Contactor Size Calculator

0
17
Contactor Size Calculator
Contactor Size Calculator

Selecting the correct contactor is one of the most essential steps in motor control circuit design. 

IEC & NEC
Contactor Size Calculator
IEEE / IEC 60947-4-1  ·  NEC Article 430  ·  Full Load Current & Derating
Standard:
Calculating…
1 · Phase Configuration
2 · Application Type
3 · Motor Parameters
Power Unit:
kW
V
4 · Derating Factors
⚠ Environmental Conditions
Calculated FLC (Full Load Current)
A
Required Derated Rating (Ie)
A
Recommended Contactor Ratings (IEC)
Contactor Amps (Ie)
Contactor Type
Utilization category
Contactor kW
Equivalent motor power
Making/Breaking
×10 Ie (AC-3/AC-3e)
Rated Voltage (Ue)
Minimum rated voltage
Insulation Voltage (Ui)
Per IEC 60947
Impulse Voltage (Uimp)
Per IEC 60947-1
Further IEC Considerations
Short-Circuit & CoordinationSelect Type 1 or Type 2 coordination. Use manufacturer-tested tables to pair this contactor with an overload relay and SCPD (fuse or MCCB) at the available fault level.
Overload ProtectionPair with an overload relay whose current range includes the motor FLC. Use Trip Class 10 for standard starts; Class 20/30 for high-inertia loads.
Control Circuit / CoilMatch coil voltage to your control supply (e.g., 24V DC or 230V AC). Size the control transformer for the inrush (pickup) VA, not just the sealed VA.
Auxiliary & Mechanical DetailsAdd auxiliary contacts (NO/NC) for seal-in circuits and PLC signals. Use mechanical interlocks for reversing starters. Verify terminal wire-size compatibility and tightening torques.
ⓘ Results are for preliminary sizing only. Always verify with manufacturer datasheets and a licensed electrical engineer before installation.
Standard Derating Factors (IEC 60947) Apply when ambient conditions exceed standard ratings (40°C / 2000 m)
ConditionValueDerating Factor
Ambient TemperatureUp to 40°C (104°F)kT = 1.00
50°C (122°F)kT = 0.95
55°C (131°F)kT = 0.90
60°C (140°F)kT = 0.85
AltitudeUp to 2000 m (6560 ft)kalt = 1.00
2500 m (8200 ft)kalt = 0.95
3000 m (9840 ft)kalt = 0.90
4000 m (13120 ft)kalt = 0.80
GroupingSingle / SpacedkG = 1.00
Tightly GroupedkG = 0.80 – 0.90
Contactor Size Chart (IEC vs. NEC) Quick reference for typical 3-phase motors. IEC: AC-3 at 400V; NEC: at 480V. PF=0.85, Eff=0.90.
Motor (kW) Voltage PF IEC Size NEC Size

Related Electrical Calculators

Related Electrical Calculators

Related Electrical Calculators

All Categories

Electrical Converters

LED Resistor Calculator Inductance of Straight Wire & Electrode Voltage Divider Calculator Current Divider Calculator Skin Effect Calculator Parallel Resistors Calculator Series Resistors Calculator Series Inductors Calculator Parallel Inductors Calculator Series Capacitors Calculator Parallel Capacitors Calculator Zener Diode & Voltage Regulator Inductance of Air Core Inductor RMS Voltage Calculator Peak Voltage Calculator Peak to Peak Voltage Calculator Capacitive Reactance Calculator Inductive Reactance Calculator Shunt Resistance Calculator Faraday's Law Calculator Earth Conductor Size Calculator Ground Wire Size Calculator Motor Current Calculator (KW) 3-Phase Power Calculator Single Phase Motor Capacitor Breaker Size Calculator Negative Sequence Voltage Calculator Short Circuit Current Calculator RC Circuit Calculator Electrical Power Calculator Resistivity Calculator Capacitance to Charge Conversion Line Current Calculator Phase Current Calculator Over Current Relay Setting Capacitor Energy Calculator Source Voltage Calculator Maximum Demand Calculator Current Efficiency Calculator Secondary Voltage Calculator Capacitor Energy & Time Calculator Resistor Color Code Calculator Medium Voltage Capacitor Calculator Voltage Unbalance Calculator Line to Phase Voltage Calculator Wire Loss Calculator Earthing Resistance Calculator Sheath Current Calculator kWh Energy Consumption Calculator Cable Tray Sizing Calculator HT to LT Current Calculator Capacitor Discharge Time Calculator

Click here for more Electrical Calculators

You can also follow us on Facebook and Linkedin to receive daily updates.

An undersized contactor fails prematurely due to contact erosion and an oversized one adds unnecessary cost and cabinet space. 

This post explains how to use the Contactor Size Calculator using an interactive calculator tool that combines 

to attain at a properly rated contactor every time.

