The Earth Fault Loop Impedance (EFLI) calculator is utilized to determine the maximum permissible earth fault loop impedance (Zs) of an electrical circuit.
Calculator
Earth Fault Loop Impedance Calculator
Type B → Ia = 5 × In
Type C → Ia = 10 × In
Type D → Ia = 20 × In
Related Electrical Calculators
Related Electrical Calculators
All Categories
Electrical Converters
Electrical Machines Calculators
Transformer Calculators
Power Systems Calculators
Battery Calculators
Electrical Engineering Excel Calculators
Unit Converters
Click here for more Electrical Calculators
You can also follow us on Facebook and Linkedin to receive daily updates.
This calculation assists to verify that the protective devices such as MCBs- miniature circuit breakers will disconnect the supply quickly enough during an earth fault & thereby ensuring electrical safety and compliance with electrical standards.
What is Earth Fault Loop Impedance?
Earth fault loop impedance is the total impedance of the fault current path from the phase conductor through the fault and back to the source through the protective conductor & supply transformer.
A lower impedance allows a higher fault current to flow which enabling protective devices to operate within the required disconnection time.
Purpose
The calculator determines:
1). Instantaneous trip current (Ia) of the selected circuit breaker.
2). Maximum permissible earth fault loop impedance (Zs).
3). Compliance of protective device operation under fault conditions.
Input Parameters
1). Uo - Nominal Phase Voltage (V)
This is the nominal voltage between phase and earth.
In many low-voltage (LV) systems, the value is 230 V.
2). Circuit Breaker Size (In)
The rated current of circuit breaker in amperes (A).
Examples include 6 A, 10 A, 16 A, 20 A, 32 A and 40 A.
3). Circuit Breaker Type
The calculator supports the following MCB characteristics that is
• Type B - Instantaneous trip current Ia = 5 x In
• Type C - Instantaneous trip current Ia = 10 x In
• Type D - Instantaneous trip current Ia = 20 x In
Formula Used
Step-1: Calculate the Instantaneous Trip Current
Ia = In x Multiplier
Where
Ia - Instantaneous trip current (A)
In - Rated current of the circuit breaker (A)
Step-2: Calculate the Maximum Permissible Earth Fault Loop Impedance
Zs = Uo / Ia
Where
Zs - Maximum permissible earth fault loop impedance (Ω)
Uo - Nominal phase voltage (V)
Ia - Instantaneous trip current (A)
Solved Example
Given
Uo = 230 V
Circuit Breaker Rating = 40 A
Breaker Type = Type B
Solution
Step-1
Ia = 40 x 5 = 200 A
Step-2
Zs = 230 / 200
Zs = 1.15 Ω
Result
The maximum permissible earth fault loop impedance is 1.15 Ω
Advantages
• Quick & accurate calculations,
• Easy verification of the protective device performance,
• Improved electrical safety,
• Reduced calculation errors and
• Suitable for engineers, electricians & inspectors.
Applications
• Electrical installation testing,
• Protective device coordination,
• Distribution board (DB) verification,
• Industrial electrical maintenance,
• Compliance with inspections and
• Electrical design calculations.
Important Notes
• Always utilize the correct nominal voltage for the installation.
• Verify the trip characteristic of the actual protective device manufacturer.
• Measured loop impedance values must be lower than the calculated maximum permissible value.
• Follow the applicable electrical standards and regulations during testing & verification.
Summary
The Earth Fault Loop Impedance Calculator is a practical online calculator tool used for determining the maximum permissible loop impedance of an electrical circuit.
By calculating the trip current and their corresponding Zs value engineers & electricians may confirm that protective devices will operate correctly during fault conditions that is improving both safety & system reliability.