What are the Primary Protection Systems used in Power Transmission Lines?

0
641
Primary Protection Systems used in Power Transmission Lines
Primary Protection Systems used in Power Transmission Lines

Power transmission line protection is necessary for assuring the reliability and safety of power systems. 

Transmission line protection systems are intended to identify and isolate faults in order to prevent equipment damage, preserve stability & ensure safety. 

Single-Line-to-Ground Fault: This occurs when one of the conductors touches the ground.

Line-to-Line Fault: A fault that occurs between two conductors.

Double Line-to-Ground Fault: A double line-to-ground fault occurs when two conductors make contact with the ground at the same time.

Three-Phase Fault: Includes all three phases & is typically severe.

Electrical protection devices include 

  1. Lightning Arresters, 
  2. Surge Protectors, 
  3. Fuses, 
  4. Relays, 
  5. Circuit Breakers, 
  6. Reclosers and others. 

Every electrical circuit contains a maximum voltage or amperage. 

If this value is surpassed, the wire will overheat, melting its insulation and igniting a fire.

Transmission line protection is essential for ensuring the safety of the both equipment & personnel while also maintaining system reliability.

Transmission lines are susceptible to failures, such as short or open circuits that can cause substantial damage if not treated immediately.

Protection systems are intended to isolate problematic sections of the line, preventing the fault from transmitting and causing additional harm.

Damage to cables occurs as the dielectric material that serves as an insulator wears out over time. 

Many causes may be contributing to this which includes thermal stress from the continuous line overloading, electrical stress from steady-state and transient overvoltages and most commonly water seeping into the cable’s insulation.

Transmission Lines
Transmission Lines

Line protection should have specific characteristics, such as the capacity to trip merely the circuit breaker physically closest to the fault area in the case of an outage. 

If the breaker at the fault location does not trip, the breaker directly adjacent to it will act as a backup. 

To prevent circuit breakers in working areas of the system from tripping for no apparent cause, ensure that the line protection relays are operating as quickly as feasible. 

The following are some of the types of protecting transmission lines:

1). Overcurrent Protection (OCP)

2). Distance Protection (Impedance Protection)

3). Differential Protection 

4). Directional Overcurrent Protection (DOCP)

5). Earth Fault Protection 

6). Pilot Protection Schemes

7). Overvoltage & Surge Protection 

8). Auto-Reclosing Protection 

9). Power Swing Blocking Protection 

10). Underfrequency and Undervoltage Protection

Overcurrent protection is the primary way for identifying defects in transmission lines. It activates when the current exceeds a predetermined limit because of overloads (or) short circuits.

Overcurrent relays monitor line current using current transformers (CTs). 

Whenever the current that is being measured is greater than the pickup setting of the relay, the relay will send a trip signal to circuit breaker device.

Overcurrent Protection (OCP)
Overcurrent Protection (OCP)

Types

Instantaneous Overcurrent (50 relay): Instantaneous Overcurrent (50 relay) operates without intentional delay, tripping quickly for high-magnitude faults near the relay position.

Time-Delayed Overcurrent (51 relay): Time-Delayed Overcurrent (51 relay implements a time delay permitting downstream devices to resolve faults first and ensuring proper coordination.

Application

Provides backup protection for the distance & differential relays.

Radial transmission lines & substations are common applications.

When it comes to EHV transmission lines, distance protection is the primary factor. The apparent impedance between relay position & the fault is one of the factors that it determined.

The formula V/I is utilized by the relay in order to determine the impedance (Z). Line length is directly proportional to impedance, which means that a fault that is closer to relay will have a lower impedance.

Zones of Protection

Zone 1: The protected line is between 80 and 90 percent; the trip is immediate.

Zone 2: remaining line length plus 20-50% of the next line, delayed trip (e.g., 0.3-0.5 seconds).

Zone 3: Backup for remote failures; longer latency (1-1.5 seconds).

Advantages

Very selective.

Basic setup does not involve direct communication.