The calculator supports 2 globally recognised electrical standards:

  • IEC 60947-4-1: Low-voltage switchgear and controlgear, Part 4-1: Contactors & motor-starters. Defines Ie (rated operational current), utilisation categories (AC-1, AC-3, AC-3e, AC-4), insulation voltage (Ui) and impulse withstand voltage (Uimp).
  • NEC Article 430: Motors, Motor Circuits and Controllers. Covers conductor sizing at 125% FLA, branch-circuit OCPD limits, overload relay settings, disconnect ratings and controller HP ratings.

Short-Circuit Protection & Coordination

Every contactor must be applied within a tested combination starter (Type 1 / Type 2 coordination) (or) with a verified upstream SCPD (fuse or MCCB).

The available fault current at the installation point should not exceed the combination Short Circuit Current Rating (SCCR). 

Always consult the manufacturers coordination tables.

Overload Relay Selection

Pair the contactor with an electronic (or) bimetallic overload relay whose current adjustment range includes the motor FLC. 

Use Trip Class 10 for standard motors and Class 20 (or) 30 for high inertia (or) frequent start applications. 

Class selection directly affects motor protection response time during locked-rotor conditions.

Control Circuit & Coil

Match the contactor coil voltage to your control supply (common options: 24 V DC, 110 V AC, 230 V AC). 

Size any control transformer for the inrush (pickup) VA which is typically 6 to 10 times the sealed VA and not the continuous sealed VA alone. 

Failure to account for inrush results in nuisance control-supply dropout during starting.

Mechanical & Auxiliary Details

Specify the correct number and type of auxiliary contacts (NO / NC) for seal-in circuits, remote indication and PLC feedback. 

For reversing starters use mechanical interlocks in addition to electrical interlocking to prevent phase-to-phase short circuits. 

Verify terminal wire-size compatibility and published tightening torques to ensure reliable connections throughout the service life of the equipment.

The full load current is the foundation of every sizing of contactor. 

The calculator uses the following relationships:

Three-phase:   I = P / (√3 x V x PF x η)

Single-phase:   I = P / (V x PF x η)

Where 

P - Motor shaft power in watts (converted from kW or HP as entered)

V - line-to-line voltage for three-phase (or) line-to-neutral for single-phase

PF - Power Factor (cos φ)

η - Motor Efficiency

Both PF and η default to typical values of 0.85 and 0.90 respectively but SHOULD be verified against the motor nameplate for accurate sizing.

Standard contactor ratings are certified at 40°C ambient and altitudes up to 2000 m. 

When site conditions exceed these limits the rated operational current must be reduced by a combined derating factor:

Ie(required) = FLC / (kT x kalt x kG)

The 3 derating factors are:

  • kT: Temperature derating factor - Accounts for reduced heat dissipation at the elevated ambient temperatures.
  • Kalt: Altitude derating factor - Air density decreases with altitude reducing the cooling capability of both the contactor & associated insulation.
  • kG: Grouping factor - When multiple contactors are mounted in a tightly packed enclosure and mutual heating reduces individual ratings. Typical values range from 0.80 to 1.00.
ConditionFactorImpact
≤ 40°C (104°F)kT = 1.00No derating required
50°C (122°F)kT = 0.955% current reduction
55°C (131°F)kT = 0.9010% current reduction
60°C (140°F)kT = 0.8515% current reduction
≤ 2000 m (6560 ft)kalt = 1.00No derating required
2500 m (8200 ft)kalt = 0.955% derating
3000 m (9840 ft)kalt = 0.9010% derating
4000 m (13120 ft)kalt = 0.8020% derating

The table below summarises typical contactor selections for standard 3 phase motors at 400 V (IEC) and 480 V (NEC) with PF = 0.85 and efficiency = 0.90.

Motor PowerVoltagePFIEC Size (AC-3)NEC Size
5.5 – 11 kW400V / 480V0.85AC-3, 18–25 ANEMA Size 1–2
12.5 – 22 kW400V / 480V0.85AC-3, 32–50 ANEMA Size 2–3
25 – 37 kW400V / 480V0.85AC-3, 50–80 ANEMA Size 3
40 – 55 kW400V / 480V0.85AC-3, 95–115 ANEMA Size 4
60 – 75 kW400V / 480V0.85AC-3, 150 ANEMA Size 4
80 – 100 kW400V / 480V0.85AC-3, 185–225 ANEMA Size 5

Note

IEC sizes shown for AC-3 category at 400 V. 

NEC NEMA sizes based on 480 V, 3-phase. 

Always confirm with the manufacturer datasheets.

Previous articleNEMA to IP Converter
Rabert T
As an electrical engineer with 5 years of experience, I focus on transformer and circuit breaker reliability in 110/33-11kV and 33/11kV substations. I am a professional electrical engineer with experience in transformer service and maintenance. I understand electrical principles and have expertise troubleshooting, repairing, and maintaining transformers, circuit breakers, and testing them.