Fuse Size Calculator

0
808
Fuse Size Calculator
Fuse Size Calculator

A fuse protects electrical circuits from overloads and short circuits by interrupting the excessive current flow.

Fuse Size Calculator

Fuse Size Calculator

NEC / IEC — Compliant Sizing Reference

IEC Mode: Motor loads (DOL starters) only · IEC 60947-4-1 · Enter motor nameplate current (In)
Results NEC Mode
Time-Delay Fuse
TD
—
Non-Time-Delay Fuse
NTD
—
▲ Round UP to the next standard fuse rating.
Standard sizes: 1, 3, 6, 10, 15, 20, 25, 30, 35, 40, 45, 50, 60, 70, 80, 90, 100, 110, 125, 150, 175, 200 A…
Motor note: If TD fuse trips during start-up, NEC permits increasing up to 225% of FLC.
‘aM’ Motor Protection Fuse
Motor Specific
— to —
In × 1.6 — In × 2.0
‘gG/gL’ General Purpose Fuse
General Purpose
— to —
In × 2.0 — In × 2.5
▲ Verify: Check time-current curves — motor starting current (Ist ≈ 6–8× In) for start duration must fall in the non-melting zone. Confirm against manufacturer coordination tables (Type 1 or Type 2).
NEC Motor Sizing
NEC 430.52 ▶
TD = FLC × 1.75 Time-Delay Fuse (175% of FLC)
NTD = FLC × 3.00 Non-Time-Delay Fuse (300% of FLC)
Use FLC from NEC Table 430.250, not the motor nameplate. If TD fuse fails during start-up, NEC permits increasing up to 225% FLC. The Overload Relay (OLR) provides the actual motor protection.
IEC Motor Sizing
IEC 60947-4-1 ▶
‘aM’ = In × 1.6 – 2.0 Motor protection fuse range
‘gG/gL’ = In × 2.0 – 2.5 General purpose fuse range
Uses motor nameplate current (In). Must verify against manufacturer time-current curves. Fuse must handle Ist (≈ 6–8× In) for tstart without melting.
NEC Other Loads
NEC 210.20(A) ▶
AC Cont. = I × 1.25 Loads operating ≥ 3 hours (lighting, heaters)
DC = I × 1.50 All DC loads — both fuse types
For DC circuits, 150% is safe standard practice for both time-delay and non-time-delay fuses. Results are the same for both types.

Related Electrical Calculators

Related Electrical Calculators

Related Electrical Calculators

All Categories

Electrical Converters

LED Resistor Calculator Inductance of Straight Wire & Electrode Voltage Divider Calculator Current Divider Calculator Skin Effect Calculator Parallel Resistors Calculator Series Resistors Calculator Series Inductors Calculator Parallel Inductors Calculator Series Capacitors Calculator Parallel Capacitors Calculator Zener Diode & Voltage Regulator Inductance of Air Core Inductor RMS Voltage Calculator Peak Voltage Calculator Peak to Peak Voltage Calculator Capacitive Reactance Calculator Inductive Reactance Calculator Shunt Resistance Calculator Faraday’s Law Calculator Earth Conductor Size Calculator Ground Wire Size Calculator Motor Current Calculator (KW) 3-Phase Power Calculator Single Phase Motor Capacitor Breaker Size Calculator Negative Sequence Voltage Calculator Short Circuit Current Calculator RC Circuit Calculator Electrical Power Calculator Resistivity Calculator Capacitance to Charge Conversion Line Current Calculator Phase Current Calculator Over Current Relay Setting Capacitor Energy Calculator Source Voltage Calculator Maximum Demand Calculator Current Efficiency Calculator Secondary Voltage Calculator Capacitor Energy & Time Calculator Resistor Color Code Calculator Medium Voltage Capacitor Calculator Voltage Unbalance Calculator Line to Phase Voltage Calculator Wire Loss Calculator Earthing Resistance Calculator Sheath Current Calculator kWh Energy Consumption Calculator Cable Tray Sizing Calculator HT to LT Current Calculator Capacitor Discharge Time Calculator

Click here for more Electrical Calculators

You can also follow us on Facebook and Linkedin to receive daily updates.

Selecting the correct fuse size is essential for 

Electrical safety, 

Equipment protection and 

System reliability. 

Using a fuse size calculator simplifies the process and ensures compliance with NEC and IEC standards.

