This post provides a structured checklist for reviewing the design and validating the design of electrical switchyards.
Scope
This checklist provides general guidance for planning and reviewing electrical switchyard designs.
Reference Standards
• Relevant IEC standards (IEC 61936-1 & IEC 60529).
• Relevant IEEE standards (IEEE 80 & IEEE 81).
• National electrical regulations & safety rules.
• Utility or grid operator requirements.
• Applicable engineering design guides.
Design Procedure
The overall switchyard design must be developed by considering the following aspects:
- The required switchyard voltage level must be identified based on the system requirements.
- The power input and output capacity must be determined according to the project load demand.
- The incoming and outgoing power transmission lines must be confirmed and incorporated into the electrical design.
- The switchyard location and orientation must be selected with respect to the overall power plant layout and transmission line paths.
- An appropriate switching scheme as per NEMA SG-4 & NEMA SG-6 must be selected considering system reliability, maintenance flexibility and cost.
- The system fault level information must be obtained from the utility (or) system studies.
- The design short circuit level for the switchyard equipment must be established accordingly.
- The Basic Insulation Level (BIL) must be determined based on the system voltage and insulation coordination requirements.
- The required electrical clearances must be established based on the voltage level and insulation requirements.
- The busbar type must be selected whether rigid busbar (or) flexible conductor busbar.
- Major switchyard equipment such as circuit breakers, isolators, current transformers (CTs), voltage transformers (PTs) and lightning arresters must be selected.
- The switchyard type must be determined such as Gas Insulated Switchgear (GIS), Air Insulated Switchyard (AIS), outdoor switchyard (or) indoor switchyard.
- The environmental and pollution levels at the project site must be evaluated.
- The insulator creepage distance requirements must be determined based on the pollution severity.
- The necessary safety and regulatory requirements must be identified and incorporated into the design.
Design Particulars
The detailed design of the switchyard must consider the following parameters:
- The required phase-to-ground and phase-to-phase clearances must be established according to the system voltage.
- The incoming and outgoing line termination arrangements must be confirmed with respect to the transmission line orientation.
- The grade level and the equipment foundation levels must be determined based on the electrical site conditions and flood levels.
- The switchyard layout configuration must be finalized based on considering the equipment arrangement and maintenance accessibility.
- The earthing grid design must be developed and step potential and touch potential levels must be evaluated for the electrical safety.
- A suitable lightning protection system must be designed for the switchyard.
- Adequate yard lighting arrangements must be established for a safe operation and maintenance.
- The necessary structural and foundation design parameters must be provided to the civil engineering team.
- The cable routing system such as cable trenches (or) cable trays must be finalized.
- The communication system requirements between the switchyard and control room must be defined.
Equipment Installation Checkpoints
During equipment installation planning the following points must be verified:
- For circuit breakers the foundation level and operating cubicle arrangement must be finalized.
- For isolators the operating height and foundation requirements must be confirmed.
- For power transformers the oil drainage system and fire protection arrangements must be get finalized.
- Adequate maintenance (preventive) access and cable entry provisions must be provided for the transformers.
- For lightning arresters the adequate electrical clearances must be ensured.
- For bus post insulators the insulator height and mounting arrangements must be verified.
- For instrument transformers (CTs and PTs) adequate spacing from the adjacent equipment must be maintained.
Cable Trenches
The cable routing system must be designed with the following considerations:
- Main and branch cable trenches must be provided for the routing power and control cables.
- The cable trench dimensions must be standardized while allowing the provision for future expansion.
- Bay wise symmetry must be maintained in cable routing to ensure an organized installation and easier maintenance.
Access Nodes
Proper access arrangements must be provided for equipment installation and maintenance:
- Safe and adequate access to all the switchyard equipment must be ensured.
- Maintenance access routes must be designed to facilitate the inspection and servicing activities.
- Approach roads must be provided to allow transportation and installation of heavy equipment.
Control Room
The control room design must address the following requirements:
- The control room elevation and layout must be determined considering cable routing and accessibility.
- Adequate space must be provided for protection panels, control panels, communication systems and auxiliary equipment.
- Provision must be made for future expansion of control and protection systems.
- Adequate ventilation and environmental control systems must be provided where ever required.
Maintenance Facilities
Maintenance provisions must be included in all switchyard design:
- Dedicated maintenance areas and equipment handling provisions must be provided.
- Adequate storage facilities and maintenance power tools must be arranged for the equipment servicing.
Safety
The switchyard design must incorporate the necessary safety precautions/measures:
- Proper fencing and security arrangements must be installed around the switchyard.
- Suitable fire protection systems must be provided for the equipment and cable installations.
- Fire extinguishers and emergency response equipment must be installed at the appropriate locations.
- Insulating mats, safety signage and warning boards must be provided to ensure a personnel safety.
Statutory Clearances
The design must obtain all the necessary statutory approvals:
- Approval must be obtained from the relevant electrical authorities and inspectorates.
- Compliance with the power grid operator requirements and utility regulations must be ensured.
- Necessary environmental and electrical safety clearances must be obtained before the project execution.