What are the different MCB Trip Curves and their Characteristics?

0
182
What are the different MCB Trip Curves and their Characteristics?
What are the different MCB Trip Curves and their Characteristics?

A trip curve also called a current time graph is a graphical illustration of a circuit breakers response. 

It illustrates the present relationship between the tripping time of the protection device.

The horizontal X-axis shows the multiples of the current via the circuit breaker. 

The Y-axis shows the circuit breakers tripping time on a logarithmic scale.

The thermal area depicts the reaction of the bimetallic contact trip unit to overcurrent. 

The curve indicates that the circuit breakers tripping time decreases as the current increases. 

The first curve in the graph represents the response of the thermal trip unit.

The magnetic region demonstrates the solenoid’s sensitivity to fault current which could be a short circuit current.

A circuit breaker has no fixed tripping period and we cannot forecast a specific tripping point. It is because environmental circumstances, such as temperature have an impact on tripping.         

Circuit breakers are utilized to instantly trip the power supply in case of an overcurrent. 

However, it must not move too quickly or unnecessarily causing complications.

Overcurrent can occur under normal circumstances such as the inrush current of a motor. 

Inrush current is the large current consumption that occurs when a motor starts causing voltage drops in the main line.

The circuit breaker must be able to control the inrush current and provide some time before tripping.

As a result, the circuit breaker used should not trip too quickly causing a nuisance nor should it trip late causing harm. 

This is when the circuit breakers trip characteristics come into effect.

The tripping curve describes how quickly a circuit breaker will trip at a given current. 

The various tripping curves divide circuit breakers into groups with each category utilized for a certain type of load. 

It is important to select a circuit breaker that gives adequate overcurrent protection.

The trip curve is a schematic representation of circuit protection devices.

  1. Fuse, 
  2. MCB, 
  3. MCCB, 
  4. Supplementary protectors, 
  5. Motor protection circuit breakers, 
  6. Overload relays, 
  7. Electronic fuses & 
  8. Air circuit breakers 

are all types of circuit protection devices. 

The diagram below shows the trip curve of an MCB.

Different MCB Trip Curves
Different MCB Trip Curves

The horizontal X-axis represents multiples of current flowing through the micro circuit breaker. The Y-axis, on a logarithmic scale, shows the time it takes for the small circuit breakers to trip.

The characteristic curve shows the correlation between current & tripping time.

MCB Trip Curves Characteristics
MCB Trip Curves Characteristics

The MCB has 5 types of characteristic curves: 

1). Type B, 

2). Type C, 

3). Type D,

4). Type K and 

5). Type Z Characteristic Curves. 

They are listed below.

Type B, C or D are classified according to the breakdown current rating at which an electromagnetic operation occurs providing short-term protection in opposition to short circuits. 

The trip curve is a graph that relates the outgoing current and the tripping time (amp-sec Curve) to make sure of maximum equipment safety & performance while preventing unintentional trips.

3 to 5 times in the magnetic trip for utilization in domestic operations where maximum sensitivity is necessary and there is small devices that demands a large start-up current. 

When the loads are resistive and if there is no inrush current use B curve MCBs.

Type B Characteristic Curves
Type B Characteristic Curves

For commercial & industrial applications Type C devices are the norm. These devices are intended to trip when the current exceeds 5-10 times the rated current which is 50-100A for a 10A electrical device. 

C curve MCBs must be utilized when loads have negligible inrush current at initiation. The optimal application involves a small transformer load.

Type D devices have more limited uses mainly in industrial use where significant inrush currents are expected, 

  • Large sized battery charging systems, 
  • Winding motors, 
  • Power transformers, 
  • X-ray equipment and some discharge lighting sources.  
Type D Characteristic Curves
Type D Characteristic Curves

Type D devices are designed to trip 10-20 times per second, i.e., 100-200A / 20A electrical devices. 

Normal connection ratings indicate the amount of time a cable may be utilized continuously under specific installation conditions. 

Wires can withstand strong currents for a limited time and without becoming damaged.

The K curve MCB is intended for motor applications in which amperage climbs fast during “start-up.” 

