/event records. | Information gathering |
| 4 | Inspect the transformer externally. | Field examination & testing |
| 5 | Perform electrical tests. | Field examination & testing |
| 6 | Analyze transformer oil. | Field examination & testing |
| 7 | Conduct internal inspection (if needed). | Internal examination |
| 8 | Compare results with the factory records. | Evaluation and conclusion |
| 9 | Identify the root cause. | Evaluation and conclusion |
| 10 | Recommend corrective actions. | Evaluation and conclusion |
Dissolved Gas Analysis (DGA)
DGA is one of the most powerful diagnostic tools for transformers.
Fault gases include:
| Gas | Chemical formula | Indicates |
|---|---|---|
| Hydrogen | H₂ | Partial discharge |
| Methane | CH₄ | Low-temperature overheating |
| Ethane | C₂H₆ | Moderate overheating |
| Ethylene | C₂H₄ | High-temperature overheating |
| Acetylene | C₂H₂ | Arcing |
| Carbon Monoxide | CO | Paper insulation degradation |
| Carbon Dioxide | CO₂ | Cellulose ageing |
Trending gas concentrations over time is more valuable than a single test result.
Buchholz Relay Case Analysis
| Aspect | Alarm only | Trip |
|---|---|---|
| Possible causes | Small amount of gas generation; Air trapped after oil filling; Minor insulation degradation | Severe internal fault; Winding short circuit; Internal arcing; Major insulation failure |
| Action | Collect gas sample; Perform DGA; Inspect oil level; Monitor the transformer | Keep the transformer isolated; Perform detailed testing; Consider internal inspection |
Pressure Relief Device (PRD) Operation
If the PRD operates:
Possible Causes
- Internal arcing.
- Rapid gas generation.
- Sudden pressure rise.
Actions
- Do not re-energize immediately.
- Inspect for oil discharge.
- Check relay records.
- Perform DGA & insulation tests.
- Open the transformer only if recommended by the manufacturer.
OLTC Failure Analysis
| Common failures | Symptoms |
|---|---|
| Contact wear | Incorrect voltage regulation |
| Carbon deposits | Tap position mismatch |
| Motor failure | Failure to change taps |
| Mechanical jamming | Excessive arcing |
| Low OLTC oil level | — |
| Control circuit faults | — |
Corrective action includes inspection, contact replacement (if required), oil replacement, and mechanism servicing.
Bushing Failure Analysis
| Typical causes | Signs |
|---|---|
| Moisture ingress | Oil leakage |
| Cracked porcelain or composite housing | Corona discharge |
| Internal insulation breakdown | Flashover marks |
| Surface contamination | Abnormal heating |
| Loose connections | — |
Routine cleaning and insulation testing help prevent failures.
Cooling System Failure
| Symptoms | Possible causes |
|---|---|
| High oil temperature | Fan motor failure |
| High winding temperature | Oil pump failure |
| Fan or pump alarms | Closed radiator valves |
| Reduced transformer loading capability | Blocked radiators |
| — | Faulty temperature controller |
Immediate repair is essential to prevent overheating.
Transformer Oil Problems
| Common oil issues | Corrective actions |
|---|---|
| Moisture contamination | Oil filtration |
| Oxidation | Oil dehydration |
| Low BDV | Oil regeneration |
| High acidity | Oil replacement (when necessary) |
| Sludge formation | — |
| Particle contamination | — |
Repair, Overhaul (or) Replacement
| Decision | Suitable / Required for |
|---|---|
| Repair (suitable for) | Minor oil leaks; Faulty accessories; Fan or pump replacement; Gasket replacement |
| Overhaul (suitable for) | Winding repair; Core tightening; OLTC refurbishment; Internal cleaning |
| Replacement (required when) | Severe winding damage; Extensive insulation failure; Economically unrepairable condition |
The analysis should be based on technical assessment, safety, reliability, and cost.
Safety Precautions during Failure Analysis
- Isolate the transformer from all power sources.
- Follow Lock-Out/Tag-Out (LOTO) procedures.
- Discharge any of the stored electrical energy.
- Wear appropriate Personal Protective Equipment (PPE).
- Handle transformer oil safely.
- Vent gas carefully prior to opening the transformer.
- Ensure adequate fire protection measures are in place.
Terms
| Term | Meaning |
|---|---|
| BDV | Breakdown Voltage (of insulating oil) |
| CT / PT | Current Transformer / Potential (Voltage) Transformer |
| DGA | Dissolved Gas Analysis |
| FAT | Factory Acceptance Test |
| LOTO | Lock-Out/Tag-Out |
| LV | Low Voltage |
| OLTC | On-Load Tap Changer |
| ONAN / ONAF | Oil Natural Air Natural / Oil Natural Air Forced (cooling methods) |
| PPE | Personal Protective Equipment |
| PRD | Pressure Relief Device |
| RCA | Root Cause Analysis |
| SCADA | Supervisory Control and Data Acquisition |
| Tan Delta | Dielectric dissipation factor, an insulation condition test |
Conclusion
Failure analysis is an essential engineering activity that goes beyond repairing damaged equipment.
It is a structured procedure of understanding the sequence of faults, identifying the root cause, and implementing corrective and preventive actions to improve system reliability.
Combining visual inspection, electrical testing, transformer oil diagnostics, protection records and engineering judgement allows engineers to make informed decisions regarding repair, overhaul, or replacement.