A Fuse Size Calculator is an electrical tool used to determine the recommended fuse rating based on current, load type and system characteristics. 

It helps engineers and electricians choose the right fuse size for AC, DC, motor and continuous loads.

Incorrect fuse sizing can result in 

  • Nuisance tripping, 
  • Equipment damage, 
  • Overheating and 
  • Fire hazards. 

Proper sizing ensures safety, efficient operation and compliance with electrical codes.

NEC Continuous Load: Fuse = Current x 1.25

NEC Motor Load: Time Delay Fuse = FLC x 1.75

NEC Motor Load: Non-Time Delay Fuse = FLC x 3.00

DC Load: Fuse = Current x 1.50

IEC mode applies specifically to motor loads (DOL starters) using the motor nameplate current (In). IEC 60947-4-1 defines 2 fuse types for motor protection:

IEC aM Fuse = Current x 1.6 to 2.0 (Lower bound to Upper bound)

IEC gG/gL Fuse = Current x 2.0 to 2.5 (Lower bound to Upper bound)

For DC circuits: 150% is the safe standard practice for both time-delay and non-time-delay fuses. 

Both fuse types yield the same result. 

For AC continuous loads: 125% accounts for heat developed over extended operation.

HP Rating208V FLC (A)230V FLC (A)460V FLC (A)575V FLC (A)
1/22.42.21.10.9
3/43.53.21.61.3
14.64.22.11.7
1-1/26.66.03.02.4
27.56.83.42.7
310.69.64.83.9
516.715.27.66.1
7-1/224.222.011.09.0
1030.828.014.011.0
1546.242.021.017.0
2059.454.027.022.0
2574.868.034.027.0

Always round UP to the next standard fuse size from this list:

Rating (A)Rating (A)Rating (A)Rating (A)Rating (A)
1154590175
32050100200
62560110225
103070125250
–3580150300+

Verify against manufacturer time-current curves. The motor starting current (Ist ≈ 6-8x In) for the start duration must fall in the non melting zone of the fuse. 

Confirm against manufacturer coordination tables (Type 1 / Type 2 coordination).

When sizing fuses for motor loads under IEC the following starting current characteristics should be considered:

  • Direct-On-Line (DOL) start: Ist ≈ 6–8x In, duration 2–10 seconds
  • Star-Delta start: Initial Ist ≈ 2–3x In (reduced starting torque)
  • Soft starter: Ist ≈ 2–4x In (adjustable ramp-up time)
  • VFD (Variable Frequency Drive): Ist ≈ 1.0–1.5x In (near-zero inrush)

Fuse selections based on motor nameplate current (In):

In (A)aM Fuse Range (A)gG/gL Fuse Range (A)Nearest Standard (IEC)
58.0 – 10.010.0 – 12.510 A
1016.0 – 20.020.0 – 25.020 A
1625.6 – 32.032.0 – 40.032 A
2032.0 – 40.040.0 – 50.040 A
2540.0 – 50.050.0 – 62.550 A
3251.2 – 64.064.0 – 80.063 A
4064.0 – 80.080.0 – 100.080 A
5080.0 – 100.0100.0 – 125.0100 A
63100.8 – 126.0126.0 – 157.5125 A
ParameterNECIEC
Governing StandardNEC 430.52 / 210.20(A)IEC 60947-4-1
Current ReferenceFLC from Table 430.250Motor nameplate (In)
Motor TD/aM Factor1.75× (175%)1.6× to 2.0×
Motor NTD/gG Factor3.00× (300%)2.0× to 2.5×
AC Continuous Load1.25× (125%)N/A (motor only)
DC Load1.50× (150%)N/A
Primarily Used InUSA, CanadaEurope, International
Overload ProtectionSeparate OLR requiredSeparate relay required
FeatureNECIEC
Motor Fuse175–300% FLC1.6–2.5 × In
StandardNEC 430.52IEC 60947-4-1
Load TypesAC/DC/MotorMotor

Fuse size calculators are widely used in industries, substations, residential systems, motor control centers and maintenance activities.

• Accurate calculations,

• Faster design process,

• Standards compliance and

• Improved electrical safety.

Multiply load current using NEC or IEC multipliers.

Continuous loads require 125% sizing under NEC.

They handle motor starting current without nuisance tripping.

The Fuse Size Calculator is an essential tool for selecting correct fuse ratings according to NEC and IEC standards. It improves safety, reliability and compliance in electrical systems.