Curves can pass through the temporary inrush of current, reducing nuisance tripping while ensuring circuit safety. 

In less than 0.01 seconds (< 0.01) the magnetic element of the K curve breaks a short circuit at ten times the rated current. 

At ten times the rated current, the K curve tripping bandwidth varies by 0.01 second.

Type K Characteristic Curves
Type K Characteristic Curves

When the current via an MCB with the type Z trip characteristics exceeds 2 to 3 times the rated current it trips immediately. 

These MCBs are particularly sensitive to short circuits & are used to protect highly sensitive electrical devices such as semiconductors. 

Low short circuit trip settings are necessary for Z type MCBs.

Type Z Characteristic Curves
Type Z Characteristic Curves
MCB Trip Curve TypeInstantaneous Magnetic Trip RangeTypical ApplicationLoad TypeKey Characteristics
Type B3 to 5 x InResidential installations, lighting circuits, heating loads & domestic appliancesResistive loads with little (or) no inrush currentHigh sensitivity, trips quickly on a small fault currents & ideal for domestic use where maximum protection is required.
Type C5 to 10 x InCommercial buildings, small motors, pumps, transformers & HVAC systemsModerate inductive loads with a moderate inrush currentMost commonly used MCB curve, balances nuisance trip prevention and fault protection.
Type D10 to 20 x InLarge motors, transformers, battery chargers, welding machines, X-ray equipment, discharge lightingHigh inrush current loadsDesigned to withstand high starting currents without nuisance tripping while providing short-circuit protection.
Type K8 to 12 x InMotor control circuits, compressors, industrial machinery, inductive loadsMotor and highly inductive loadsSpecially designed for motor starting currents. Provides enhanced overload protection while tolerating temporary inrush currents.
Type Z2 to 3 x InElectronic circuits, semiconductor devices, PLCs, sensitive instrumentationHighly sensitive electronic loadsExtremely sensitive short-circuit protection. Trips very quickly at low fault currents to protect delicate equipment.
Curve TypeSensitivityInrush Current ToleranceCommon Use
Z CurveVery HighVery LowSensitive electronics and semiconductors
B CurveHighLowResidential and lighting circuits
C CurveMediumMediumCommercial and general-purpose circuits
K CurveMedium-LowHighMotors and inductive loads
D CurveLowVery HighHeavy industrial equipment and transformers
MCB CurveTrip Range
Z Curve2–3 × In
B Curve3–5 × In
C Curve5–10 × In
K Curve8–12 × In
D Curve10–20 × In

Z Curve → Sensitive electronics.

B Curve → Domestic/resistive loads.

C Curve → General commercial and industrial loads.

K Curve → Motors and inductive equipment.

D Curve → Heavy inrush current equipment and transformers.

B-Curve: Suitable for domestic & light commercial uses such as heaters & lighting. Trips range from 3 to 5 times of rated current.

C-curve: Suitable for commercial & industrial applications that is requiring low-level surges.

D-Curve: Suitable for circuits with a strong inrush currents such as motors & transformers.

The Type B MCB trips faster than Type C & Type D MCBs for the same fault current level.

MCB Trip Characteristics

Type B MCB: Trips at 3 – 5 times of the rated current (fastest).

Type C MCB: Trips at 5 – 10 times of the rated current.

Type D MCB: Trips at 10 – 20 times of the rated current (slowest).

Fastest Trip: Type B MCB

Used for residential circuits, lighting loads and low inrush current applications.

Example: A 10A Type B MCB can trip instantly at 30–50A while a 10 A Type C MCB may need a current of 50 – 100A to trip instantly.

The MCB trips 3 to 5 times the entire load current according to the B curve. It is mostly utilized in home settings with resistive loads, including as lighting fixtures and low-surge domestic appliances.

The MCB trips 5 to 10 times the full load current when it has a C curve. It is utilized in commercial and industrial settings where there is a larger risk of short circuit currents such as fluorescent lighting and mostly inductive loads.

The MCB trips 10 to14 times the full load current according to the D curve. It is utilized in situations where inrush currents may be quite high such as in X-ray machines.