MCCB & MCB Sizing Chart

0
377
MCCB and MCB Sizing Chart
MCCB and MCB Sizing Chart

The MCCB sizing and selection table is an essential reference table used for selecting the appropriate Molded Case Circuit Breaker (MCCB) (or) Miniature Circuit Breaker (MCB) depending upon the connected electric load that is rated in kilowatts (kW). 

The table ensures a safe & reliable operation of electrical systems by incorporating the safety margins & a standard breaker ratings as per DEWA regulations.

The table is detailed to simplify the selection of circuit breakers for a wide range of different electrical loads. 

It helps engineers, electricians and designers to choose the correct protective device without complex calculations.

The table starts with the base electrical load expressed in kilowatts. 

Each load value represents the actual connected load in the system.

A 25% safety margin is added to the base load. 

This additional margin ensures that the breaker does not trip under any normal fluctuations (or) temporary overload conditions.

Higher load factors such as 50%, 75% and 100% are also considered in the tables. 

These values give flexibility for the future expansion in detail and their design considerations.

The adjusted load value is utilized to determine the appropriate breaker rating. 

The standard MCCB rating is selected such that it is equal to (or) higher than the calculated load.

This ensures that the breaker operates safely without any nuisance tripping. 

It also protects cables and equipment from the overload and short circuit conditions.

Lower load applications typically use Miniature Circuit Breakers (MCBs).

These are applicable for small current ratings and residential (or) light commercial loads.

Higher load applications use Molded Case Circuit Breakers (MCCBs).

These are designed for the industrial and heavy duty applications with higher current ratings.

Current (A) = (Power (kW) x 1000) / (√3 x Voltage x Power Factor)

For 10 kW load at 415V and PF 0.8: 

Given

Kw = 10 Kw

V = 415 V

PF = 0.8

Formula

Current (A) = (Power (kW) x 1000) / (√3 x Voltage x Power Factor)

Solution

Current (A) = (10 x 1000) / (√3 x 415 x 0.8)

Current ≈ 17.36 A

Answer

Select next standard MCCB = 20A.

The inclusion of a 25% safety margin improves the system reliability. 

It prevents frequent tripping due to the minor load variations.

Proper breaker selection protects electrical equipment from damage. 

It also enhances the overall safety of the electrical installation.

S. NoLoad (kW)25%50%75%100%125%MCCB (A)
13.454.315.186.046.908.636
25.747.188.6110.0511.4814.3510
39.1911.4913.7916.0818.3822.9716
411.4914.3617.2320.1122.9828.7220
514.3617.9521.5425.1328.7235.9025
618.3822.9727.5732.1636.7645.9532
722.9728.7134.4540.2045.9457.4440
828.7235.9043.0850.2657.4471.8050
936.1845.2354.2763.3272.3690.4563
1045.9557.4468.9380.4191.90114.8880
1157.4471.8086.16100.52114.88143.60100
1271.8089.75107.70125.65143.60179.50125
1391.90114.88137.85160.83183.80229.75160
14114.87143.59172.31201.02229.74287.18200
15143.59179.49215.38251.28287.18358.98250
16172.31215.39258.47301.54344.62430.78300
17201.03251.29301.55351.80402.06502.58350
18229.74287.18344.61402.05459.48574.35400
19287.20359.00430.80502.60574.40718.00500
20361.85452.31542.78633.24723.70904.63630
21459.49574.36689.24804.11918.981148.73800
MCB Chart Representation
MCB Chart Representation

This table outlines the selection process for Molded Case Circuit Breakers (MCCBs) according to the Dubai Electricity and Water Authority (DEWA) regulations. 

It calculates the necessary MCCB size based on the connected load in kilowatts (kW). 

A 25% safety factor is added to the initial load to determine the adjusted load requirement. 

These standards ensure uniformity & safety in electrical installations.

Using DEWA approved selection methods helps in obtaining approvals and maintaining compliance in projects.

S.NoLoad (kW)25%50%75%100%125%MCCB (A)
15.747.188.6110.0511.4814.3510
28.6210.7712.9315.0817.2421.5515
311.4914.3617.2320.1122.9828.7220
417.2321.5425.8530.1534.4643.0830
522.9728.7134.4540.2045.9457.4440
628.7235.9043.0850.2657.4471.8050
734.4643.0851.6960.3168.9286.1560
845.9557.4468.9380.4191.90114.8880
957.4471.8086.16100.52114.88143.60100
1071.8089.75107.70125.65143.60179.50125
1191.90114.88137.85160.83183.80229.75160
12103.38129.22155.07180.91206.76258.45180
13114.87143.59172.31201.02229.74287.18200
14129.23161.54193.85226.15258.46323.08225
15143.59179.49215.38251.28287.18358.98250
16172.31215.39258.47301.54344.62430.78300
17201.03251.29301.55351.80402.06502.58350
18229.74287.18344.61402.05459.48574.35400
  1. The table simplifies the design process. 
  2. It reduces calculation errors and saves time. 
  3. It ensures proper protection of electrical systems. 
  4. It also provides a standardized method to breaker selection.
  1. The MCCB selection table is widely used in residential buildings. 
  2. It is also used in commercial complexes and industrial facilities.
  3. It assists in panel design and load distribution planning. 
  4. It is also useful in energy management and system upgrades.

The 125% Rule in Electrical Load is that electricians must understand and attain knowledge. 

The 125% rule requires that 

  • Branch circuits, 
  • Feeders and 
  • Overcurrent protective devices (breakers) 

for continuous loads (running 3 hours / more) be rated at 125% of the total load.

The maximum normal current rating of an MCB may technically range up to just 125A whereas the maximum normal current rating of an MCCB is usually much higher ranging from 16A to as high as an almost 1600A.

The MCCB selection and sizing table is an essential online tool for electrical engineers and technicians. 

It provides a detailed, structured and reliable method for the purpose of selecting the right circuit breakers based on the load requirements and safety margins.

It ensures a safe operation, regulatory compliance & efficient electrical system design.