Top 22 Safety Guidelines for Electrical Testing and Commissioning

0
227
Top 22 Safety Guidelines for Electrical Testing and Commissioning
Top 22 Safety Guidelines for Electrical Testing and Commissioning

The safety of those who are conducting tests and those who are working on construction projects should always be the top concern. 

In order to ensure everyone’s safety, the following are basic guidelines:

Use safety shoes, a helmet, safety gloves (rubber-electrical), a rubber mat, fire extinguishers, and other safety equipment.

Before working on power circuits (LT or HT), disconnect all power sources by opening and closing circuit breakers.

Close earthing switches or, if not available, do local earthing.

To avoid accidents caused by opening the wrong panel or equipment, double-check that work is started on the correct panel or equipment.

Panel
Panel

To prevent illegal access, tag all breaker boxes and switches and use padlocks wherever possible.

Tagging and Padlocks
Tagging and Padlocks

Delegate work exclusively to qualified individuals after validating their credentials and abilities.

To avoid misunderstandings, give clear and specific directions.

Keep unauthorized personnel away from the test area by roping it off if required and posting warning signs.

Before beginning any test, make a detailed plan, including a circuit schematic for understanding.

Carefully handle test equipment such as meggers, earth testers, multimeters, & high-voltage test sets.

Secure both ends of cables during testing & verify that responsible workers are properly stationed.

To avoid accidents, apply voltage to the transformer’s low-voltage side with caution.

When there is current flowing through the primary circuit, do not open the CT secondary.

CT Secondary Circuits
CT Secondary Circuits

During a primary injection test, start with 10% of the rated current & verify all secondary circuits before escalating to the full rated current.

After performing megger or high-voltage testing, connect the equipment to earth with an insulated wire.

Before working on a motor, make sure the controller is disconnected & tagged out.

When working on equipment, make sure the switchgear is controlled locally. Control should only be returned after the work is completed.

Always utilize suitable tools and devices, and avoid line testers. Use a multimeter, making sure it’s set to the proper parameter and range.

Use long jumpers during testing to draw attention if not removed.

Before you start working on unknown equipment, carefully read the operating handbook.

When turning on equipment for the first time, remove all staff from the area and make sure fire extinguishers are in place.

Before paralleling transformers, do a low-voltage phasing check to ensure that there is no voltage across the bus coupler breaker once both transformers are turned on.

Transformer Paralleling
Transformer Paralleling

Isolate PTs by removing the control plug (or) secondary fuses prior to providing electricity to the PT secondary circuit.

Always discharge the closing & tripping springs in the circuit breaker mechanism box by turning off the control power, tripping and closing the breaker, and then tripping again.

Do not replace a blown HRC fuse with bare wire; instead, install a new HRC fuse with the appropriate rating.