Disadvantages

Fault resistance has the potential to affect accuracy.

Power swings may cause misoperation.

Distance Protection (Impedance Protection)
Distance Protection (Impedance Protection)

Differential protection isolates faults within a portion by comparing current entering and exiting it.

The relay will trip if I1 ≠ I2 exceeds a certain threshold, indicating an internal malfunction. This is based on Kirchhoff’s current law.

Advantages

Extremely quick (20-40 ms).

Absolute selectivity.

Disadvantages

Needs CTs on both ends.

Applications

Generator/transformer units.

Busbars.

Transmission lines are rather short.

Differential Protection
Differential Protection

Fault current in interconnected networks can travel in several directions. Directional overcurrent relays detect whether the fault is upstream (or) downstream.

For the purpose of determining the direction of the fault, the operating concept includes comparing phase angle of the voltage & the current. 

Only in cases where the fault is in the forward direction does it function.

Advantages 

Prevents unnecessary tripping for problems outside the protection zone.

Applications

Ring networks,

Parallel transmission lines.

Earth faults arise when a conductor contacts the earth or grounded equipment, usually due to insulation failure.

Types

Residual Earth Fault Protection: Residual Earth Fault Protection measures residual current (the sum of three-phase currents). Any imbalance suggests leakage to the earth.

Sensitive Earth Fault Protection Sensitive Earth Fault Protection identifies very small leakage currents (which is frequently in ungrounded / high-resistance grounded systems).

Importance

Prevents equipment damage caused by extended arcing.

Reduces the chance of fire.

Pilot protection exchanges signals between line ends using communication channels (fiber optics, microwave, and PLC).

Types

Direct Under reach Transfer Tripping: An immediate trip for faults within the zone.

Permissive Overreach Transfer Tripping:  Tripping occurs only when both ends notice an overreach fault & transmit a permitted signal.

Blocking Schemes: Prevents tripping if the remote end signals a defect in the other direction.

Advantages

High-speed operation (<100 ms),

Long lines require a high level of reliability.

Pilot Protection
Pilot Protection

Lightning surges & switching overvoltages are two types of risk factors that can affect transmission systems.

Equipment Used

Lightning Arresters (LA) divert surge currents securely to ground.

Surge Capacitors/Reactors controls the rate of voltage growth.

Advantages

Prevents insulation degradation.

Increases the useful life of the equipment.

Up to 80% of line faults are temporary and typically resolve themselves (e.g., lightning flashovers, tree contact).

After a fault trip, the breaker automatically recloses after a predetermined interval (single-shot / multi-shot reclosing).

Advantages

Increases reliability,

Reduces the duration of outages.

Note: This is most commonly used on overhead wires rather than cables.

Auto-Reclosing Protection 
Auto-Reclosing Protection 

Distance relays may misunderstand large power swings during system disturbances as faults.

Power swing blocking relays detect impedance changes during swings and prevent tripping unless a defect is identified.

Avoids disconnecting healthy wires during instability situations.

Underfrequency Protection

Detects when the system frequency falls below a predetermined threshold owing to a generation shortfall.

Load shedding is performed gradually in order to prevent the failure of the system.

Undervoltage Protection

Monitors supply voltage & trips (or) alerts when it falls below permitted limits.

Prevents prolonged undervoltage, which can harm motors and delicate equipment.

Protection 
Protection 
  • IEC 60255-151: specifies functional criteria for overcurrent relays.
  • IEC 61850-7-4: specifies data models for the distance relays in the substation automation.
  • ANSI C37.2: specifies device function number 87.
  • IEEE C37.234: specifies earth fault prevention for lines.
  • IEC 60255-127: Power swing detector elements.

Power transmission circuits must be protected for grid stability, equipment safety & supply continuity. 

Transmission protection at present includes primary distance, differential relays, backup overcurrent & communication-assisted methods. 

Numerical relays and smart grid technology have made protection systems faster, more accurate & better coordinated.